Default Zinsco Main and Sub panels

Besides the age and the double tap on the main, the EGCs and Neutrals together in the sub panel. The knock outs missing and the cable on the sub missing the clamp coming into the sub panel. And yes it had pointed screws that came with this little jewel. Am I missing anything?

The main panel is mounted outside on the north side of the house and the sub-panel is located in the garage on the opposite side. As you can see the main disconnect is 100 amps/Zinsco. The double tap that is coming out of there is going to the AC compressor that is right nest to it. This feeds the sub-panel that is on the opposite side of the garage.
Attached Thumbnails
zinsco-main-and-sub-panels-picture-078.jpg   zinsco-main-and-sub-panels-picture-080.jpg   zinsco-main-and-sub-panels-picture-081.jpg   zinsco-main-and-sub-panels-100_0183.jpg   zinsco-main-and-sub-panels-picture-104.jpg  

Reply With Quote
Need a home inspection in Virginia? Check out InterNACHI's listing of Virginia certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 4/13/11, 8:44 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Zinsco Main and Sub panels

Where do the double tap conductors terminate?
Reply With Quote
  #3  
Old 4/13/11, 8:55 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Zinsco Main and Sub panels

The EGC's and neutrals being bonded at the sub panel is only half of the issue. The EGC's need to be bonded to the enclosure, while the neutrals remain isolated.

It's a "hot-mess" and needs fixin'.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #4  
Old 4/13/11, 9:17 PM
dmcmullen dmcmullen is offline
New User
 
Join Date: Nov 2008
Location: Wheatland, CA
Posts: 25
Please Note: dmcmullen is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Zinsco Main and Sub panels

The double tap terminates in the disconnect for the AC condenser disconnect that is right next to the Main panel.

David
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 7:37 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts