Default What is wrong with this picture??

200 amp service equipment.
Attached Thumbnails
wrong-picture-12501-ne-1-ct-miami-laine-3.jpg 3.jpg
Views:	261
Size:	71.6 KB
ID:	8310  
Reply With Quote
  #2  
Old 1/11/07, 7:14 PM
rlind rlind is offline
InterNACHI Member
 
Join Date: Oct 2003
Location: Oak Park, IL
Posts: 59
Default Re: What is wrong with this picture??

Ill advised use of "double" breakers?
Reply With Quote
  #3  
Old 1/11/07, 7:26 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,730
Default Re: What is wrong with this picture??

Quote:
Originally Posted by wsiegel
What is wrong with this picture?? ...200 amp service equipment.
What is your opinion, William?



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #4  
Old 1/11/07, 7:39 PM
William E. Siegel William E. Siegel is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 1,788
Default Re: What is wrong with this picture??

That jumper connection at the top bothers me. I am assuming that it is a copper to copper splice (as the other cable is copper). The downsizing of the wire is raising a red flag to me. Wanted to see what you gents thought about it.
Reply With Quote
  #5  
Old 1/11/07, 7:47 PM
cbuell's Avatar
cbuell cbuell is offline
Active Poster
 
Join Date: Feb 2004
Location: Shorline, WA
Posts: 383
Please Note: cbuell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What is wrong with this picture??

The neutral wire is frequently smaller. Although it looks strange----GE makes a 200 amp breaker that looks like that with each of the four segments marked 200amps. I don't like it but I am told that they are OK. Let's see what Paul has to say. Could you see any "issues" with the way the splice was done?
Reply With Quote
  #6  
Old 1/11/07, 7:49 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,730
Default Re: What is wrong with this picture??

The splice looks neat enough...

I guess my old eyes can't see the reduction in conductor size.

Was the smallest conductor rated for the service amperage?



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #7  
Old 1/11/07, 7:53 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: What is wrong with this picture??

Well I will give one thing to start the ball rolling....needs to WRAP that "Grounded" conductor with some white tape for starters.

Who's Next.........can only do one at a time....

Hint.....I am seeing COLORS....thehehehe...and misleading colors at BEST...



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #8  
Old 1/11/07, 7:56 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: What is wrong with this picture??

Does that panel have a bridged bonding connection on the bottom to connect those two buss bars, and is the buss bar bonded to the panel enclosure...can't see that from the image..probably lower and on the LEFT.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #9  
Old 1/11/07, 8:00 PM
cbuell's Avatar
cbuell cbuell is offline
Active Poster
 
Join Date: Feb 2004
Location: Shorline, WA
Posts: 383
Please Note: cbuell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What is wrong with this picture??

Whooops!! Boy do I have egg on my face-----the splice is not the neutral and then I would definately have concerns about the wire size change. Sorry about that.
Reply With Quote
  #10  
Old 1/11/07, 8:04 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: What is wrong with this picture??

Quote:
Originally Posted by cbuell
Whooops!! Boy do I have egg on my face-----the splice is not the neutral and then I would definately have concerns about the wire size change. Sorry about that.
The splice looks ok, can't really tell if the conductor is smaller or possibly just a change from lets say USE to THHn or something in the panel.....would have to get a better look at it to tell.

Hey brother...no egg......you made a GREAT recovery...



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #11  
Old 1/11/07, 10:41 PM
rromoser's Avatar
rromoser rromoser is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Fishers, IN
Posts: 187
Default Re: What is wrong with this picture??

Can't see any GEC leaving the panel. It too might be near the bottom.
Reply With Quote
  #12  
Old 1/11/07, 11:57 PM
tmantsch's Avatar
tmantsch tmantsch is offline
Active Poster
 
Join Date: Dec 2004
Location: Garland, TX
Posts: 112
Please Note: tmantsch is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What is wrong with this picture??

There is no dead front cover!??

No color designation for the Neutral.
...and the orange sheathed conductors were made in China...
Reply With Quote
  #13  
Old 1/12/07, 12:04 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: What is wrong with this picture??

lol...what don't you like my colors hint....lol



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #14  
Old 1/12/07, 12:11 AM
Joe Farsetta's Avatar
Joe Farsetta Joe Farsetta is offline
ESOP Committee Member
 
Join Date: Oct 2002
Location: Pearl River, NY
Posts: 3,207
Default Re: What is wrong with this picture??

Almost looks as if uppermost red conductor to top right breaker has a damaged (or burned/melted) sheath.
Reply With Quote
  #15  
Old 1/12/07, 1:40 AM
lcapaul's Avatar
lcapaul lcapaul is offline
Active Poster
 
Join Date: Jun 2005
Location: Rathdrum, ID
Posts: 1,598
Please Note: lcapaul is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What is wrong with this picture??

None of the smaller wires coming in from the top are protected by sheathing through the clamps.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
What is wrong with this picture? mcyr General Inspection Discussion 1 7/20/07 9:08 AM
What is wrong with this picture? mcyr General Inspection Discussion 6 7/19/07 10:34 PM
What's wrong with this picture? gromicko HVAC 2 2/10/07 3:18 AM
Can someone tell me what is wrong with this picture. Can you cite a code? gromicko Electrical 24 3/24/06 4:24 PM


All times are GMT -4. The time now is 5:18 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts