Question Wrong panel enclosure screws

I wont put the wrong panel screws back in ( pointed).
At a recent inspection, the Realtor got very huffy with me and demanded i put the home " back in the condition i found it" .

I flat out refused to put them back in, especially since the dead front cover was also missing breaker knockouts- so no substantial protection anyway.

My question is: do i have to put them back in if i feel it is unsafe?

Is there a law i can reference, i don't quite recall exactly but i remember something to that effect.




Joseph Tribuzio 708 453 8447
Tribuzio Home Inspection Services

CHICAGOLAND, ILLINOIS
www.thishomeinspector.com

ID# NACHI07062507

IL Lic#450.003128

Radon lic# RNIT2008216
Home Inspector Pro Software

HIP Web Hosting


Reply With Quote
Need a home inspection in Utah? Check out InterNACHI's listing of Utah certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 1/21/11, 6:32 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Wrong panel enclosure screws

IMO unless you want to make a repair and accept the liability related to that repair I would put it back the same way I found it.
Reply With Quote
  #3  
Old 1/21/11, 6:37 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Wrong panel enclosure screws

So if they were all pointed, would you leave the cover completely off to prove your point that it's a hazard and create a greater hazard?

If you see a wire could be damaged by a particular screw, leave that one out. Otherwise, put them in to secure the cover to prevent someone from getting hurt.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com



Last edited by jfunderburk; 1/21/11 at 11:18 PM..
Reply With Quote
  #4  
Old 1/21/11, 6:41 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Wrong panel enclosure screws

Might be a good idea to carry a few with you.
If there were no wires in the way they should always be put back to secure the panel cover.

Example:
Ledger board is nailed in so I will remove them.
Reply With Quote
  #5  
Old 1/21/11, 6:47 PM
Joseph Tribuzio's Avatar
Joseph Tribuzio Joseph Tribuzio is offline
InterNACHI Member
 
Join Date: Jul 2007
Location: Harwood Heights, IL 60706
Posts: 708
Default Re: Wrong panel enclosure screws

OK, thanks guys, i see your points - but the dead front was missing many breaker knockouts. So it was unsafe in any case.




Joseph Tribuzio 708 453 8447
Tribuzio Home Inspection Services

CHICAGOLAND, ILLINOIS
www.thishomeinspector.com

ID# NACHI07062507

IL Lic#450.003128

Radon lic# RNIT2008216
Home Inspector Pro Software

HIP Web Hosting


Reply With Quote
  #6  
Old 1/21/11, 7:18 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Wrong panel enclosure screws

You should always leave the property in the same - or better - condition than it was when you arrived. To leave the cover off, the panel is less safe.

If I felt that the panel cover could not be safely replaced, I would have called an electrician myself.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #7  
Old 1/22/11, 8:20 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Wrong panel enclosure screws

I have on occasion "blunted" a pointy screw for my own safety.

I also carry a few extra panel screws with me.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #8  
Old 1/22/11, 9:00 AM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,107
Default Re: Wrong panel enclosure screws

I agree with Joe.
What I do is tell me client,take a picture of the screws and replace them back on the dead front in the panel making sure no wires are near the screws.
Take another picture of the panel with knock outs missing and carry on with inspection.Then eye roll my eyes at my clients.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #9  
Old 1/22/11, 3:44 PM
Jackie R. Minchey Jackie R. Minchey is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Rockvale, Tn
Posts: 19
Default Re: Wrong panel enclosure screws

I recall a couple of years ago i was removing a panel screww that happened to be sharp pointed, evidently when it was installed, it damaged the sheathing on a hot #12 wire, but the arc hard created a small valley in the screw that was not touching..when I started backing the screw out...pow, it tripped main breaker, fried the circuits on my electric screwdriver and shot it across the garage, luckily had on rubber soled shoes! I did not replace that particular screw, but took photo, then made sure that the remaining screws did not touch wires when i replaced the panel...then notified everyone at the end of the dangers...if someone lese would have done that without rubber soled shoes, could have been a serious accident! What's worse, it was a new construction inspect!
Reply With Quote
  #10  
Old 1/24/11, 12:21 AM
Joseph Tribuzio's Avatar
Joseph Tribuzio Joseph Tribuzio is offline
InterNACHI Member
 
Join Date: Jul 2007
Location: Harwood Heights, IL 60706
Posts: 708
Default Re: Wrong panel enclosure screws

Quote:
Originally Posted by mlarson View Post
I have on occasion "blunted" a pointy screw for my own safety.

I also carry a few extra panel screws with me.
THANK YOU MICHEAL , thats a really good idea. Silly question, but are all panel screws same thread and size?




Joseph Tribuzio 708 453 8447
Tribuzio Home Inspection Services

CHICAGOLAND, ILLINOIS
www.thishomeinspector.com

ID# NACHI07062507

IL Lic#450.003128

Radon lic# RNIT2008216
Home Inspector Pro Software

HIP Web Hosting


Reply With Quote
  #11  
Old 1/24/11, 12:25 AM
Joseph Tribuzio's Avatar
Joseph Tribuzio Joseph Tribuzio is offline
InterNACHI Member
 
Join Date: Jul 2007
Location: Harwood Heights, IL 60706
Posts: 708
Default Re: Wrong panel enclosure screws

Quote:
Originally Posted by jminchey View Post
I recall a couple of years ago i was removing a panel screww that happened to be sharp pointed, evidently when it was installed, it damaged the sheathing on a hot #12 wire, but the arc hard created a small valley in the screw that was not touching..when I started backing the screw out...pow, it tripped main breaker, fried the circuits on my electric screwdriver and shot it across the garage, luckily had on rubber soled shoes! I did not replace that particular screw, but took photo, then made sure that the remaining screws did not touch wires when i replaced the panel...then notified everyone at the end of the dangers...if someone lese would have done that without rubber soled shoes, could have been a serious accident! What's worse, it was a new construction inspect!
good example. The screws I were looking at were kinda long and the panel wiring was all over, so hesitant to stick my hand in there and start moving wires around ya know? Mine was a house flipper. total cheap rehab crap workmanship all over the place.




Joseph Tribuzio 708 453 8447
Tribuzio Home Inspection Services

CHICAGOLAND, ILLINOIS
www.thishomeinspector.com

ID# NACHI07062507

IL Lic#450.003128

Radon lic# RNIT2008216
Home Inspector Pro Software

HIP Web Hosting


Reply With Quote
  #12  
Old 1/25/11, 2:46 PM
agallatin agallatin is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Trail BC
Posts: 194
Default Re: Wrong panel enclosure screws

I have seen many panels where the original screws were in the dead front , but the threads were stripped and half the dead front was hanging out enouugh that you could stick your hand between the dead front and the panel . My own panel was like that after the electrician left .



galaxyhomeinspections.com



An amateur built the Ark !
Professionals built the Titanic !
Reply With Quote
  #13  
Old 1/26/11, 5:20 PM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,107
Default Re: Wrong panel enclosure screws

That is why I do what I said I do. Including making sure the screws I pull out go into the same place.
If you change them and screw up the threads you could be creating a problem.
If you drop a screw behind something, carry one long screw driver that has been magnetized by a speaker.
If you can't get it [note it on the report] and tell the Home owner.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
Need a home inspection in Utah? Check out InterNACHI's listing of Utah certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 1/27/11, 4:20 PM
agallatin agallatin is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Trail BC
Posts: 194
Default Re: Wrong panel enclosure screws

Good point Kevin ! I'm going to get one of those screwdrivers .



galaxyhomeinspections.com



An amateur built the Ark !
Professionals built the Titanic !
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
100 amp Service w/new 200 amp panel mlong Electrical Inspections 10 2/7/08 2:08 AM
Free Books And Articles For Electrical jtedesco1 Electrical Inspections 14 1/6/08 6:45 PM
Panel Inspection Safety roconnor Electrical Inspections 10 9/24/06 9:02 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 7:36 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts