Default Zinsco

I understand the Zinsco hazard summary and refferred my client to have the panel evaluated by a licensed electrician.

My question is are there any noticable issues with this panel.

It is in a condo built in 1973.

Panel was rated for 90 amps. Didnt see a main disconnect. Other than pointed screws at the dead front cover I didnt see any issues in the panel.

The panel was quite dusty/dirty.
Attached Thumbnails
zinsco-86206-avon-006-small-.jpg.jpg
Views:	151
Size:	40.7 KB
ID:	7142   zinsco-86206-avon-007-small-.jpg.jpg
Views:	125
Size:	17.7 KB
ID:	7143   zinsco-86206-avon-008-small-.jpg.jpg
Views:	162
Size:	69.1 KB
ID:	7144   zinsco-86206-avon-009-small-.jpg.jpg
Views:	156
Size:	66.9 KB
ID:	7145  
Reply With Quote
  #2  
Old 11/21/06, 2:15 PM
ccbrands1 ccbrands1 is offline
Active Poster
 
Join Date: Jan 2006
Posts: 220
Please Note: ccbrands1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Zinsco

other than being a zinsco;

white wires used as hots should be marked with black tape.

with as few of breakers there are, the 6 hand movement rule for disconnects should not apply.
Reply With Quote
  #3  
Old 11/21/06, 5:05 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Zinsco

That is not the service equipment, so there is no requirement for a service disconnect within that panel (the "six-throw" rule doesn't apply to remote panels).

Zinsco panels that are located at interior locations such as this, are less "problematic" than exterior units that are exposed to the elements. However, some Zinsco breakers will fail to open when an over-current condition occurs.

This particular installation looks like it was never equipped with an exterior, hinged cover. That, I assume, is the reason for all of the lint and debris at the interior of the panel. At a minimum, I would not hesitate to recommend that it be cleaned.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #4  
Old 11/21/06, 5:30 PM
wsiegel wsiegel is offline
Active Poster
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 2,542
Please Note: wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Zinsco

If this is not the service equipment, should not the grounds and neutrals be seppartated. Also there are three ground wires on one terminal.
Reply With Quote
  #5  
Old 11/21/06, 7:18 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,717
Default Re: Zinsco

Hope you called out that non-approved dryer vent pipe.



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #6  
Old 11/21/06, 8:22 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,482
Default Re: Zinsco

Quote:
Originally Posted by wsiegel
If this is not the service equipment, should not the grounds and neutrals be seppartated. Also there are three ground wires on one terminal.
Good thinking...If it's a load side panel, they should be separated and the grounded conductors isolated.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #7  
Old 11/21/06, 9:38 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Zinsco

Quote:
Originally Posted by wdecker
Hope you called out that non-approved dryer vent pipe.
Is that foil flex really not approved for dryers? I thought it was only the plastic kind that couldn't be used on dryers. Seems like that foil flex is all I ever see connecting the dryer to the pipe in the wall, in fact all my dryers are hooked up with it.
Reply With Quote
  #8  
Old 11/21/06, 10:10 PM
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 5,447
Default Re: Zinsco

M1501.1 General.
Dryer exhaust systems shall be independent of all other systems, shall convey the moisture to the outdoors and shall terminate on the outside of the building.

Exhaust ducts shall be constructed of minimum 0.016-inch-thick rigid metal, having smooth interior surfaces with joints running in the direction of air flow. Flexible transition ducts used to connect the dryer to the exhaust duct system shall be limited to single lengths, not to exceed 8 feet in length and shall be listed and labeled in accordance with UL 2158A.



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
  #9  
Old 11/21/06, 10:32 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Zinsco

Quote:
Originally Posted by wsiegel
If this is not the service equipment, should not the grounds and neutrals be seppartated. Also there are three ground wires on one terminal.
Uuuhyep.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #10  
Old 11/21/06, 11:02 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Zinsco

Quote:
Originally Posted by jwilliams4
M1501.1 General.
Dryer exhaust systems shall be independent of all other systems, shall convey the moisture to the outdoors and shall terminate on the outside of the building.

Exhaust ducts shall be constructed of minimum 0.016-inch-thick rigid metal, having smooth interior surfaces with joints running in the direction of air flow. Flexible transition ducts used to connect the dryer to the exhaust duct system shall be limited to single lengths, not to exceed 8 feet in length and shall be listed and labeled in accordance with UL 2158A.
So the flex is okay in the situations I described, as long as it does not exceed 8 feet. It seems like a piece of flex running from the dryer to the roof vent would also be acceptable under this rule as long as it is 8 feet or less. The roof vent pipe, no matter how short, would be the "duct system". Does that make sense?

Sorry for the OT postings.
Reply With Quote
  #11  
Old 11/21/06, 11:16 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,717
Default Re: Zinsco

Quote:
Originally Posted by brian winkle
Is that foil flex really not approved for dryers? I thought it was only the plastic kind that couldn't be used on dryers. Seems like that foil flex is all I ever see connecting the dryer to the pipe in the wall, in fact all my dryers are hooked up with it.
The only approved dryer vent pipe is rigid, galvanized pipe or corregated pipe.

The kind with the 'slinky' in it presents a non-smooth surface and can lead to lint fires.

Look at the box it came in. "Not approved for use with dryer vents"

Simple.



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #12  
Old 11/21/06, 11:23 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,717
Default Re: Zinsco

Quote:
Originally Posted by brian winkle
So the flex is okay in the situations I described, as long as it does not exceed 8 feet. It seems like a piece of flex running from the dryer to the roof vent would also be acceptable under this rule as long as it is 8 feet or less. The roof vent pipe, no matter how short, would be the "duct system". Does that make sense?

Sorry for the OT postings.
No. It does not make sense.

I had a (small) fire in my house.

It was caused by such a dryer vent pipe.

"Smooth interior surface", What part of this don't you understand?

Lint fires (from clothes dryers) account for 49% of all residential home fires.

"Save your clients, save the world!"

Hope this helps;



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #13  
Old 11/22/06, 10:55 AM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Zinsco

I am not trying to start an arguement here but I have a valid concern over the way I have been connecting dryers . If it is not safe I want to fix it. Each dryer is connected with one to three feet of aluminum flex to the hard pipe in the wall. It is the same stuff you describe with the slinky inside. Now I went out to the shed where there is a plastic bag containing "deflect-o" brand 4" flexible aluminum "air duct". It does state on the bag "Not recomended for dryer venting". It is 25 feet long. This is what I use for venting bathroon fans with 4" exhaust fittings.

Then there are some boxes from Ace Hardware that say "Flexible aluminum dryer vent duct" The stuff inside looks the same as the kind in the bag. The one in the box is made in the US, the bag comes from Canada. The box says "UL listed, but it doesn't say for what it is listed. It is only five feet long. This is what I use for dryer venting transitions. Again, it it called "Dryer vent duct" on the box.

The corregated pipe you refer to, if it is what I am picturing, does not have a smooth interior surface. It is made up of aluminum in a spiral shape with grooves and ridges on the inside. It comes compressed and you stretch it out. The piece I have has no label.

So I guess the part I don't understand is what I should actually be using for the transition. Is there a product that is flexible AND has a smooth interior surface?

Excuse me if I sound ignorant, I am just trying to learn. I am the type of person that insists on doing a job 100% correct.
Reply With Quote
  #14  
Old 11/22/06, 11:15 AM
Keith Swift, PhD. Keith Swift, PhD. is offline
InterNACHI Member
 
Join Date: Nov 2005
Location: Northridge, CA
Posts: 1,391
Default Re: Zinsco

One simple question generates a fountain of information. Where else except on the NACHI message board.



InterNACHI Vice President, InterNACHI Editor-in-Chief, co-founder CalNACHI

Reply With Quote
  #15  
Old 11/22/06, 11:19 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 7,708
Send a message via Yahoo to jfunderburk
Default Re: Zinsco

Quote:
Originally Posted by jpope
That is not the service equipment...
How did you make that determination?



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
WTB: FP and Zinsco scoslett Electrical Inspections 6 2/28/07 8:52 PM
Zinsco Sylvania gkoehl Electrical Inspections 10 2/5/07 6:17 PM
Zinsco cbuell Electrical Inspections 4 1/4/07 4:31 PM
Zinsco panel jsmith3 Electrical Inspections 4 3/28/06 8:39 PM


All times are GMT -4. The time now is 2:13 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts