Default Wiring issue for range-comments welcome

Aloha,

I did an inspection today and I found an issue that I called out but would like to know what others think.
The 50 amp range breaker had two 10 ga wires at each pole for a total of 4. Besides the obvious double tap, if these wires were soldered together would it be acceptable?
I could not determine where or how the business ends terminated. Any thoughts/comments welcome.

My thanks in advance.



Kent Fonoimoana
TRIsland Home Inspections, LLC
Laie, Hawaii

"For your Peace in Paradise"
http://www.TRIsland.com
Reply With Quote
  #2  
Old 7/16/07, 5:18 AM
kfonoimoana's Avatar
kfonoimoana kfonoimoana is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Laie, Hi
Posts: 49
Default Re: Wiring issue for range-comments welcome

Sorry forgot to press "upload" on original post...so here is a pic.
Attached Thumbnails
wiring-issue-range-comments-welcome-img_0027.jpg  



Kent Fonoimoana
TRIsland Home Inspections, LLC
Laie, Hawaii

"For your Peace in Paradise"
http://www.TRIsland.com
Reply With Quote
  #3  
Old 7/16/07, 6:20 AM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,619
Default Re: Wiring issue for range-comments welcome

Quote:
Originally Posted by kfonoimoana
Aloha,

I did an inspection today and I found an issue that I called out but would like to know what others think.
The 50 amp range breaker had two 10 ga wires at each pole for a total of 4. Besides the obvious double tap, if these wires were soldered together would it be acceptable?
I could not determine where or how the business ends terminated. Any thoughts/comments welcome.

My thanks in advance.
No . You made a good call, Repair required by qualified Person.
I have no idea where the #10s are going but you can not have a 50 amp breaker giving protection to a #10 wire.

Roy Cooke



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #4  
Old 7/16/07, 8:45 AM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Wiring issue for range-comments welcome

310.4 Conductors in Parallel.
Aluminum, copper-clad aluminum, or copper conductors of size 1/0 AWG and larger, comprising each phase, polarity, neutral, or grounded circuit conductor, shall be permitted to be connected in parallel (electrically joined at both ends).

Good Call
Reply With Quote
  #5  
Old 7/16/07, 8:46 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Wiring issue for range-comments welcome

I have seen this before. It is the result of a kitchen remodel where there was a 30 amp cooktop and a 30 amp wall oven. The remodel replaced them both with a free standing range. The clever remodelers "re wired" for a 50 amp circuit.
Reply With Quote
  #6  
Old 7/16/07, 9:36 PM
wsiegel wsiegel is offline
Active Poster
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 2,649
Please Note: wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Wiring issue for range-comments welcome

Its wrong, wrong, wrong. Write it up and move on.
Reply With Quote
  #7  
Old 7/16/07, 9:47 PM
kfonoimoana's Avatar
kfonoimoana kfonoimoana is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Laie, Hi
Posts: 49
Default Re: Wiring issue for range-comments welcome

Thanks again for responses. Wrote it up under creative electrical no nos.



Kent Fonoimoana
TRIsland Home Inspections, LLC
Laie, Hawaii

"For your Peace in Paradise"
http://www.TRIsland.com
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Top Ten Wiring Hazards Threaten Life and Property jtedesco1 Electrical Inspections 3 9/2/08 5:15 PM
Top Ten Wiring Hazards jtedesco1 Electrical Inspections 6 9/1/08 8:26 PM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical Inspections 0 7/2/07 12:35 PM
For those in favor of licensing gbeaumont Legislation, Licensing & Legal Issues for Inspectors 70 5/21/07 3:09 PM
Tidbits from the ASHI Message Board jbushart Miscellaneous Discussion for Inspectors 126 4/27/07 11:05 AM


All times are GMT -4. The time now is 7:32 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts