I understand the Zinsco hazard summary and refferred my client to have the panel evaluated by a licensed electrician.
My question is are there any noticable issues with this panel. It is in a condo built in 1973. Panel was rated for 90 amps. Didnt see a main disconnect. Other than pointed screws at the dead front cover I didnt see any issues in the panel. The panel was quite dusty/dirty. |
|
#2
|
|||
|
|||
|
Please Note:
ccbrands1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
other than being a zinsco;
white wires used as hots should be marked with black tape. with as few of breakers there are, the 6 hand movement rule for disconnects should not apply. |
|
#3
|
||||
|
||||
|
That is not the service equipment, so there is no requirement for a service disconnect within that panel (the "six-throw" rule doesn't apply to remote panels).
Zinsco panels that are located at interior locations such as this, are less "problematic" than exterior units that are exposed to the elements. However, some Zinsco breakers will fail to open when an over-current condition occurs. This particular installation looks like it was never equipped with an exterior, hinged cover. That, I assume, is the reason for all of the lint and debris at the interior of the panel. At a minimum, I would not hesitate to recommend that it be cleaned. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#4
|
|||
|
|||
|
Please Note:
wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
If this is not the service equipment, should not the grounds and neutrals be seppartated. Also there are three ground wires on one terminal.
|
|
#5
|
||||
|
||||
|
Hope you called out that non-approved dryer vent pipe.
Will Decker, CMI ILL License # 450.0002240 Board Certified Master Inspector Decker Home Services, LLC Chicago and Northern Suburban Home Inspections Office: (847) 676-8393 Cell: (847) 609-2345 Home: (847) 673-2702 wjd@DeckerHomeServices.com www.DeckerHomeServices.com Learn, Educate, Serve and have fun doing it! |
|
#6
|
|||
|
|||
|
Quote:
InterNachi Awards Portal: http://co.nachi.org/inachiawards/ ____________________________________________ "An Education, not just an Inspection" Larry Kage, CMI Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector serving the Traverse City, Michigan area and beyond.
|
|
#7
|
|||
|
|||
|
Please Note:
brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#8
|
|||
|
|||
|
M1501.1 General.
Dryer exhaust systems shall be independent of all other systems, shall convey the moisture to the outdoors and shall terminate on the outside of the building. Exhaust ducts shall be constructed of minimum 0.016-inch-thick rigid metal, having smooth interior surfaces with joints running in the direction of air flow. Flexible transition ducts used to connect the dryer to the exhaust duct system shall be limited to single lengths, not to exceed 8 feet in length and shall be listed and labeled in accordance with UL 2158A. "not just an inspection, but an education" www.homesweethomecincinnati.com Democracy is two wolves and a lamb. Liberty is a well-armed lamb. B. Franklin |
|
#9
|
||||
|
||||
|
Quote:
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#10
|
|||
|
|||
|
Please Note:
brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Sorry for the OT postings. |
|
#11
|
||||
|
||||
|
Quote:
The kind with the 'slinky' in it presents a non-smooth surface and can lead to lint fires. Look at the box it came in. "Not approved for use with dryer vents" Simple. Will Decker, CMI ILL License # 450.0002240 Board Certified Master Inspector Decker Home Services, LLC Chicago and Northern Suburban Home Inspections Office: (847) 676-8393 Cell: (847) 609-2345 Home: (847) 673-2702 wjd@DeckerHomeServices.com www.DeckerHomeServices.com Learn, Educate, Serve and have fun doing it! |
|
#12
|
||||
|
||||
|
Quote:
I had a (small) fire in my house. It was caused by such a dryer vent pipe. "Smooth interior surface", What part of this don't you understand? Lint fires (from clothes dryers) account for 49% of all residential home fires. "Save your clients, save the world!" Hope this helps; Will Decker, CMI ILL License # 450.0002240 Board Certified Master Inspector Decker Home Services, LLC Chicago and Northern Suburban Home Inspections Office: (847) 676-8393 Cell: (847) 609-2345 Home: (847) 673-2702 wjd@DeckerHomeServices.com www.DeckerHomeServices.com Learn, Educate, Serve and have fun doing it! |
|
#13
|
|||
|
|||
|
Please Note:
brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
I am not trying to start an arguement here but I have a valid concern over the way I have been connecting dryers . If it is not safe I want to fix it. Each dryer is connected with one to three feet of aluminum flex to the hard pipe in the wall. It is the same stuff you describe with the slinky inside. Now I went out to the shed where there is a plastic bag containing "deflect-o" brand 4" flexible aluminum "air duct". It does state on the bag "Not recomended for dryer venting". It is 25 feet long. This is what I use for venting bathroon fans with 4" exhaust fittings.
Then there are some boxes from Ace Hardware that say "Flexible aluminum dryer vent duct" The stuff inside looks the same as the kind in the bag. The one in the box is made in the US, the bag comes from Canada. The box says "UL listed, but it doesn't say for what it is listed. It is only five feet long. This is what I use for dryer venting transitions. Again, it it called "Dryer vent duct" on the box. The corregated pipe you refer to, if it is what I am picturing, does not have a smooth interior surface. It is made up of aluminum in a spiral shape with grooves and ridges on the inside. It comes compressed and you stretch it out. The piece I have has no label. So I guess the part I don't understand is what I should actually be using for the transition. Is there a product that is flexible AND has a smooth interior surface? Excuse me if I sound ignorant, I am just trying to learn. I am the type of person that insists on doing a job 100% correct. |
|
#14
|
|||
|
|||
|
One simple question generates a fountain of information. Where else except on the NACHI message board.
InterNACHI Vice President, InterNACHI Editor-in-Chief, co-founder CalNACHI Author of Manual For a Happy Home & Inspect & Protect |
|
#15
|
||||
|
||||
|
Quote:
“The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| WTB: FP and Zinsco | scoslett | Electrical Inspections | 6 | 2/28/07 8:52 PM |
| Zinsco Sylvania | gkoehl | Electrical Inspections | 10 | 2/5/07 6:17 PM |
| Zinsco | cbuell | Electrical Inspections | 4 | 1/4/07 4:31 PM |
| Zinsco panel | jsmith3 | Electrical Inspections | 4 | 3/28/06 8:39 PM |