Quote:
Originally Posted by gbeaumont View Post
LOL, sorry Mike, just couldn't resist

BTW there is obviously a problem eilther with the way the outlet is wired or a grounding problem in the appliance.

Regards

Gerry
Close Gerry. Very close.

BTW-I cleaned my fingernails

You win the next clue.
Attached Thumbnails
would-you-do-100_1300-small-.jpg.JPG
Views:	33
Size:	36.1 KB
ID:	29249  



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
Find an InterNACHI certified Virginia Home Inspector (and anywhere else in North America)
  #17  
Old 6/13/09, 6:29 PM
Gerry Beaumont's Avatar
Gerry Beaumont Gerry Beaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 5,749
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: What would you do?

HI Mike

I see your reversed polarity and raise you one false ground, do I win yet??

Regards

Gerry



Virtue is more to be feared than vice, because its excesses are not subject to the regulation of conscience.
Adam Smith (1723-1790)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106
Reply With Quote
  #18  
Old 6/13/09, 6:37 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: What would you do?

Quote:
Originally Posted by gbeaumont View Post
HI Mike

I see your reversed polarity and raise you one false ground, do I win yet??

Regards

Gerry
You're well along the way to solving the case detective Beaumont.

They plugged the three prong refer into the cheater and then the 2-wire extension cord and into the reverse polarity outlet.

I didn't measure the available fault current on the refrigerator but I bet it was high. I would want to touch that fridge standing on the carpet which is on a grade slab.

What did I do next?

Or what would you do?



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #19  
Old 6/13/09, 6:39 PM
Gerry Beaumont's Avatar
Gerry Beaumont Gerry Beaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 5,749
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: What would you do?

Quote:
Originally Posted by mlarson View Post

Or what would you do?
Run , or unplug the extension cord

Regards

gerry



Virtue is more to be feared than vice, because its excesses are not subject to the regulation of conscience.
Adam Smith (1723-1790)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106
Reply With Quote
  #20  
Old 6/13/09, 6:39 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,744
Default Re: What would you do?

Quote:
Originally Posted by mlarson View Post
What did I do next?
Get a drink straight from the faucet while holding onto the fridge?



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #21  
Old 6/13/09, 6:41 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: What would you do?

Quote:
Originally Posted by gbeaumont View Post
Run , or unplug the extension cord

Regards

gerry
Well I was alone at the inspection and there were items in the fridge.

House was under contract and staged but no one living there.



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #22  
Old 6/13/09, 7:38 PM
Gerry Beaumont's Avatar
Gerry Beaumont Gerry Beaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 5,749
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: What would you do?

Quote:
Originally Posted by mlarson View Post
Well I was alone at the inspection and there were items in the fridge.

House was under contract and staged but no one living there.
well if I were being really kind (which generaly I'm not) I might have just plugged the extension cord into a properly wired outlet. MAYBE

Gerry



Virtue is more to be feared than vice, because its excesses are not subject to the regulation of conscience.
Adam Smith (1723-1790)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106
Reply With Quote
  #23  
Old 6/13/09, 7:50 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What would you do?

You cannot assume there is voltage present on the refrigerator just from your NC tester. There are many instances where an NC tester will sound off when there is no voltage present. Try it sometime on a metal light fixture connected to a two wire system. Or just holding it close to a two wire, ungrounded receptacle.

Once you get the ring from your NC tester, the next step would be to pull out an analog tester, bring in a known ground, and check for voltage.

Of course I know this is not in the scope of an inspection, so the next step might involve a sparky. Even if the fridge cabinet is not energized, the metal appliances plugged into a two wire system should be addressed.
Reply With Quote
  #24  
Old 6/13/09, 8:00 PM
Michael Roberson's Avatar
Michael Roberson Michael Roberson is offline
InterNACHI Member
 
Join Date: May 2008
Location: Scottville, Mi
Posts: 931
Default Re: What would you do?

First I would run around on the carpet in my socks, and see if I can ground myself to the fridge.

Then I would show them this picture, and remind them never to plug anything bigger than a lamp into an extension cord.
Attached Thumbnails
would-you-do-burnt-cord.jpg  
Reply With Quote
  #25  
Old 6/14/09, 9:54 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: What would you do?

Quote:
Originally Posted by brian winkle View Post
You cannot assume there is voltage present on the refrigerator just from your NC tester. There are many instances where an NC tester will sound off when there is no voltage present. Try it sometime on a metal light fixture connected to a two wire system. Or just holding it close to a two wire, ungrounded receptacle.
That is correct.

What I decided to do was this.

I didn't have my meter with me and I not wanting to leave this potentially hazardous situation the way it was.

I removed the 2-wire cheater and 2-wire cord and pulled the refrigerator fridge out far enough to plug it in normally.

This was the result.
Attached Thumbnails
would-you-do-100_1316-small-.jpg.JPG
Views:	22
Size:	23.5 KB
ID:	29258  



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #26  
Old 6/14/09, 10:52 AM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 2,442
Default Re: What would you do?

Your the MAN Micheal ! I bet you kept the cheater didn't you. come on now we know you did. Put it the old tool pouch thinking i can use that someday . lololol
Reply With Quote
  #27  
Old 6/14/09, 11:14 AM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,098
Default Re: What would you do?

When Texas adopted a new SOP in Feb of this year many of us scoffed at the new requirement to "Report as deficient...appliances and metal pipes that
are not bonded or grounded". I have found two range hoods and one dishwasher in the last 3 months that were not bonded and grounded. My inspection protocol for this has added about 2-3 minutes to my inspection time.
Reply With Quote
  #28  
Old 6/14/09, 2:42 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: What would you do?

Quote:
Originally Posted by wwilson3 View Post
Your the MAN Micheal ! I bet you kept the cheater didn't you. come on now we know you did. Put it the old tool pouch thinking i can use that someday . lololol
Nope

I coiled it up and put it under the bar.
Attached Thumbnails
would-you-do-100_1311-small-.jpg.JPG
Views:	23
Size:	50.4 KB
ID:	29261  



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
Find an InterNACHI certified Virginia Home Inspector (and anywhere else in North America)
  #29  
Old 6/15/09, 12:50 PM
George P. Wells's Avatar
George P. Wells George P. Wells is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Michigan
Posts: 367
Send a message via Skype™ to gwells
Default Re: What would you do?

Quote:
Originally Posted by mlarson View Post
I didn't measure the available fault current on the refrigerator but I bet it was high.
The safe thing to do would be to assume that the AFC is 10kA at all points in a house.

It would be difficult to determine the AFC at the refrigerator because you would need to know the kVA rating and impedance (Z%) of the transformer, and the combined impedance of service conductors and branch circuit conductors to determine the available fault current.

With rare exceptions, residential systems are approximately 10k AFC measured at the transformer bushings. The AFC will be less at the refrigerator because of the added impedance of the conductors between the transformer and the refrigerator.

Electric utility companies are often required to ensure an AFC of 10kA or less for residential single phase services because most residential electrical equipment is rated for 10k AFC.
Reply With Quote
  #30  
Old 6/15/09, 12:54 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: What would you do?

George. I meant to say leakage current not fault current. Thanks.



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 4:27 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts