Default Wiring question in panel

The panel was not labeled.

There is one wire with a red and black connected two 2 breakers. It is located at the bottom right of the panel.

Can someone explain why this is wired this way.

The dryer & stove are gas.

Thanks
Attached Thumbnails
wiring-question-panel-91107-033-small-.jpg.jpg
Views:	142
Size:	59.9 KB
ID:	9146   wiring-question-panel-91107-035-small-.jpg.jpg
Views:	118
Size:	53.6 KB
ID:	9147  
Reply With Quote
  #2  
Old 2/13/07, 8:27 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Wiring question in panel

Well...it could be either the IMFAMOUS multiwire circuit or a 240V load that they simply did not understand the concept of EITHER having to be on a properly TIED breaker.

If no other ACTUAL 240V loads in the house to speak of....then it is a multiwire circuit...and if so....read my explanation on THIS thread listed below

http://www.nachi.org/forum/f19/main-panel-new-construction-13442/



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year

Last edited by pabernathy; 2/13/07 at 8:31 PM..
Reply With Quote
  #3  
Old 2/13/07, 8:30 PM
cbuell's Avatar
cbuell cbuell is offline
Active Poster
 
Join Date: Feb 2004
Location: Shorline, WA
Posts: 380
Please Note: cbuell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Wiring question in panel

What is the amperage of the breakers. Looks like a multi-wire circuit or a 240 breaker with a missing handle tie. You would almost have to know what it goes to to make a determination if the breakers are 20 amp or 15 amp.
Reply With Quote
  #4  
Old 2/13/07, 8:36 PM
David C. Macy's Avatar
David C. Macy David C. Macy is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: NE. OH
Posts: 2,555
Default Re: Wiring question in panel

Quote:
Originally Posted by cbuell
What is the amperage of the breakers. Looks like a multi-wire circuit or a 240 breaker with a missing handle tie. You would almost have to know what it goes to to make a determination if the breakers are 20 amp or 15 amp.
There 2 20 amp breakers. The basement was poorly finished. I had to dismantle half the wall to get to the panel. I left all the framing on the floor & told my client to have the framing removed as it is a violation of panel clearences. The home was vacant & I try to do my best to open the panel.
Reply With Quote
  #5  
Old 2/13/07, 9:44 PM
wsiegel wsiegel is offline
Active Poster
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 2,542
Please Note: wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Wiring question in panel

Was that the service equipment or a distribution panel. If it is a distribution panel, the grounds and neutrals need to be separated.
Reply With Quote
  #6  
Old 2/14/07, 10:40 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Wiring question in panel

William,

Lets HOPE it is the Main Distribution Panel because not only that but the NICE large GREEN bonding screw in place would be a problem as well....lol



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #7  
Old 2/14/07, 10:47 AM
David C. Macy's Avatar
David C. Macy David C. Macy is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: NE. OH
Posts: 2,555
Default Re: Wiring question in panel

Yes it is the main distribution panel & I did call out the green bonding screw.

I have asked the question pertaining to this screw many times.

Correct me if I am wrong. The purpose of the bond screw is to direct any stray current to ground & not to the panel cover. For example if a hot wire was energizing the panel & someone touched the metal dead front cover then hopefully the current is directed to groungd & not the person in contact with the cover.

It seems there are many different ways that the bonding screw & strap are connected.

It seems like this is often not done correctly.

Thanks
Reply With Quote
  #8  
Old 2/14/07, 10:51 AM
Harold E. Miller's Avatar
Harold E. Miller Harold E. Miller is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Camano Island, WA
Posts: 708
Default Re: Wiring question in panel

Quote:
Originally Posted by dmacy
Yes it is the main distribution panel & I did call out the green bonding screw.

I have asked the question pertaining to this screw many times.

Correct me if I am wrong. The purpose of the bond screw is to direct any stray current to ground & not to the panel cover. For example if a hot wire was energizing the panel & someone touched the metal dead front cover then hopefully the current is directed to groungd & not the person in contact with the cover.

It seems there are many different ways that the bonding screw & strap are connected.

It seems like this is often not done correctly.

Thanks
No the green bonding screw needs to be installed when it is the main panel......only when it is a distribution panel is it removed.
Reply With Quote
  #9  
Old 2/14/07, 10:58 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: Wiring question in panel

[quote=dmacy]Yes it is the main distribution panel & I did call out the green bonding screw./quote]

Allright guys, now I'm confused.
Paul, please clear up any confusion here.
Please bear with me.

?What would you need to call out if the panel pictured is the "Main Distribution PANEL" as I assume you mean it contains the Service Discontent?
The Green bonding screw is as it should be and I also see the strap tyeing the neutral and ground bus together.
Reply With Quote
  #10  
Old 2/14/07, 11:02 AM
David C. Macy's Avatar
David C. Macy David C. Macy is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: NE. OH
Posts: 2,555
Default Re: Wiring question in panel

I am sorry that I am confused & confusing you.

The panel pictured is the main panel. It is not a sub panel.

Sorry
Reply With Quote
  #11  
Old 2/14/07, 11:06 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: Wiring question in panel

Quote:
Originally Posted by dmacy
I am sorry that I am confused & confusing you.

The panel pictured is the main panel. It is not a sub panel.

Sorry
Then why would you "call out" the green screw?
Reply With Quote
  #12  
Old 2/14/07, 11:14 AM
Harold E. Miller's Avatar
Harold E. Miller Harold E. Miller is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Camano Island, WA
Posts: 708
Default Re: Wiring question in panel

The bonding screw in the picture grounds the neutral buss to the main service panel housing, so that if it became energized it would not shock you....it would have a path to ground.

The difference is in the distribution panels (sub panels) that have isolated ground and neutrals. Removal of the bonding screw is important to keep the neutral and grounds seperate.

Paul can probably explain it better, but that is my best.
Reply With Quote
  #13  
Old 2/14/07, 11:19 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: Wiring question in panel

Quote:
Originally Posted by hmiller
The bonding screw in the picture grounds the neutral buss to the main service panel housing, so that if it became energized it would not shock you....it would have a path to ground.

The difference is in the distribution panels (sub panels) that have isolated ground and neutrals. Removal of the bonding screw is important to keep the neutral and grounds seperate.

Paul can probably explain it better, but that is my best.
Yes, that is exactly my understanding.

David said he "called out" the green screw.
Perhaps he only means that he called out its presence and not that it was a defect.
Reply With Quote
  #14  
Old 2/14/07, 11:34 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Wiring question in panel

David,

NO...what I was saying in response to Williams question...not your post. He was asking IF it was a Sub-Panel so to speak and if to the G & N should be separated...I was saying if it TRULY was ( which I do not think it is ) a SUB-PANEL then that GREEEEENNNN screw would need to be removed also.

On the STRAY thing......ahh..not really...lol......the excessive voltage or fault current is making its way BACK to the panel and to the source which is at the transformer...but you have the concept in that the bonding jumper is NEEDED to complete the path.......

So in this case...it is VERY needed if this is a main distribution panel.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #15  
Old 2/14/07, 11:35 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Wiring question in panel

lol....HE DID NOT call out the green screw I hope......Sorry I was on the phone with a customer when I was replying........read my post please



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Top Ten Wiring Hazards Threaten Life and Property jtedesco1 Electrical Inspections 3 9/2/08 6:15 PM
Panel Question gmckenzie Electrical Inspections 9 8/24/07 2:25 AM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical Inspections 0 7/2/07 1:35 PM