Default Zinsco

zinsco-elec4.jpg

Zinsco Load Center, 100 Amp service.

Deferred it to a licensed electrician due to the name and several other things. The realtor called me and gave me an ear full as he could not understand why it is that I am so hard on electrical. I told him electrical can burn homes down and worst it can kill and I thought that was reason enough. He said "Is the house burning down"? I said no and I can not predict if it will due to this set up nor can I tell him if the water heater will blow the house up tomorrow. Long story short, could you guru's tell me anything and everthing you can see with this set up. Could you also tell me how you would have wrote it up? I am feeling a little beat up on this one and maybe I can learn not to be as he put it "scaring his buyers away". Here is how
I wrote it up
MAIN PANEL: Panel was full and may need to be upgraded for future needs. Main wires are aluminum - need to maintain oxidizing agent on the wires. Panel cover was missing some screws. Evidence of rust in panel. BRANCH WIRES: No signs of overheating were evident at the time of the inspection. Zinsco Load Center. See Electrical Remarks

The Remarks Section:
A Zinsco TM or SylvaniaTM-Zinsco electrical panel is installed in this building. Electrical hazards may be present in the electrical panel which could result in overheating, fire, or inability to turn off the electrical power in the home. A licensed electrician who is familiar with this equipment should be called to inspect the panel for immediate fire and shock hazards, and regardless of its visually-apparent condition www.inspect-ny.com/electric/Zinsco.htm

My Photo comments:
Zinsco Electrical Load Center located in the garage. 2-Shots. See electrical remarks. Recommend a licensed electrician evaluate. Note: This does not mean the unit is bad but it does mean a more intrusive inspection is recommended.


I also told him I do not pull the breakers to look as this is for the electrician.

I don't know, maybe I am hard on electrical and do not wite it up as I should and if this is the case please let me know. Oh by the way, this is not to mention with in the electrical section I also pointed out things such as double tapping breakers a broken breaker switch etc. I won't go on because I wanted you to look at the panel. Hope you can blow it up to see better.

Thanks for oyur help,
Randy

Reply With Quote
  #2  
Old 3/10/08, 11:45 AM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,749
Default Re: Zinsco

Randy...your verbiage sounds fine to me. The only thing...I might re-think the use of "immediate fire & shock hazards" to something like "latent hazards and defects". A layperson could envision sparks & such with your phrase but it is not totally inaccurate though.

Here is my standard comment re: Zinsco & FPE:
Quote:
The home is equipped with a Zinsco brand service panel. Zinsco panels are considered problematic by industry professionals due to their high failure rate. Failure of any component within the electrical system can result in electrocution and/or fire. I recommend a careful, detailed analysis of these panels by a licensed electrician to determine if any corrective action is needed.
Reply With Quote
  #3  
Old 3/10/08, 4:52 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Zinsco

Michael is using a modified version of my narrative. The only difference is the recommended action. Here is my version;

Quote:
The home is equipped with a Zinsco brand panel. Zinsco components are considered problematic by industry professionals due to their high failure rate. Failure of any component within the electrical system may result in fire and/or electrocution. Evaluation of the panel by a qualified electrician is advised to determine its safety, integrity and performance.
Occasionally, I will add this to the end as well. . .

Quote:
You can learn more about this issue at http://www.inspect-ny.com/electric/zinsco.htm
Your picture is too small for me to see anything of value, but it appears to be one with copper bus-bars, rather than AL.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #4  
Old 3/10/08, 5:28 PM
Randy D. Stufflebeem's Avatar
Randy D. Stufflebeem Randy D. Stufflebeem is offline
InterNACHI Member
 
Join Date: Nov 2006
Location: Galesburg, IL
Posts: 3,281
Default Re: Zinsco

Thanks for your report - it's obvious you really know what you're doing. My wife and I would like to pay you to walk through the house with us giving us a basic understanding of utilities and maintenance. We'll contact you when we get in town (after April 7th).
Thanks again,
David

Just received this e-mail from the client I was supossed to have scared the heck out of as per their agent. My clients are from Washington and I gladly accepted their offer without the pay.

Regardless, I thank you guys for helping me with this matter and giving me your honest opinion and how you write it up. If you don't mind I would like to use your words next time.
Thanks again,
Randy
Reply With Quote
  #5  
Old 3/10/08, 5:38 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Zinsco

Use it as you wish. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #6  
Old 3/10/08, 10:06 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,749
Default Re: Zinsco

I'm sure mine came from Jeff sometime over the last couple of years....use 'em, modify 'em, make 'em your's, that's why we post 'em.
Reply With Quote
  #7  
Old 3/11/08, 12:28 AM
pdickerson pdickerson is offline
InterNACHI Member
 
Join Date: May 2004
Location: Clinton, WA
Posts: 341
Default Re: Zinsco

I thought your comments were reasonable, appropriate, and not at all alarmist. Nice work.
Reply With Quote
  #8  
Old 3/11/08, 1:48 PM
Greg Seelhorst Greg Seelhorst is offline
New User
 
Join Date: Mar 2008
Posts: 2
Please Note: Greg Seelhorst is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Zinsco

NACHI -

Can you identify this panel and where I can get manufacturer specifications
for this model? It looks like you have tons of experience with this line of
MSPs.

Regards,


Greg Seelhorst
Installation Coordinator
NABCEP Certified Solar PV Installer
Solar Works
4925 Gravenstein Hwy North
Sebastopol, CA
707-829-2518 (work)
707-849-6819 (cell)
Attached Thumbnails
zinsco-zinsco-125-amp-.jpg  
Reply With Quote
  #9  
Old 3/11/08, 7:36 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Zinsco

Model MTMB10 (12-24) UF, manufactured by GTE Sylvania

Obtaining Manuf Specs may be difficult. These have been discontinued for quite some time.

May I ask what your interest in this panel is?




IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #10  
Old 3/11/08, 8:00 PM
Greg Seelhorst Greg Seelhorst is offline
New User
 
Join Date: Mar 2008
Posts: 2
Please Note: Greg Seelhorst is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Zinsco Model MTMB10 (12-24) UF, manufactured by GTE Sylvania

jpope -

Thanks for the info. I went to a neighbor's house and found the specs. Check out the attached photo for reference. I am using them for solar info. In Article 690 it explains that the room for solar can be the busbar rating x 1.2 minus the MSP breaker rating. So, an MSP with a 125 Amp busbar rating and a 100 breaker will leave us with room for 50 Amps of solar. Does this sound right?

I know all of the warnings on the Sylvania's and we will start warning people. The problem is that we are in too deep and a change may cost close to $1,000 in delays and people's time to change the panel at this point. We have done this many times over, I just hadn't seen this model of Sylvannia lately and couldn't remember.
Attached Thumbnails
zinsco-sylvannia-mtmb10-12-14-125-amp.jpg 125 AMP.jpg
Views:	74
Size:	111.1 KB
ID:	19457  
Reply With Quote
  #11  
Old 3/11/08, 8:38 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Zinsco Model MTMB10 (12-24) UF, manufactured by GTE Sylvania

Quote:
Originally Posted by Greg Seelhorst
In Article 690 it explains that the room for solar can be the busbar rating x 1.2 minus the MSP breaker rating. So, an MSP with a 125 Amp busbar rating and a 100 breaker will leave us with room for 50 Amps of solar. Does this sound right?
I can't help you there. That's Greek to me

I have a vested interest in this particular panel, but I can't discuss it on this open board. Do you have an email address where I can reach you?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"Magnetrip" by Zinsco rspriggs Electrical Inspections 8 12/4/07 10:44 PM
Another Kind of Zinsco jpope Electrical Inspections 10 3/6/07 9:41 PM
WTB: FP and Zinsco scoslett Electrical Inspections 6 2/28/07 7:52 PM
Zinsco cbuell Electrical Inspections 4 1/4/07 3:31 PM
Zinsco information bking Electrical Inspections 1 4/2/06 11:49 PM


All times are GMT -4. The time now is 7:37 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts