Default Is this a Zinsco Main Panel ?

The house was built in 1976.... Usually I see the writing on the panel
indicating its a Zinsco. I seen some observed arcing on the panel.
Didnt observe any problems with the Branch circuits.
What should be the write up?

David





Reply With Quote
Need a home inspection in Oregon? Check out InterNACHI's listing of Oregon certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 11/22/10, 10:28 AM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 8,234
Default Re: Is this a Zinsco Main Panel ?

Sure looks like one.



Wayne Wilson
East TN Home Inspections LLC
Knoxville, Oak Ridge, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.
865-256-1490

http://site.myhomeinspection.net

Reply With Quote
  #3  
Old 11/22/10, 10:41 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Is this a Zinsco Main Panel ?

Yes, it is.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #4  
Old 11/22/10, 7:31 PM
Robert Ernst Robert Ernst is offline
InterNACHI Member
 
Join Date: Sep 2010
Location: Sparks,NV
Posts: 654
Default Re: Is this a Zinsco Main Panel ?

It's probably a Sylvania (they bought Zinsco) panel due to the age could be why you don't see the Zinco name or the sticker came off. The Internnachi electrical course states "Due to the frequent failure of the connection between the breaker and its bus, the inspector should recommend full evaluation and possible replacement of the panel."
Looks like you could have that issue going on with those burn marks. They have issues with the clips that hold it to the bus. With that problem and that they are so close to the dead front breakers can be knocked loose when taking off the dead front. Could be the reason for the burn marks. If the electrician doesn't convince them to change it the insurance company might. I've owned homes with Zinsco and Stabloc panels and never had an issue but with what I know now I would have changed them.

Last edited by rernst1; 11/24/10 at 11:54 AM..
Reply With Quote
  #5  
Old 11/22/10, 9:29 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: Is this a Zinsco Main Panel ?

Quote:
Originally Posted by wwilson3 View Post
Sure looks like one.
There is definately nothing that looks quite like those panels is there!




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
  #6  
Old 11/24/10, 9:53 AM
Philippe G. Heller's Avatar
Philippe G. Heller Philippe G. Heller is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: San Diego, CA
Posts: 171
Default Re: Is this a Zinsco Main Panel ?

I would also state that the panel is full which precludes a visual evaluation of the buss bars. It also limits future expansion, and always let the buyer know that the Zinsco/Sylvalia panels are suspect. Here's why:

Buyer moves in and hire an electrician to (fill in the blank). If the electrician sees an opportunity to sell the client a new panel, he will throw you under the bus (pun intended) and say "your inspector should have told you these are a fire hazard".

Always recommend that the client research these panels and determine if they want to pursue an upgrade. Since there were no official recalls, just speculation, you cannot call for replacement.



Philippe Heller
The San Diego Real Estate Inspection Co.
http://www.sdinspections.com
www.facebook.com/sdinspections
Reply With Quote
  #7  
Old 11/24/10, 9:57 AM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,956
Default Re: Is this a Zinsco Main Panel ?

Quote:
Originally Posted by pheller View Post
..you cannot call for replacement.

Says who? I give my client a choice of two options....have it removed or install a smoke detector immediately above it. It's the code inspector who is limited in what he can enforce...but there is no such restriction upon a home inspector and what he can recommend to his client for the preservation of his life and property.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
  #8  
Old 11/24/10, 10:04 AM
Philippe G. Heller's Avatar
Philippe G. Heller Philippe G. Heller is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: San Diego, CA
Posts: 171
Default Re: Is this a Zinsco Main Panel ?

I fully agree that they should be replaced. But on what grounds can you say that it must be replaced? Unless there is a recall that I don't know about.



Philippe Heller
The San Diego Real Estate Inspection Co.
http://www.sdinspections.com
www.facebook.com/sdinspections
Reply With Quote
  #9  
Old 11/24/10, 10:12 AM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,956
Default Re: Is this a Zinsco Main Panel ?

Quote:
Originally Posted by pheller View Post
I fully agree that they should be replaced. But on what grounds can you say that it must be replaced? Unless there is a recall that I don't know about.
I never use the word "must" in anything I write in an inspection report. I can only "recommend".

Under what authority "must" anyone comply with the directives of a home inspector?



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
  #10  
Old 11/24/10, 10:25 AM
Philippe G. Heller's Avatar
Philippe G. Heller Philippe G. Heller is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: San Diego, CA
Posts: 171
Default Re: Is this a Zinsco Main Panel ?

Here's what we put:

The panel was manufactured by Zinsco/Sylvania. These panels were made with alloy buss bars which are easily dented. Because of this, a poor connection with the circuit breakers sometimes develops which can create a fire hazard. We recommend that you consult with a licensed electrician as to the integrity of this electric panel. More information can also be found at http://www.inspect-ny.com/electric/Zinsco.htm

Concerns: Probably because I am in CA, I would be concerned about getting sued by a seller if the buyer cancelled over my recommendation to replace the panel. The seller has a good case to claim a loss if my negligent actions cause him to lose money.



Philippe Heller
The San Diego Real Estate Inspection Co.
http://www.sdinspections.com
www.facebook.com/sdinspections
Reply With Quote
  #11  
Old 11/24/10, 10:50 AM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,956
Default Re: Is this a Zinsco Main Panel ?

Quote:
Originally Posted by pheller View Post
Concerns: Probably because I am in CA, I would be concerned about getting sued by a seller if the buyer cancelled over my recommendation to replace the panel. The seller has a good case to claim a loss if my negligent actions cause him to lose money.
What if he sued you because of a "recommendation" to replace a furnace with a cracked heat exchanger? A 30 year old water heater with a corroded base?

If your reports do not recommend improvements over observed conditions that are less than optimal, what are their value? I do not understand.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
  #12  
Old 11/24/10, 11:12 AM
Philippe G. Heller's Avatar
Philippe G. Heller Philippe G. Heller is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: San Diego, CA
Posts: 171
Default Re: Is this a Zinsco Main Panel ?

There is a difference between a cracked heat exchanger (broken item) or rusted water heater (worn item) and just recommending that something gets replaced.

I was simply asking on what grounds you would recommend replacing the Zinsco? Just the reputation? An opinion? A recall?



Philippe Heller
The San Diego Real Estate Inspection Co.
http://www.sdinspections.com
www.facebook.com/sdinspections
Reply With Quote
  #13  
Old 11/24/10, 11:24 AM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,956
Default Re: Is this a Zinsco Main Panel ?

Quote:
Originally Posted by pheller View Post
There is a difference between a cracked heat exchanger (broken item) or rusted water heater (worn item) and just recommending that something gets replaced.

I was simply asking on what grounds you would recommend replacing the Zinsco? Just the reputation? An opinion? A recall?
There are two schools of thought among electrical contractors on Zinsco and FP boxes. If they have been there for 40 years the odds are they will be fine...or, these devices were catching fire when they were new and we can only expect them to become more dangerous the older they get.

If there was a recently paroled child rapist living next door that I knew about and I knew that my client had three young daughters who would be playing in the unfenced backyard....I would alert him to the danger and recommend that he install or take whatever measures he needed to make them safe. Will the rapist act upon his impulses or will he remain dormant? Your guess as to this...or the future integrity of an electrical service panel with a history of fire...is just a guess.

I recommend that, based upon its history and the potential for loss of life or property, that he replace it or put a smoke detector over it, at a minimum. Whether he gets the seller to do it, does it himself, or decides to walk away from the deal....it matters little to me and has no bearing on my report.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
Need a home inspection in Oregon? Check out InterNACHI's listing of Oregon certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 11/24/10, 12:24 PM
Robert Ernst Robert Ernst is offline
InterNACHI Member
 
Join Date: Sep 2010
Location: Sparks,NV
Posts: 654
Default Re: Is this a Zinsco Main Panel ?

I agree with not suggesting replacement. When I see one of those problem panels on an inspection or not I inform the people about the possible issues with that equipment and suggest they get a Licensed Electrician to look at it. We can't see some signs of a problem because we can't remove the breakers. The breakers have been known to arc and weld to the buss. The breakers have also been known to not trip (look at the video below). I know an electrician that has been doing the job for 50 years. He told me he recommends replacement since the product is obsolete and there are safer products now. He will never tell people it's going to burn the house down since he doesn't know if it will or not. There is also alternatives to replacement of the panel. There are replacement breakers that claim to be better and there are also retrofit panel boards so you can just replace the guts of the panel. Let the electrician make the final call in my opinion.
http://www.youtube.com/watch?v=uMV1jmDn3o4
Reply With Quote
  #15  
Old 11/24/10, 8:56 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Is this a Zinsco Main Panel ?

From today. . .
Attached Thumbnails
zinsco-main-panel-20101124_12.jpg   zinsco-main-panel-20101124_13.jpg   zinsco-main-panel-20101124_14.jpg  



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Main Panel clearance from sink jscaparo Electrical Inspections 2 3/30/10 12:41 AM
Main and Sub Panel gheller Electrical Inspections 10 9/25/08 9:22 PM
Outlet off of Main Panel? jlevy Electrical Inspections 2 8/5/08 5:18 PM
Electrical Safety Foundation International Links jtedesco1 Electrical Inspections 5 12/8/07 3:10 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 7:37 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts