Default Would call this out???

Would you call this out!


Thanks!
Attached Thumbnails
would-call-out-100_2378.jpg  
Reply With Quote
Find an InterNACHI certified Rhode Island Home Inspector (and anywhere else in North America)
  #2  
Old 6/4/09, 6:09 PM
Andrew Rook Andrew Rook is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Hamilton, NJ
Posts: 199
Default Re: Would call this out???

Yes.

Comment - compiled from several sources on this board...

Electric panel—Neutral wires installed underneath the same screw. Safety hazard. More than one “grounded conductor” (neutral /white) wire per screw on the neutral bus bar (double tapped/lugged). Each “grounded conductor” is supposed to have it’s very own screw on the bus bar, no other “grounded conductor” or “grounding conductor” (bare copper wire) should be under the screw with the “grounded conductor”. Recommend repair by a licensed electrician.



Andrew Rook
NJ Home Inspector
License # 24GI00063600

Rook Home Inspections LLC
Hamilton NJ
(609) 588 - 0125
www.RookInspections.com
www.MercerCountyHomeInspection.com

Be Smart, Be Sure, Be Inspected TM
Reply With Quote
  #3  
Old 6/4/09, 6:10 PM
David C. Macy's Avatar
David C. Macy David C. Macy is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Broadview Hts., OH
Posts: 1,427
Default Re: Would call this out???

Let me take a shot.

I would on the grouped neutrals.

The information below I obtained from someone on this board.

"Neutral wires are doubled or bundled together on the neutral bus bar. Although
common practice in the past, this is unsafe due to the need to turn off multiple circuit breakers to work on any of the circuits using these wires. A qualified electrician should evaluate and repair as necessary."

It would depend on the age of the install on the ground and neutral connections.

Best to have each neutral on its own terminal and the grounds can be doubled together.
Attached Thumbnails
would-call-out-grounded-nuetral-conductor-terminals-small-.gif.gif
Views:	46
Size:	45.9 KB
ID:	29063  

Last edited by dmacy; 6/4/09 at 6:15 PM..
Reply With Quote
  #4  
Old 6/4/09, 6:15 PM
William Thacker's Avatar
William Thacker William Thacker is offline
InterNACHI Member
 
Join Date: Dec 2008
Location: Pennsylvania
Posts: 354
Default Re: Would call this out???

Quote:
Originally Posted by bhartley View Post
Would you call this out!


Thanks!
If there were indications of a neutral being overheated (brown or scorched insulation).

That is not uncommon to see in a older installs.

Multiple neutrals concern me more than multiple grounds under one lug though.
Reply With Quote
  #5  
Old 6/4/09, 6:22 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,301
Default Re: Would call this out???

I always call it out but I doubt it ever gets fixed.



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #6  
Old 6/4/09, 6:27 PM
Buck Hartley, CMI Buck Hartley, CMI is offline
InterNACHI Member
 
Join Date: Nov 2005
Location: Shawnee, KS
Posts: 820
Default Re: Would call this out???

four years old. I called it. Thanks!
Reply With Quote
  #7  
Old 6/4/09, 8:35 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 4,961
Default Re: Would call this out???

Have, do and will.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #8  
Old 6/4/09, 9:05 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,762
Send a message via Yahoo to jfunderburk
Default Re: Would call this out???

Quote:
Originally Posted by bhartley View Post
Would you call this out!


Thanks!
All day long.



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #9  
Old 6/4/09, 9:10 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,762
Send a message via Yahoo to jfunderburk
Default Re: Would call this out???

Quote:
Originally Posted by dmacy View Post

"Neutral wires are doubled or bundled together on the neutral bus bar. Although
common practice in the past, this is unsafe due to the need to turn off multiple circuit breakers to work on any of the circuits using these wires. A qualified electrician should evaluate and repair as necessary."
Never heard that reasoning before. I think the reason has more to do with conductivity where energized conductors may not receive a proper connection.

At any rate, I don't specify a reason. I just tell them it's not allowed by today's commonly accepted standards.



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #10  
Old 6/4/09, 9:18 PM
pdoane's Avatar
pdoane pdoane is offline
Active Poster
 
Join Date: Dec 2005
Location: Olympia, WA
Posts: 2,040
Please Note: pdoane is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Would call this out???

- Has been a violation going back to the Standard 67 of the UL
- Most panel manufactures require each neutral wire under its own lug EVEN if grouping of ground wires are approved.
Reply With Quote
  #11  
Old 6/4/09, 10:14 PM
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 11,642
Default Re: Would call this out???

Quote:
Originally Posted by pdoane View Post
- Has been a violation going back to the Standard 67 of the UL
- Most panel manufactures require each neutral wire under its own lug EVEN if grouping of ground wires are approved.
Nice to see you Peter.



"Never ever threaten anyone in Camoflage"
Tim Wilson

"Not everyone follows the same path"
Governor Sanford, musings on the Appalachian Trail
Reply With Quote
  #12  
Old 6/4/09, 11:03 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 4,961
Default Re: Would call this out???

Waddup Pete?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #13  
Old 6/4/09, 11:20 PM
Darren Spencer Darren Spencer is offline
InterNACHI Member
 
Join Date: Nov 2007
Location: Bellevue, WA
Posts: 495
Default Re: Would call this out???

Always.



Need a Link Exchange? Inspector Links


Seattle,WA Commercial Inspectors

Reply With Quote
Find an InterNACHI certified Rhode Island Home Inspector (and anywhere else in North America)
  #14  
Old 6/5/09, 4:44 PM
pdoane's Avatar
pdoane pdoane is offline
Active Poster
 
Join Date: Dec 2005
Location: Olympia, WA
Posts: 2,040
Please Note: pdoane is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Would call this out???

Hey, Brian and Jeff! WHAT UP!
Reply With Quote
  #15  
Old 6/6/09, 3:42 AM
George P. Wells's Avatar
George P. Wells George P. Wells is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Michigan
Posts: 343
Send a message via Skype™ to gwells
Default Re: Would call this out???

Quote:
Originally Posted by jfunderburk View Post
Never heard that reasoning before. I think the reason has more to do with conductivity where energized conductors may not receive a proper connection.
There are a couple of different bad things that can happen with two grounded conductors on a terminal that is not designed for more than one conductor.

The grounded conductor is a current carrying conductor. The grounded conductor is energized but has no potential (Voltage) between it and ground. If the connection is lost, there is a potential between the grounded conductor (which is no longer grounded) and ground. Anyone coming into contact with the white wire elsewhere in the house could be electrocuted.

The other major problem is that if the two grounded conductors are in contact with each other but have a loose connection to the bus bar, 240V could be impressed on 120V loads (if they are on opposite legs). That's a common cause of electrical fires.

The bottom line is that the two white wires under the same screw can cause both a fire and a shock hazard.




Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Cell Phone Do not call #'s bjones5 Canadian Inspectors 10 1/31/09 1:17 PM
Last Call for INSPECTVUE SOFTWARE DISCOUNT $845.00 includes Tax...... jwatts1 Hardware, Software & Publications 4 8/8/07 11:47 AM
Last call for 2006 pricing for Inspection Management Systems from TheScheduleCenter gromicko Misc. Discussion 1 12/20/06 9:22 AM


All times are GMT -4. The time now is 2:35 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts