Default Re: What would requirements be???

i agree with the last two. why is everyone so interested in inspecting to code, when that is not the job of the home inspector. sure, it is good to know some of those things for guidance, but I wouldn't report that something is or isn't a code violation, unless I was trained to do so. just a comment. I would report that there is no light or outlet and be done with it.

I do agree that this is a good example though of whether an outlet is necessary though.
Reply With Quote
  #17  
Old 4/11/08, 9:37 AM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,950
Default Re: What would requirements be???

I've come to appreciate that "code"....as a basic minimum standard....can be widely interpretted.

The code books, themselves, say so. They leave it to the discretion of every AHJ tasked with enforcing it to interpret it in the manner that is necessary to preserve the intent...within their jurisdiction.

The code books tell the designers and the technicians that....even when an AHJ says it is "okay"....they can still be held liable. This is why they have a duty to appeal "bad" interpretations since, even if they comply, it is still their necks on the line.

Likewise, with us.

The intent of the provision is what is important to us...just as it is to the AHJ. If a lack of available receptacles can cause our client to overuse extension cords and risk their safety....regardless of what one or two "experts" might say....our duty is to call it out.

That is what the code books say to do.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
  #18  
Old 4/11/08, 2:29 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What would requirements be???

James, you are doing what many AHJs do. You are imposing your opinion as fact. Sorry, but you are incorrect that this area REQUIRES a receptacle.

You can suggest it, or say it is a good idea, which I have NO problem with, but that was NOT the original question.
In fact, your profession is more stating opinion than anything else. This ideology is repeated time and time again: you guys don't do code.

The original question was is a receptacle required. NO, it is NOT.
I also repeat, I make this statement strictly from a code standpoint.
You find me a code that says it is required and I'll read it.


Quote:
The code books tell the designers and the technicians that....even when an AHJ says it is "okay"....they can still be held liable.
I am curious as to what "code book" you found this in.
Reply With Quote
  #19  
Old 4/11/08, 2:30 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What would requirements be???

Quote:
Originally Posted by mmatalik
why is everyone so interested in inspecting to code, when that is not the job of the home inspector.
Michael, quite the opposite. Most of you HIs are saying code is not the issue. I am not an HI.
I am merely make code references for clarification and factual purposes.
Reply With Quote
  #20  
Old 4/11/08, 2:55 PM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: What would requirements be???

At a minuim it is a hallway. It requires switched controled lighting outlet inside.

Also, there should be a switch for a light outside.

tom
Reply With Quote
  #21  
Old 4/11/08, 2:57 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What would requirements be???

A hallway??????
Reply With Quote
  #22  
Old 4/11/08, 3:01 PM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: What would requirements be???

Quote:
Originally Posted by Speedy Petey
A hallway??????
http://www.merriam-webster.com/dictionary/hallway

http://www.merriam-webster.com/dictionary/foyer

At a minimum.

tom

Last edited by tdietrich1; 4/11/08 at 3:08 PM..
Reply With Quote
  #23  
Old 4/11/08, 4:15 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,950
Default Re: What would requirements be???

Quote:
Originally Posted by Speedy Petey


I am curious as to what "code book" you found this in.
NEC, Annex G, 80.29



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
  #24  
Old 4/11/08, 4:50 PM
klott's Avatar
klott klott is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: monroe, ga
Posts: 8,707
Default Re: What would requirements be???

Speedy,I did not know that you're not a HI, mighty nice of you to come here and help out. Ken
Reply With Quote
  #25  
Old 4/11/08, 5:26 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What would requirements be???

Quote:
Originally Posted by jbushart
NEC, Annex G, 80.29
And here I thought you guys didn't do code.
Reply With Quote
  #26  
Old 4/11/08, 5:32 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,950
Default Re: What would requirements be???

Quote:
Originally Posted by Speedy Petey
And here I thought you guys didn't do code.
We do....but we do it our own way.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
  #27  
Old 4/11/08, 6:10 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What would requirements be???

That room needs a receptacle every couple feet of wall space, a light, a battery backed up emergency light, battery backed up exit signs, grab bars, luminescent egress path tape on the floor, smoke detector, rate of rise detector, fire alarm horn and strobe, fire alarm manual pull station, smoke evacuation fans, audible exit instruction annunciator, anthrax detector, hitching post for bomb sniffing dog, metal detector at the door, and lever type locksets. That ought to cover it.

[Don't get too wacky. It's a porch. It needs very minimal lighting of some sort to satisfy the building code and that's it. If the door going into the house has a window in it, there would be enough light shining through it from the light inside to satisfy the building code requirements, minimal as they are. ]
Reply With Quote
  #28  
Old 4/11/08, 6:12 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,049
Default Re: What would requirements be???

You forgot the trap door for the tax assessor.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

[/I]
Reply With Quote
  #29  
Old 4/11/08, 8:21 PM
sfalvey sfalvey is offline
InterNACHI Member
 
Join Date: May 2005
Location: Newbury, NH
Posts: 393
Default Re: What would requirements be???

As always, I appreciate the input and conversation.

Thanks for the participation.



Scott Falvey
Clear View Home Inspections, LLC
Newbury, NH
NACHI#05051292
www.clearviewhomeinspectionsllc.com
Reply With Quote
  #30  
Old 4/12/08, 12:57 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What would requirements be???

As for the code issue, I am not sure there is a violation given what I see here.

At the risk of another red box I will say again, why do you care what the code says. If it is going to be a convenience/design issue for the customer, cite it. You are a home inspector, not a code inspector.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Florida Licensing Bill - Action Soon jburkeson1 Legislation, Licensing & Legal Issues for Inspectors 250 7/1/10 4:50 PM
Liability question jcahill Legislation, Licensing & Legal Issues for Inspectors 30 8/24/08 4:10 PM
Importance of the AHJ check mcyr General Inspection Discussion 6 2/21/07 8:18 PM


All times are GMT -4. The time now is 5:11 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts