Aloha,
I did an inspection today and I found an issue that I called out but would like to know what others think. The 50 amp range breaker had two 10 ga wires at each pole for a total of 4. Besides the obvious double tap, if these wires were soldered together would it be acceptable? I could not determine where or how the business ends terminated. Any thoughts/comments welcome. My thanks in advance. Kent Fonoimoana TRIsland Home Inspections, LLC Laie, Hawaii "For your Peace in Paradise" http://www.TRIsland.com |
|
#2
|
||||
|
||||
|
Sorry forgot to press "upload" on original post...so here is a pic.
Kent Fonoimoana TRIsland Home Inspections, LLC Laie, Hawaii "For your Peace in Paradise" http://www.TRIsland.com |
|
#3
|
||||
|
||||
|
Quote:
I have no idea where the #10s are going but you can not have a 50 amp breaker giving protection to a #10 wire. Roy Cooke Need help on inspection call my cell 613-827-2011 I like email Roycooke@hotmail.com Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun. |
|
#4
|
||||
|
||||
|
Please Note:
Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
310.4 Conductors in Parallel.
Aluminum, copper-clad aluminum, or copper conductors of size 1/0 AWG and larger, comprising each phase, polarity, neutral, or grounded circuit conductor, shall be permitted to be connected in parallel (electrically joined at both ends). Good Call |
|
#5
|
|||
|
|||
|
Please Note:
brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
I have seen this before. It is the result of a kitchen remodel where there was a 30 amp cooktop and a 30 amp wall oven. The remodel replaced them both with a free standing range. The clever remodelers "re wired" for a 50 amp circuit.
|
|
#6
|
|||
|
|||
|
Please Note:
wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Its wrong, wrong, wrong. Write it up and move on.
|
|
#7
|
||||
|
||||
|
Thanks again for responses. Wrote it up under creative electrical no nos.
Kent Fonoimoana TRIsland Home Inspections, LLC Laie, Hawaii "For your Peace in Paradise" http://www.TRIsland.com |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Top Ten Wiring Hazards Threaten Life and Property | jtedesco1 | Electrical Inspections | 3 | 9/2/08 5:15 PM |
| Top Ten Wiring Hazards | jtedesco1 | Electrical Inspections | 6 | 9/1/08 8:26 PM |
| Nice Report on AL Wire Terminations - Enjoy | pabernathy | Electrical Inspections | 0 | 7/2/07 12:35 PM |
| For those in favor of licensing | gbeaumont | Legislation, Licensing & Legal Issues for Inspectors | 70 | 5/21/07 3:09 PM |
| Tidbits from the ASHI Message Board | jbushart | Miscellaneous Discussion for Inspectors | 126 | 4/27/07 11:05 AM |