I wont put the wrong panel screws back in ( pointed).
At a recent inspection, the Realtor got very huffy with me and demanded i put the home " back in the condition i found it" . I flat out refused to put them back in, especially since the dead front cover was also missing breaker knockouts- so no substantial protection anyway. My question is: do i have to put them back in if i feel it is unsafe? Is there a law i can reference, i don't quite recall exactly but i remember something to that effect. Joseph Tribuzio 708 453 8447 Tribuzio Home Inspection Services CHICAGOLAND, ILLINOIS www.thishomeinspector.com ID# NACHI07062507 IL Lic#450.003128 Radon lic# RNIT2008216 Home Inspector Pro Software HIP Web Hosting |
| Need a home inspection in Utah? Check out InterNACHI's listing of Utah certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
IMO unless you want to make a repair and accept the liability related to that repair I would put it back the same way I found it.
|
|
#3
|
||||
|
||||
|
So if they were all pointed, would you leave the cover completely off to prove your point that it's a hazard and create a greater hazard?
If you see a wire could be damaged by a particular screw, leave that one out. Otherwise, put them in to secure the cover to prevent someone from getting hurt. “The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com Last edited by jfunderburk; 1/21/11 at 11:18 PM.. |
|
#4
|
||||
|
||||
|
Might be a good idea to carry a few with you.
If there were no wires in the way they should always be put back to secure the panel cover. Example: Ledger board is nailed in so I will remove them. |
|
#5
|
||||
|
||||
|
OK, thanks guys, i see your points - but the dead front was missing many breaker knockouts. So it was unsafe in any case.
Joseph Tribuzio 708 453 8447 Tribuzio Home Inspection Services CHICAGOLAND, ILLINOIS www.thishomeinspector.com ID# NACHI07062507 IL Lic#450.003128 Radon lic# RNIT2008216 Home Inspector Pro Software HIP Web Hosting |
|
#6
|
||||
|
||||
|
You should always leave the property in the same - or better - condition than it was when you arrived. To leave the cover off, the panel is less safe.
If I felt that the panel cover could not be safely replaced, I would have called an electrician myself. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#7
|
||||
|
||||
|
I have on occasion "blunted" a pointy screw for my own safety.
I also carry a few extra panel screws with me. You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell |
|
#8
|
||||
|
||||
|
I agree with Joe.
What I do is tell me client,take a picture of the screws and replace them back on the dead front in the panel making sure no wires are near the screws. Take another picture of the panel with knock outs missing and carry on with inspection.Then eye roll my eyes at my clients. THE RIGHT TRAK CIAQP, IAC2 Certified Master Inspector kwoodinspections@hotmail.com www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ www.linkedin.com/in/kevinwoodiaq OOVOO account kwoodinspections Cell: 705-971-2096 Ph : 705-946-2676 |
|
#9
|
|||
|
|||
|
I recall a couple of years ago i was removing a panel screww that happened to be sharp pointed, evidently when it was installed, it damaged the sheathing on a hot #12 wire, but the arc hard created a small valley in the screw that was not touching..when I started backing the screw out...pow, it tripped main breaker, fried the circuits on my electric screwdriver and shot it across the garage, luckily had on rubber soled shoes! I did not replace that particular screw, but took photo, then made sure that the remaining screws did not touch wires when i replaced the panel...then notified everyone at the end of the dangers...if someone lese would have done that without rubber soled shoes, could have been a serious accident! What's worse, it was a new construction inspect!
|
|
#10
|
||||
|
||||
|
THANK YOU MICHEAL , thats a really good idea. Silly question, but are all panel screws same thread and size?
Joseph Tribuzio 708 453 8447 Tribuzio Home Inspection Services CHICAGOLAND, ILLINOIS www.thishomeinspector.com ID# NACHI07062507 IL Lic#450.003128 Radon lic# RNIT2008216 Home Inspector Pro Software HIP Web Hosting |
|
#11
|
||||
|
||||
|
Quote:
Joseph Tribuzio 708 453 8447 Tribuzio Home Inspection Services CHICAGOLAND, ILLINOIS www.thishomeinspector.com ID# NACHI07062507 IL Lic#450.003128 Radon lic# RNIT2008216 Home Inspector Pro Software HIP Web Hosting |
|
#12
|
|||
|
|||
|
I have seen many panels where the original screws were in the dead front , but the threads were stripped and half the dead front was hanging out enouugh that you could stick your hand between the dead front and the panel . My own panel was like that after the electrician left .
galaxyhomeinspections.com An amateur built the Ark ! Professionals built the Titanic ! |
|
#13
|
||||
|
||||
|
That is why I do what I said I do. Including making sure the screws I pull out go into the same place.
If you change them and screw up the threads you could be creating a problem. If you drop a screw behind something, carry one long screw driver that has been magnetized by a speaker. If you can't get it [note it on the report] and tell the Home owner. THE RIGHT TRAK CIAQP, IAC2 Certified Master Inspector kwoodinspections@hotmail.com www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ www.linkedin.com/in/kevinwoodiaq OOVOO account kwoodinspections Cell: 705-971-2096 Ph : 705-946-2676 |
| Need a home inspection in Utah? Check out InterNACHI's listing of Utah certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#14
|
|||
|
|||
|
Good point Kevin ! I'm going to get one of those screwdrivers .
galaxyhomeinspections.com An amateur built the Ark ! Professionals built the Titanic ! |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| 100 amp Service w/new 200 amp panel | mlong | Electrical Inspections | 10 | 2/7/08 2:08 AM |
| Free Books And Articles For Electrical | jtedesco1 | Electrical Inspections | 14 | 1/6/08 6:45 PM |
| Panel Inspection Safety | roconnor | Electrical Inspections | 10 | 9/24/06 9:02 PM |
| Bad electrical problem | Pest Guy | Electrical Inspections | 4 | 1/20/06 9:26 PM |