Default Would call this out???

Would you call this out!


Thanks!
Attached Thumbnails
would-call-out-100_2378.jpg  
Reply With Quote
Find an InterNACHI certified Washington Home Inspector (and anywhere else in North America)
  #2  
Old 6/4/09, 5:09 PM
arook arook is offline
Active Poster
 
Join Date: Jan 2006
Location: Hamilton, NJ
Posts: 256
Please Note: arook is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Would call this out???

Yes.

Comment - compiled from several sources on this board...

Electric panel—Neutral wires installed underneath the same screw. Safety hazard. More than one “grounded conductor” (neutral /white) wire per screw on the neutral bus bar (double tapped/lugged). Each “grounded conductor” is supposed to have it’s very own screw on the bus bar, no other “grounded conductor” or “grounding conductor” (bare copper wire) should be under the screw with the “grounded conductor”. Recommend repair by a licensed electrician.
Reply With Quote
  #3  
Old 6/4/09, 5:10 PM
David C. Macy's Avatar
David C. Macy David C. Macy is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: NE. OH
Posts: 2,657
Default Re: Would call this out???

Let me take a shot.

I would on the grouped neutrals.

The information below I obtained from someone on this board.

"Neutral wires are doubled or bundled together on the neutral bus bar. Although
common practice in the past, this is unsafe due to the need to turn off multiple circuit breakers to work on any of the circuits using these wires. A qualified electrician should evaluate and repair as necessary."

It would depend on the age of the install on the ground and neutral connections.

Best to have each neutral on its own terminal and the grounds can be doubled together.
Attached Thumbnails
would-call-out-grounded-nuetral-conductor-terminals-small-.gif.gif
Views:	70
Size:	45.9 KB
ID:	29063  

Last edited by dmacy; 6/4/09 at 5:15 PM..
Reply With Quote
  #4  
Old 6/4/09, 5:15 PM
William Thacker's Avatar
William Thacker William Thacker is offline
InterNACHI Member
 
Join Date: Dec 2008
Location: Pennsylvania
Posts: 354
Default Re: Would call this out???

Quote:
Originally Posted by bhartley View Post
Would you call this out!


Thanks!
If there were indications of a neutral being overheated (brown or scorched insulation).

That is not uncommon to see in a older installs.

Multiple neutrals concern me more than multiple grounds under one lug though.
Reply With Quote
  #5  
Old 6/4/09, 5:22 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,049
Default Re: Would call this out???

I always call it out but I doubt it ever gets fixed.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

[/I]
Reply With Quote
  #6  
Old 6/4/09, 5:27 PM
Buck Hartley, CMI's Avatar
Buck Hartley, CMI Buck Hartley, CMI is offline
InterNACHI Member
 
Join Date: Nov 2005
Location: Shawnee, KS
Posts: 1,567
Default Re: Would call this out???

four years old. I called it. Thanks!
Reply With Quote
  #7  
Old 6/4/09, 7:35 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Would call this out???

Have, do and will.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #8  
Old 6/4/09, 8:05 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,342
Send a message via Yahoo to jfunderburk
Default Re: Would call this out???

Quote:
Originally Posted by bhartley View Post
Would you call this out!


Thanks!
All day long.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #9  
Old 6/4/09, 8:10 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,342
Send a message via Yahoo to jfunderburk
Default Re: Would call this out???

Quote:
Originally Posted by dmacy View Post

"Neutral wires are doubled or bundled together on the neutral bus bar. Although
common practice in the past, this is unsafe due to the need to turn off multiple circuit breakers to work on any of the circuits using these wires. A qualified electrician should evaluate and repair as necessary."
Never heard that reasoning before. I think the reason has more to do with conductivity where energized conductors may not receive a proper connection.

At any rate, I don't specify a reason. I just tell them it's not allowed by today's commonly accepted standards.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #10  
Old 6/4/09, 8:18 PM
Peter Doane's Avatar
Peter Doane Peter Doane is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Olympia, WA
Posts: 2,055
Default Re: Would call this out???

- Has been a violation going back to the Standard 67 of the UL
- Most panel manufactures require each neutral wire under its own lug EVEN if grouping of ground wires are approved.



Peter Doane
Realty Check Inspection Service
NACHI ID# 05120681
Reply With Quote
  #11  
Old 6/4/09, 9:14 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Would call this out???

Quote:
Originally Posted by pdoane View Post
- Has been a violation going back to the Standard 67 of the UL
- Most panel manufactures require each neutral wire under its own lug EVEN if grouping of ground wires are approved.
Nice to see you Peter.
Reply With Quote
  #12  
Old 6/4/09, 10:03 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Would call this out???

Waddup Pete?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #13  
Old 6/4/09, 10:20 PM
Darren Spencer Darren Spencer is offline
InterNACHI Member
 
Join Date: Nov 2007
Location: Bellevue, WA
Posts: 549
Default Re: Would call this out???

Always.



Need a Link Exchange? Inspector Links


Seattle,WA Commercial Inspectors

Reply With Quote
Find an InterNACHI certified Washington Home Inspector (and anywhere else in North America)
  #14  
Old 6/5/09, 3:44 PM
Peter Doane's Avatar
Peter Doane Peter Doane is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Olympia, WA
Posts: 2,055
Default Re: Would call this out???

Hey, Brian and Jeff! WHAT UP!



Peter Doane
Realty Check Inspection Service
NACHI ID# 05120681
Reply With Quote
  #15  
Old 6/6/09, 2:42 AM
George P. Wells, CMI's Avatar
George P. Wells, CMI George P. Wells, CMI is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Michigan
Posts: 554
Send a message via Skype™ to gwells
Default Re: Would call this out???

Quote:
Originally Posted by jfunderburk View Post
Never heard that reasoning before. I think the reason has more to do with conductivity where energized conductors may not receive a proper connection.
There are a couple of different bad things that can happen with two grounded conductors on a terminal that is not designed for more than one conductor.

The grounded conductor is a current carrying conductor. The grounded conductor is energized but has no potential (Voltage) between it and ground. If the connection is lost, there is a potential between the grounded conductor (which is no longer grounded) and ground. Anyone coming into contact with the white wire elsewhere in the house could be electrocuted.

The other major problem is that if the two grounded conductors are in contact with each other but have a loose connection to the bus bar, 240V could be impressed on 120V loads (if they are on opposite legs). That's a common cause of electrical fires.

The bottom line is that the two white wires under the same screw can cause both a fire and a shock hazard.



BestInspectors.Net
& Real Estate Training Academy

Inspection Report Software for
Windows - iOS - Mac - Android

Continuing Education
Home and Commercial Building Inspection - Skilled Trades – Real Estate – Appraisal – NFPA 921

http://www.bestinspectors.net

est. 1992
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Cell Phone Do not call #'s bjones5 Canadian Inspectors 10 1/31/09 12:17 PM
Last Call for INSPECTVUE SOFTWARE DISCOUNT $845.00 includes Tax...... jwatts1 Inspection Hardware, Software & Publications 4 8/8/07 10:47 AM
Last call for 2006 pricing for Inspection Management Systems from TheScheduleCenter gromicko Miscellaneous Discussion for Inspectors 1 12/20/06 8:22 AM


All times are GMT -4. The time now is 5:11 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts