Default Wiring in the ground

I got a call today asking how far in the ground does electric conduit need to be installed. This electric was running to the garage from the house and was installed only a few inches down. Of course, we do not determine how far electric is installed in the ground but I would like to know for myself.

If there is a minimal depth requirement, does anyone have the code for that?

Thanks ahead of time.
Reply With Quote
  #2  
Old 8/28/07, 11:22 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,194
Default Re: Wiring in the ground

Hello Kevin,
Not sure about "code", but when I built my home, the (underground) SE from the road to the transformer was min. 30"...and the (underground) conduit to the garage and other outbuildings was min. 18"...(in 199.
Reply With Quote
  #3  
Old 8/28/07, 11:27 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Wiring in the ground

UF Cable generally requires 24" of cover whereas rigid metallic conduit can be as little as 6". There are quite a few variables. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #4  
Old 8/28/07, 11:28 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Wiring in the ground

There are many depth requirements, ranging from 6 inches to 24 inches, depending on type of conduit, type and size of circuit, and location of the run.
Reply With Quote
  #5  
Old 8/28/07, 11:32 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Wiring in the ground

whoops wrong thread

Last edited by brian winkle; 8/28/07 at 11:48 PM..
Reply With Quote
  #6  
Old 8/29/07, 12:24 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Wiring in the ground

Dude...if you are just looking for Depths and a Code Reference...NEC 2005 See Section 300.5



Paul W. Abernathy
Reply With Quote
  #7  
Old 8/30/07, 12:48 PM
Kevin Luce's Avatar
Kevin Luce Kevin Luce is offline
Active Poster
 
Join Date: Apr 2005
Location: Highland, Indiana
Posts: 201
Please Note: Kevin Luce is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Wiring in the ground

Quote:
Originally Posted by pabernathy
Dude...if you are just looking for Depths and a Code Reference...NEC 2005 See Section 300.5
I guess I need a little help understanding this Section. Column 1, 2, 3 and 5 I understand. Column 4 is where I'm a little confused.

It's written "Column 4 Residential Branch Ciurcuits Rated 120 Volts or Less with GFCI Portection and Maximum Overcurrent Protection of 20 amperes". It reads that "All locations not specified below" in the "location of Wiring Method or circuit" applies, then burial of 12 inches is needed. Now, Column 1 is for direct burial cables or conductors, column 2 is for rigid metal counduit or intermediate metal conduit, Column 3 is for nonmatallic raceways listed for direct burial without concrete encasement or other approved raceways and column 5 is for circuts for control of irrigation and landscape lighting limited to not more than 30 volts and installed with UF or in other identified cable or Raceway.

Could collumn 4 fall under wiring going to a detached garage where the outlet in that garage is protected by a GFCI breaker?
Reply With Quote
  #8  
Old 8/30/07, 1:32 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Wiring in the ground

Yep...unless it applies to any of the locations that are indeed listed below.

For example it could actually be 6" or 4" as well as the 12" you are seeing....if the conditions of the allowance listed.



Paul W. Abernathy
Reply With Quote
  #9  
Old 8/30/07, 2:10 PM
Kevin Luce's Avatar
Kevin Luce Kevin Luce is offline
Active Poster
 
Join Date: Apr 2005
Location: Highland, Indiana
Posts: 201
Please Note: Kevin Luce is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Wiring in the ground

Just to make sure I have this right. If you had 120 volt circuit protected by a GFCI breaker going to a detached garage in Non metallic Raceway, then the 18 inch burial (column 3, first row) is then reduced to 12 inches (column 4, first row). And if the circuit is in rigid metal conduit, then it doesn't matter if it GFCI protected, the depth is 6 inches (column 2, first row).

If the above information is correct, I feel I understand this table completely.
Reply With Quote
  #10  
Old 8/30/07, 2:31 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Wiring in the ground

Correct.....however in your example chances are the circuit run to the detached garage would be GFCI anyway..... if there is power in the detached garage the receptacles have to be GFCI protected.

But without looking back I think you have it.



Paul W. Abernathy
Reply With Quote
  #11  
Old 9/1/07, 12:06 AM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Wiring in the ground

But Paul I believe the CIRCUIT must be GFCI protected. So the GFCI in the garage wouldn't cut it, you'd need a breaker at the beginning of the circuit to qualify for 12" depth.
Reply With Quote
  #12  
Old 9/1/07, 10:46 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Wiring in the ground

my statement was that if he did have receptacles in a garage ( not refering to the depth issue ) that they would need to be GFCI...not that the circuit could be protected with a GFCI receptacle versus a GFCI breaker...I was simply refering to IF he had a garage that was detached....to not forget the receptacles would need to be GFCI protected...as a general statement.



Paul W. Abernathy
Reply With Quote
  #13  
Old 9/1/07, 10:48 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Wiring in the ground

Quote:
Originally Posted by pabernathy
Correct.....however in your example chances are the circuit run to the detached garage would be GFCI anyway..... if there is power in the detached garage the receptacles have to be GFCI protected.

But without looking back I think you have it.
See my statement......it would GFCI anyway because of his using 20A GFCI option for depth......so I was being kinda MOOT on the GFCI requirement within the garage....it would kinda cover it in the first instance.....get my drift.



Paul W. Abernathy
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 7 4/16/12 9:51 PM
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical Inspections 0 7/2/07 12:35 PM
K&T splice. egarcia1 Electrical Inspections 13 2/3/07 6:36 AM
No Ground Rod - Sure Test Says Wiring OK away Electrical Inspections 16 6/22/06 1:44 AM


All times are GMT -4. The time now is 7:32 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts