Do you keep extra panel covers as well?
Reply With Quote
Find an InterNACHI certified District Of Columbia Home Inspector (and anywhere else in North America)
  #17  
Old 5/1/09, 8:25 AM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 7,642
Default Re: Would you remove this cover?

Quote:
Originally Posted by bdoles2 View Post
Do you keep extra panel covers as well?
I keep a tiny Electrician in the back of the truck to fix things during the inspection. He gets along with the tiny foundation and roofer guys. However the tiny plumber had to be let go he showed crack.
Reply With Quote
  #18  
Old 5/1/09, 8:54 AM
bdoles2's Avatar
bdoles2 bdoles2 is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Atlanta, GA
Posts: 3,071
Please Note: bdoles2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Would you remove this cover?

In a way, Wayne makes a good point. (not sure if you meant it that way)

Where do you stop? Do you replace the TPRV if it's faulty? Do you replace or repair a vent boot if it's cracked? Do you install a ground rod if one is missing and is required? Do you properly rebuild the deck if it's not supported correctly?

Point is, if you repair one defect - they may expect you to repair them all. Even a small one like improper panel cover screws.
Reply With Quote
  #19  
Old 5/1/09, 9:24 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: Would you remove this cover?

Quote:
Originally Posted by bdoles2 View Post
Do you keep extra panel covers as well?
Sorry if that offends you in some way.



He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father

The democracy will cease to exist when you take away from those who are willing to work and give to those who would not. Thomas Jefferson

Never underestimate the difficulty of changing false beliefs by facts.
- Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
and
Minnesota Home Inspector

Reply With Quote
  #20  
Old 5/1/09, 9:26 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: Would you remove this cover?

Quote:
Originally Posted by wwilson3 View Post
I keep a tiny Electrician in the back of the truck to fix things during the inspection. He gets along with the tiny foundation and roofer guys. However the tiny plumber had to be let go he showed crack.
More likely you have cards that say "George Bush did this" to put on every defect you find.



He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father

The democracy will cease to exist when you take away from those who are willing to work and give to those who would not. Thomas Jefferson

Never underestimate the difficulty of changing false beliefs by facts.
- Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
and
Minnesota Home Inspector

Reply With Quote
  #21  
Old 5/1/09, 9:28 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: Would you remove this cover?

Quote:
Originally Posted by bdoles2 View Post
In a way, Wayne makes a good point. (not sure if you meant it that way)

Where do you stop? Do you replace the TPRV if it's faulty? Do you replace or repair a vent boot if it's cracked? Do you install a ground rod if one is missing and is required? Do you properly rebuild the deck if it's not supported correctly?

Point is, if you repair one defect - they may expect you to repair them all. Even a small one like improper panel cover screws.
No to all the above.

You have my permission to put all the pointy headed screws back into the panel covers you want.



He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father

The democracy will cease to exist when you take away from those who are willing to work and give to those who would not. Thomas Jefferson

Never underestimate the difficulty of changing false beliefs by facts.
- Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
and
Minnesota Home Inspector

Reply With Quote
  #22  
Old 5/1/09, 10:23 AM
bdoles2's Avatar
bdoles2 bdoles2 is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Atlanta, GA
Posts: 3,071
Please Note: bdoles2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Would you remove this cover?

Quote:
Originally Posted by mlarson View Post
Sorry if that offends you in some way.
Sorry you concluded that I was offended. You know that I don't pay any attention to what you have to say!
Reply With Quote
  #23  
Old 5/1/09, 10:53 AM
jcundiff's Avatar
jcundiff jcundiff is offline
Active Poster
 
Join Date: May 2005
Location: Fairview Park, OH
Posts: 251
Please Note: jcundiff is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Would you remove this cover?

Why wouldn't an HI take that cover off? It is certainly readily accessible and He'd certainly have cause to investigate.
Reply With Quote
  #24  
Old 5/1/09, 11:02 AM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,490
Default Re: Would you remove this cover?

Would you remove the cover from a Fed Pacific panel full of loose stablocks? Many (myself, included) will not. Without knowing what is behind it, how can you determine that it is safe to remove?

The unsafe modifications made to the original equipment that can be readily observed is enough to call in a licesned electrician to repair or replace....no matter what is behind the sheet metal and drywall screws.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Inspecting in Aurora, Branson, Carthage, Granby, Joplin, Kimberling City, Monett, Mount Vernon, Neosho, Nixa, Purdy, Reed Spring, Republic, Springfield and surrounding areas.

Reply With Quote
  #25  
Old 5/1/09, 11:16 AM
klott's Avatar
klott klott is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: monroe, ga
Posts: 8,709
Default Re: Would you remove this cover?

Quote:
Originally Posted by bkelly2 View Post
Jackpot.
Crackpot.



"It's not what you believe that matters...it matters what you believe!"
Reply With Quote
  #26  
Old 5/1/09, 11:17 AM
klott's Avatar
klott klott is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: monroe, ga
Posts: 8,709
Default Re: Would you remove this cover?

Quote:
Originally Posted by mlarson View Post
More likely you have cards that say "George Bush did this" to put on every defect you find.
Ouch!



"It's not what you believe that matters...it matters what you believe!"
Reply With Quote
  #27  
Old 5/1/09, 11:24 AM
klott's Avatar
klott klott is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: monroe, ga
Posts: 8,709
Default Re: Would you remove this cover?

Quote:
Originally Posted by jpope View Post
Would you remove this cover?
Why risk it when it has to be written up anyway?



"It's not what you believe that matters...it matters what you believe!"
Reply With Quote
  #28  
Old 5/1/09, 12:04 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Would you remove this cover?

The panel was over-sized James, so replacing it was easy, The drywall screws were in the drywall, not the enclosure.

Quote:
Originally Posted by rray View Post
I don't even know what it is since it's labeled "sub panel." What the heck is a sub panel?
That was actually (almost) my reasoning for removing this cover. I would have hated to refer an electrician to this, only to find that it was simply covering a hole in the wall.

I'm not necessarily saying it was the "right" call, but it was "my" call.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
Find an InterNACHI certified District Of Columbia Home Inspector (and anywhere else in North America)
  #29  
Old 5/1/09, 12:29 PM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Lake Forest, Il
Posts: 1,117
Default Re: Would you remove this cover?

Yes... I would open the sub. Along with the obvious hazard of a FPE Stab-Lok, I would state that the cover should have been a properly UL listed panel cover. That's if the buyer wasn't worried about the FPE.

Jeff



Jeff Wicklander
Corwick Home Services

Join my business on Facebook
Reply With Quote
  #30  
Old 5/1/09, 9:43 PM
RAY THOROMAN RAY THOROMAN is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Gainesville, GA
Posts: 612
Default Re: Would you remove this cover?

Quote:
Originally Posted by jpope View Post
The panel was over-sized James, so replacing it was easy, The drywall screws were in the drywall, not the enclosure.



That was actually (almost) my reasoning for removing this cover. I would have hated to refer an electrician to this, only to find that it was simply covering a hole in the wall.

I'm not necessarily saying it was the "right" call, but it was "my" call.


Can't say yes or no one this one. I'd likely make that decision in the field. Depends on many variables.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Electric Panel dmozzillo Electrical Inspections 26 1/26/09 2:18 PM
It's not necassary to remove Electrical Panel Cover. dvalley Electrical Inspections 13 7/3/07 4:22 PM
Live weather cover jnicholson Electrical Inspections 13 10/31/06 11:31 PM


All times are GMT -4. The time now is 6:15 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts