Default Zinsco

The bus bars on this Zinsco had heated to the point that it damaged the mounts. When I removed the cover, the entire setup almost fell out.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net

Last edited by jpope; 2/28/07 at 4:14 PM..
Reply With Quote
  #2  
Old 1/1/06, 10:57 PM
cmccann's Avatar
cmccann cmccann is offline
Active Poster
 
Join Date: Nov 2003
Location: Canton, MI
Posts: 473
Please Note: cmccann is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Zinsco

Wow Jeff, you are the master!!!
Reply With Quote
  #3  
Old 1/2/06, 3:37 AM
Joe Hugenroth Joe Hugenroth is offline
InterNACHI Member
 
Join Date: May 2004
Location: Fresno, CA
Posts: 755
Default Re: Zinsco

Yikes!! I see a ton of Zinscos around here, and I always write them up, but the worst I have seen is a little oxidation and some loose breakers. Nothing like that!
Reply With Quote
  #4  
Old 1/2/06, 11:03 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Zinsco

I think Jeff lives in the Zinsco capital of the world...would you believe jeff down here in VA I am lucky to see maybe only 2-3 Zinsco's a year( way more Fed.Pacific around here )...and usually they are on the electrical side when we are upgrading them.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #5  
Old 1/2/06, 11:44 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,039
Default Re: Zinsco

I see 10 or 15 Zinsco panels in a month and maybe 5 or so FPE. This was not the worst I've seen, but it's up there in the top ten. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #6  
Old 1/3/06, 7:40 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,247
Default Re: Zinsco

I think Zinsco accounts for about half of my inspections, with FPE and the early 1980's Sylvania accounting for another 25%. Murray and GE in the newer homes.
Reply With Quote
  #7  
Old 1/3/06, 10:05 AM
twheeler
Guest
 
Posts: n/a
Please Note: is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Zinsco

Jeff, I want to move down there. I love seeing those type of deficiencies. And great pic, by the way.
Reply With Quote
  #8  
Old 2/17/06, 1:11 PM
jweinberg's Avatar
jweinberg jweinberg is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: San Jose, CA
Posts: 420
Please Note: jweinberg is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Zinsco

Quote:
Originally Posted by jpope
I see 10 or 15 Zinsco panels in a month and maybe 5 or so FPE. This was not the worst I've seen, but it's up there in the top ten. . .
Jeff,

Do you have some standard Zinsco Veribiage you put in your reports that you wouldn't mind sharing with us? It would be greatly appreciated.

Jeff
Reply With Quote
  #9  
Old 2/17/06, 6:13 PM
cbuell's Avatar
cbuell cbuell is offline
Active Poster
 
Join Date: Feb 2004
Location: Shorline, WA
Posts: 383
Please Note: cbuell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Zinsco

Jeff "Zinsco" Pope,
Here is a Zinsco from my inspection today. Tons of issues besides being a Zinsco. I especially like the double tapped neutral to the sub-panel; and, the sub panel hot conductors and neutral fed individually through 1/2" romex connectors.
Charlie
Attached Thumbnails
zinsco-ramseur-118.jpg  
Reply With Quote
  #10  
Old 2/17/06, 7:21 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,039
Default Zinsco

Quote:
Originally Posted by jweinberg
Do you have some standard Zinsco Veribiage you put in your reports that you wouldn't mind sharing with us? It would be greatly appreciated.
IMHO, Zinsco, unlike FPE, deserves a bit more consideration before making a blanket statement for repair and/or replacement. The one pictured by Charles is another story

If you are unsure and would just rather be safe, this statement is probably the most prudent, and can be used as a general comment for Zinsco and FPE.

Quote:
The home is equipped with a Zinsco brand electrical panel(s). Zinsco components are considered problematic by industry professionals due to their high failure rate. Failure of any component within the electrical system may result in fire and/or electrocution. Further evaluation of the electrical panel by a state licensed electrical contractor is advised to determine its safety, integrity and performance.
You should follow up a statement like this with a list of any observed deficiencies.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net

Last edited by jpope; 2/17/06 at 7:41 PM..
Reply With Quote
  #11  
Old 2/22/06, 11:16 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,247
Default Re: Zinsco

The name "Zinsco" is enough "observed" deficiency for me. I don't take covers off simply because of what you noted in your first post and my own experience doing property renovations. I think everything I've ever renovated here in San Diego had a Zinsco panel.
Reply With Quote
  #12  
Old 2/23/06, 11:14 PM
jweinberg's Avatar
jweinberg jweinberg is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: San Jose, CA
Posts: 420
Please Note: jweinberg is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Zinsco

Thanks Jeff...

Quote:
Originally Posted by jpope
If you are unsure and would just rather be safe, this statement is probably the most prudent, and can be used as a general comment for Zinsco and FPE.
The home is equipped with a Zinsco brand electrical panel(s). Zinsco components are considered problematic by industry professionals due to their high failure rate. Failure of any component within the electrical system may result in fire and/or electrocution. Further evaluation of the electrical panel by a state licensed electrical contractor is advised to determine its safety, integrity and performance.
Reply With Quote
  #13  
Old 2/23/06, 11:20 PM
Jay Moge's Avatar
Jay Moge Jay Moge is offline
Active Poster
 
Join Date: Aug 2005
Location: Derry New Hampshire
Posts: 761
Please Note: Jay Moge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Zinsco

Jeff, you need to start a zinsco museum.
Reply With Quote
  #14  
Old 2/23/06, 11:56 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,039
Default Re: Zinsco

...



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #15  
Old 2/24/06, 10:10 AM
Mark A. Timpani's Avatar
Mark A. Timpani Mark A. Timpani is online now
InterNACHI Member
 
Join Date: May 2004
Location: Tucson, AZ
Posts: 1,614
Default Re: Zinsco

Is this a zinsco or one of the problematic panels?
Attached Thumbnails
zinsco-100_9260-small-.jpg.JPG
Views:	46
Size:	17.0 KB
ID:	1549   zinsco-100_9294-small-.jpg.JPG
Views:	62
Size:	35.6 KB
ID:	1550   zinsco-100_9295-small-.jpg.JPG
Views:	76
Size:	40.2 KB
ID:	1551  




"Be Proud of Your Home, Go With Pride!"
'Not just a Home Inspection, but an Education'

Pride Property Inspections provides professional Home Inspections throughout Tucson and Southern Arizona including Pima, Cochise, Pinal, Santa Cruz, Graham counties.

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
WTB: FP and Zinsco scoslett Electrical 6 2/28/07 8:52 PM
Zinsco Sylvania gkoehl Electrical 10 2/5/07 6:17 PM
Zinsco cbuell Electrical 4 1/4/07 4:31 PM
Zinsco panel jsmith3 Electrical 4 3/28/06 8:39 PM


All times are GMT -4. The time now is 12:18 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts