Would you call this out!
Thanks! |
| Find an InterNACHI certified Rhode Island Home Inspector (and anywhere else in North America) |
|
#2
|
|||
|
|||
|
Yes.
Comment - compiled from several sources on this board... Electric panel—Neutral wires installed underneath the same screw. Safety hazard. More than one “grounded conductor” (neutral /white) wire per screw on the neutral bus bar (double tapped/lugged). Each “grounded conductor” is supposed to have it’s very own screw on the bus bar, no other “grounded conductor” or “grounding conductor” (bare copper wire) should be under the screw with the “grounded conductor”. Recommend repair by a licensed electrician. Andrew Rook NJ Home Inspector License # 24GI00063600 Rook Home Inspections LLC Hamilton NJ (609) 588 - 0125 www.RookInspections.com www.MercerCountyHomeInspection.com Be Smart, Be Sure, Be Inspected TM |
|
#3
|
||||
|
||||
|
Let me take a shot.
I would on the grouped neutrals. The information below I obtained from someone on this board. "Neutral wires are doubled or bundled together on the neutral bus bar. Although common practice in the past, this is unsafe due to the need to turn off multiple circuit breakers to work on any of the circuits using these wires. A qualified electrician should evaluate and repair as necessary." It would depend on the age of the install on the ground and neutral connections. Best to have each neutral on its own terminal and the grounds can be doubled together. Last edited by dmacy; 6/4/09 at 6:15 PM.. |
|
#4
|
||||
|
||||
|
If there were indications of a neutral being overheated (brown or scorched insulation).
That is not uncommon to see in a older installs. Multiple neutrals concern me more than multiple grounds under one lug though. |
|
#5
|
||||
|
||||
|
I always call it out but I doubt it ever gets fixed.
"Never underestimate the difficulty of changing false beliefs by facts." |
|
#6
|
|||
|
|||
|
four years old. I called it. Thanks!
|
|
#7
|
||||
|
||||
|
Have, do and will.
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ℠ Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#8
|
||||
|
||||
|
Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#9
|
||||
|
||||
|
Quote:
At any rate, I don't specify a reason. I just tell them it's not allowed by today's commonly accepted standards. Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#10
|
||||
|
||||
|
Please Note:
pdoane is a non-member guest and is in no way affiliated with InterNACHI or its members.
- Has been a violation going back to the Standard 67 of the UL
- Most panel manufactures require each neutral wire under its own lug EVEN if grouping of ground wires are approved. |
|
#11
|
|||
|
|||
|
Quote:
"Never ever threaten anyone in Camoflage" Tim Wilson "Not everyone follows the same path" Governor Sanford, musings on the Appalachian Trail
|
|
#12
|
||||
|
||||
|
Waddup Pete?
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ℠ Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#13
|
|||
|
|||
|
Always.
|
| Find an InterNACHI certified Rhode Island Home Inspector (and anywhere else in North America) |
|
#14
|
||||
|
||||
|
Please Note:
pdoane is a non-member guest and is in no way affiliated with InterNACHI or its members.
Hey, Brian and Jeff! WHAT UP!
|
|
#15
|
||||
|
||||
|
Quote:
The grounded conductor is a current carrying conductor. The grounded conductor is energized but has no potential (Voltage) between it and ground. If the connection is lost, there is a potential between the grounded conductor (which is no longer grounded) and ground. Anyone coming into contact with the white wire elsewhere in the house could be electrocuted. The other major problem is that if the two grounded conductors are in contact with each other but have a loose connection to the bus bar, 240V could be impressed on 120V loads (if they are on opposite legs). That's a common cause of electrical fires. The bottom line is that the two white wires under the same screw can cause both a fire and a shock hazard. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Cell Phone Do not call #'s | bjones5 | Canadian Inspectors | 10 | 1/31/09 1:17 PM |
| Last Call for INSPECTVUE SOFTWARE DISCOUNT $845.00 includes Tax...... | jwatts1 | Hardware, Software & Publications | 4 | 8/8/07 11:47 AM |
| Last call for 2006 pricing for Inspection Management Systems from TheScheduleCenter | gromicko | Misc. Discussion | 1 | 12/20/06 9:22 AM |