I got a call today asking how far in the ground does electric conduit need to be installed. This electric was running to the garage from the house and was installed only a few inches down. Of course, we do not determine how far electric is installed in the ground but I would like to know for myself.
If there is a minimal depth requirement, does anyone have the code for that? Thanks ahead of time. |
|
#2
|
||||
|
||||
|
Hello Kevin,
Not sure about "code", but when I built my home, the (underground) SE from the road to the transformer was min. 30"...and the (underground) conduit to the garage and other outbuildings was min. 18"...(in 199 Jeffrey R. Jonas Critical Eye Property Inspections JRJ Consultants Owatonna, Minnesota Chapter President InterNachi Awards Portal: http://co.nachi.org/inachiawards/
|
|
#3
|
||||
|
||||
|
UF Cable generally requires 24" of cover whereas rigid metallic conduit can be as little as 6". There are quite a few variables. . .
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#4
|
|||
|
|||
|
Please Note:
brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
There are many depth requirements, ranging from 6 inches to 24 inches, depending on type of conduit, type and size of circuit, and location of the run.
|
|
#5
|
|||
|
|||
|
Please Note:
brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
whoops wrong thread
Last edited by brian winkle; 8/28/07 at 11:48 PM.. |
|
#6
|
|||
|
|||
|
Dude...if you are just looking for Depths and a Code Reference...NEC 2005 See Section 300.5
Paul W. Abernathy |
|
#7
|
||||
|
||||
|
Please Note:
Kevin Luce is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
It's written "Column 4 Residential Branch Ciurcuits Rated 120 Volts or Less with GFCI Portection and Maximum Overcurrent Protection of 20 amperes". It reads that "All locations not specified below" in the "location of Wiring Method or circuit" applies, then burial of 12 inches is needed. Now, Column 1 is for direct burial cables or conductors, column 2 is for rigid metal counduit or intermediate metal conduit, Column 3 is for nonmatallic raceways listed for direct burial without concrete encasement or other approved raceways and column 5 is for circuts for control of irrigation and landscape lighting limited to not more than 30 volts and installed with UF or in other identified cable or Raceway. Could collumn 4 fall under wiring going to a detached garage where the outlet in that garage is protected by a GFCI breaker? |
|
#8
|
|||
|
|||
|
Yep...unless it applies to any of the locations that are indeed listed below.
For example it could actually be 6" or 4" as well as the 12" you are seeing....if the conditions of the allowance listed. Paul W. Abernathy |
|
#9
|
||||
|
||||
|
Please Note:
Kevin Luce is a non-member guest and is in no way affiliated with InterNACHI or its members.
Just to make sure I have this right. If you had 120 volt circuit protected by a GFCI breaker going to a detached garage in Non metallic Raceway, then the 18 inch burial (column 3, first row) is then reduced to 12 inches (column 4, first row). And if the circuit is in rigid metal conduit, then it doesn't matter if it GFCI protected, the depth is 6 inches (column 2, first row).
If the above information is correct, I feel I understand this table completely. |
|
#10
|
|||
|
|||
|
Correct.....however in your example chances are the circuit run to the detached garage would be GFCI anyway.....
But without looking back I think you have it. Paul W. Abernathy |
|
#11
|
|||
|
|||
|
Please Note:
brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
But Paul I believe the CIRCUIT must be GFCI protected. So the GFCI in the garage wouldn't cut it, you'd need a breaker at the beginning of the circuit to qualify for 12" depth.
|
|
#12
|
|||
|
|||
|
my statement was that if he did have receptacles in a garage ( not refering to the depth issue ) that they would need to be GFCI...not that the circuit could be protected with a GFCI receptacle versus a GFCI breaker...I was simply refering to IF he had a garage that was detached....to not forget the receptacles would need to be GFCI protected...as a general statement.
Paul W. Abernathy |
|
#13
|
|||
|
|||
|
Quote:
Paul W. Abernathy |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| AFCI Questions and Answers - Mike Holt | pabernathy | Electrical Inspections | 7 | 4/16/12 9:51 PM |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical Inspections | 19 | 8/23/11 3:56 PM |
| Nice Report on AL Wire Terminations - Enjoy | pabernathy | Electrical Inspections | 0 | 7/2/07 12:35 PM |
| K&T splice. | egarcia1 | Electrical Inspections | 13 | 2/3/07 6:36 AM |
| No Ground Rod - Sure Test Says Wiring OK | away | Electrical Inspections | 16 | 6/22/06 1:44 AM |