Default What would happen?

Inspection yesterday (30th) the service panel had "grounding conductors" and "grounded conductors" together on the bus bars under one screw. I told client this was a safety issue and should be looked at (although I see this quite often up here) the house is ten years old and this is original wiring. Client asked me what could happen if wiring left like that? I don't really know? What could happen and what should I have told client?
Attached Thumbnails
would-happen-img_3670.jpg  
Reply With Quote
Need a home inspection in Minnesota? Check out InterNACHI's listing of Minnesota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 5/2/10, 12:47 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What would happen?

Probably nothing, but the two wires (grounded and grounding) are not permitted in the same hole but they are permitted on the same bus. You were correct to point that out. It's an actual NEC violation too.

Quote:
408.41 Grounded Conductor Terminations.
Each grounded conductor shall terminate within the panelboard in an individual terminal that is not also used for another conductor.
Exception: Grounded conductors of circuits with parallel conductors shall be permitted to terminate in a single terminal if the terminal is identified for connection of more than one conductor.
Reply With Quote
  #3  
Old 5/2/10, 12:50 AM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: What would happen?

Can I install the neutral and ground conductor in the same termination?

Attached Files
File Type: pdf Double Tap Neutral Grounds.pdf (60.3 KB, 133 views)



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #4  
Old 5/2/10, 8:29 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What would happen?

Quote:
Originally Posted by ccurrins View Post
Can I install the neutral and ground conductor in the same termination?


Nice resource. As the document mentioned this has been part of the UL listing standard for quite some time. However, since many electricians are unfamiliar with every nuance of the listing standard it was highly ignored. The inclusion of the actual standard in the NEC has made this prohibition much clearer for the installer who is more familiar with the requirements of the electrical code.
Reply With Quote
  #5  
Old 5/2/10, 8:30 AM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 2,037
Default Re: What would happen?

It can cause a poor connection, which can lead to overheating of the conductors like this.




Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
Houston Thermal Inspections & Infrared Imaging Find us on Facebook
Houston Home Inspector

Houston, TX
Reply With Quote
  #6  
Old 5/2/10, 6:54 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: What would happen?

The larger of the issues with this type of installation that with more and more multi-wire branch circuit installations going on the risk of someone pulling loose a common neutral (grounded conductor) and creating a 240V series circuit is highly at risk. Another factor is that many times the installers may use two different sized conductors which makes it hard to compress the proper torque on conductors of different circular mils thus potentially leaving one with a poor connect when it is really needed.......and I wont elaborate on that.

While the manufacturers have been clear on this via UL 67 for many years and with talking with Eaton quite a bit, the practice should be discontinued and actually why it made it into the 2002 NEC directly to help encourage what manufacturers already want.



Paul W. Abernathy
Reply With Quote
  #7  
Old 5/3/10, 7:01 PM
Mark Thiltgen Mark Thiltgen is offline
InterNACHI Member
 
Join Date: Feb 2009
Location: St Michael, MN
Posts: 73
Default Re: What would happen?

Thanks everyone, I can now give a fairly intelligent answer when they ask me about what would happen. I sometimes would do a nice little jig and try to distract them but NO MORE!
Reply With Quote
  #8  
Old 5/3/10, 8:00 PM
Mark Thiltgen Mark Thiltgen is offline
InterNACHI Member
 
Join Date: Feb 2009
Location: St Michael, MN
Posts: 73
Default Re: What would happen?

When did they decide the neutrals and grounds should not go under the same teminal? I see in Pauls answer that in 2002 the NEC changed this. Is that when they officially put it in writing that they could not go together under one terminal? thanks again
Reply With Quote
  #9  
Old 5/3/10, 8:23 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What would happen?

Quote:
Originally Posted by mthiltgen View Post
When did they decide the neutrals and grounds should not go under the same teminal? I see in Pauls answer that in 2002 the NEC changed this. Is that when they officially put it in writing that they could not go together under one terminal? thanks again
\

As I stated in a previous post it has always been part of the UL listing of the equipment. By inserting it directly into the NEC wording it will be read by a much broader audience of electricians. Many electricians had never even read a UL listing standard.
Reply With Quote
  #10  
Old 5/3/10, 9:37 PM
Mark Thiltgen Mark Thiltgen is offline
InterNACHI Member
 
Join Date: Feb 2009
Location: St Michael, MN
Posts: 73
Default Re: What would happen?

Thank you Robert, right in front of me!
Reply With Quote
  #11  
Old 5/3/10, 10:03 PM
James E. Braun, CMI's Avatar
James E. Braun, CMI James E. Braun, CMI is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Jefferson City, MO
Posts: 6,945
Default Re: What would happen?

I just ask electricians, why do they have all those screws on a buss bar if you are not suppose to use them?

Their reaction is
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
What happen here ? bhartley Structural Inspections 5 9/27/09 9:09 AM
Insurance ? What can Happen to YOU ! phughes Miscellaneous Discussion for Inspectors 12 4/23/06 12:43 PM


All times are GMT -4. The time now is 7:33 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts