Default What is wrong with this electrical panel?

http://www.nachi.org/nastypanel2006.htm



Nick Gromicko, Certified Master Inspector

Find a Home Inspector
"Just as iron sharpens iron, one man sharpens another." Proverbs 27:17
Reply With Quote
  #2  
Old 2/26/06, 1:28 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What is wrong with this electrical panel?

Thanks for posting this mess Nick, I built around 50 defects into the panel and although it may be difficult to tell which ones they are, the time when we can look at it in person will be the best way for me to describe what I did to this nice new equipment!
Reply With Quote
  #3  
Old 2/26/06, 1:48 PM
Leonard E. Ungar's Avatar
Leonard E. Ungar Leonard E. Ungar is offline
InterNACHI Member
 
Join Date: Oct 2003
Location: Bayport, NY
Posts: 351
Default Re: What is wrong with this electrical panel?

JoE;
It might take some time to wright up all the defects, But it is a good learning curve.
Keep up the good work.
Was nice seeing you again at the convention, Glad they gave you a repreeve

Regards Len
Reply With Quote
  #4  
Old 2/26/06, 1:56 PM
Nick Gromicko's Avatar
Nick Gromicko Nick Gromicko is offline
InterNACHI Member
 
Join Date: Aug 2002
Location: Valley Forge, PA
Posts: 30,613
Default Re: What is wrong with this electrical panel?

Joe, is this the same panel you shipped to me?



Nick Gromicko, Certified Master Inspector

Find a Home Inspector
"Just as iron sharpens iron, one man sharpens another." Proverbs 27:17
Reply With Quote
  #5  
Old 2/26/06, 2:15 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What is wrong with this electrical panel?

Quote:
Originally Posted by gromicko
Joe, is this the same panel you shipped to me?
Yes it is Nick, and Thanks Len, I am happy to be back!

If any NYS Full HI Provider needs an Instructor I am recognized as a NYS Technical Instructor and can lend a hand and present a 6 hour electrical seminar, maybe I can come to LI again, my old home town was Corona, NY.
Reply With Quote
  #6  
Old 2/26/06, 4:19 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: What is wrong with this electrical panel?

Hey Guys,

I most certainly think every HI here should get a pad out, get a nice sharp pencil and look at each image one at a time.

Not every defect will be seen as images do not always tell the whole story but I challenge you all to write a list of defects from image to image and POST them here.

Nice work JOE.......some are obvious and some are not so obvious...thats the best way to train.....

I will most certainly start my list.....always easier when you are making the defect than trying to notice them.......nice learning experience for members.



Paul W. Abernathy
Reply With Quote
  #7  
Old 2/26/06, 4:20 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: What is wrong with this electrical panel?

USe the following format....

IMAGE # 1- Defects
A.)
B.)
C.)
and so on..........

P.S. I would say # 14 is my favorite image.....

ACTUALLY......would it be considered for some CE points IF you did the list and sent it to ME and JOE to review them versus posting here....what do you say NICK.....



Paul W. Abernathy

Last edited by pabernathy; 2/26/06 at 4:24 PM..
Reply With Quote
  #8  
Old 2/26/06, 4:26 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,206
Default Re: What is wrong with this electrical panel?

Joe you are right, you have to see most of these types of electrical problems in person, pictures just don't have all the right angles and distances. It would take awhile to study the panel in order to locate that many defects.

Looks like that panel would be referred to a licensed electrician by any home inspector even with just a quick glance. Many inspectors do not believe in listing every defect when a certain number per system has been found, they just refer the whole system to the tradesman. There are pros and cons to this method. I have found that contractors usually only repair the exact problems listed in a report and do not go any further. Usually they even leave out a few in the report and add a new one or two.

The one I built is a tricky one for the most part, many of the problems would be missed by a lot of inspectors and a few would be missed by every inspector including myself.

The reason that I made mine somewhat tricky is because everyone that examines it already has the advantage of knowing it has been preloaded with problems.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #9  
Old 2/26/06, 4:34 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: What is wrong with this electrical panel?

Actually I think it is just good practice to try...most certainly you will stop at some point and simply refer it on but I think it is nice to play with for new inspectors and even some seasoned ones to SEE if they can find the defects...

Sure we wont see them all....but many are obvious and those are the important ones....when someone starts missing the obvious is when we start to worry...lol..

I must say however Joe....could you not find any RUST to smear on it to make it look more realistic ...thehehehe...we need some nasty, rusty, cobweb filled ones also...lol......Where Jeff Pope when you need him..lol



Paul W. Abernathy
Reply With Quote
  #10  
Old 2/26/06, 6:31 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What is wrong with this electrical panel?

Thanks Bruce.

Paul: Rusty buckets are easy to find and list, and the panel I built was on the spur of the moment during the two days my wife threw me out because she was the contractor for the kitchen and bathroom remodel. Why after traveling overnight now still on the Amtrak to be into Boston after 24 hours, I was told to get out in the morning so the painters could finish their work!

As long as the Lady is happy that's what counts and she surprised me saying we would go to Italy again this Summer.
Reply With Quote
  #11  
Old 2/26/06, 6:55 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What is wrong with this electrical panel?

OK, first the directory is not complete. We should be sure that it is accurate and specific, if not call it out as a defect. The other information on this glued page is also very important, and it would be my first discussion and here we will find the instructions, one of which said only use my breakers Dude!



#13.
Reply With Quote
  #12  
Old 2/26/06, 6:59 PM
Nick Gromicko's Avatar
Nick Gromicko Nick Gromicko is offline
InterNACHI Member
 
Join Date: Aug 2002
Location: Valley Forge, PA
Posts: 30,613
Default Re: What is wrong with this electrical panel?

Give me more!



Nick Gromicko, Certified Master Inspector

Find a Home Inspector
"Just as iron sharpens iron, one man sharpens another." Proverbs 27:17
Reply With Quote
  #13  
Old 2/26/06, 7:04 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What is wrong with this electrical panel?

Will do Nick, can you take some real close ups of the page above, this way we can discuss the instructions, not saying that the HI should list all only to have them be aware!
Reply With Quote
  #14  
Old 2/26/06, 7:29 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What is wrong with this electrical panel?

#15


The two lower GFCI CB's and the two AFCI's on the right are not of the same manufacturer and the use of the wire handle tie does what?

It does nothing it was just put there to make it clear that the use of anything other that an "identified" handle tie is not permitted.
Reply With Quote
  #15  
Old 2/26/06, 7:46 PM
jclark1's Avatar
jclark1 jclark1 is offline
Active Poster
 
Join Date: Nov 2005
Location: Vashon, Wa
Posts: 644
Please Note: jclark1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What is wrong with this electrical panel?

Kind of like shooting fish in a barrell. I'll start w/ #1.
1) Bare (#6 or#8?) too long, not installed in a workmanlike manner. Too close to energized parts.
2) Black conductor not identified as a grounded conductor (can be id'd w/ white tape if #6 or larger). Can't tell what size it is from pic.
3) Same as above connected to ground or neutral lug (can't tell from pic#1) on the right side of the pic.
4) 100 amp providing overcurrent protection for what looks like #6 or #8 (can't tell from pic) copper wire.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
NACHI.TV producing "Panel from Hell" show: How to inspect an electrical service panel gromicko Miscellaneous Discussion for Inspectors 17 12/5/07 2:32 PM
City electrical inspector says move the meter and panel cbottger Electrical Inspections 9 4/4/07 8:59 PM
Copper Tie in Electrical Panel Jan Lombard Electrical Inspections 17 3/29/07 11:36 PM
Electrical Panel Installation csteele Electrical Inspections 12 9/19/06 9:30 AM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 5:12 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts