Found a Zinsco panel in a "condo" yesterday... actually was built as an a rental apartment, then turned "Condo" in 2006 - originally built in 1973.
Breakers are all loose, pushed down, but no heat buildup, no hot spots, and no other signs of problem yet! I showed the client and recommended immediate eval by an electrician.
I recommended the whole box be replaced.
Not only that, but the cover was held on by various sharp screws.
Attached Thumbnails
zinsco-panels-p1020833.jpg   zinsco-panels-p1020837.jpg   zinsco-panels-p1020835.jpg  



Andy Cox
http://www.CoxInspections.com
Kissimmee, FL
You’re Your Own Job Security.
Reply With Quote
Need a home inspection in South Dakota? Check out InterNACHI's listing of South Dakota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 4/30/10, 12:19 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Zinsco panels

Bravo Andy!



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #3  
Old 4/30/10, 1:44 PM
Andrew Cox Andrew Cox is offline
InterNACHI Member
 
Join Date: May 2006
Location: Kissimmee, FL
Posts: 1,064
Default Re: Zinsco panels

WOW! I rarely get a Bravo! Thanks.



Andy Cox
http://www.CoxInspections.com
Kissimmee, FL
You’re Your Own Job Security.
Reply With Quote
  #4  
Old 4/30/10, 6:58 PM
Zoe Fackler Zoe Fackler is offline
InterNACHI Member
 
Join Date: Jul 2005
Location: Riverview, FL
Posts: 313
Default Re: Zinsco panels

Google is wonderfull!!
I actaully had a home that had a Zinsco Panel. I bought it in the 80's in Texas and was told I could not buy breakers. Not the case. You can almost always by - remakes. There are even breakers available for the old Montgomery Ward panels.
But here's what I found out::::

Moderator Post (s) for this thread:
>Yes.....FPE No-trip bydoug seibert on 08/16/2004
>ALWAYS ask the advice of a licensed electrician ! bydoug seibert on 08/17/2004
>Zinsco replacement breaker bydoug seibert on 06/07/2006
• I'm an electrical [COLOR=blue !important][COLOR=blue !important]contractor[/COLOR][/COLOR] in Seattle and have been in the contracting business since 1973. Started wiring houses in 1953. So I have a little bit of expereince with a variety of electrical equipment.
• Regarding the Zinsco electrical panels, I offer the following comments:
• Originally made in Puerto Rico and installed in the 60's and 70's thoughout the USA market. Lots of these are in both single family homes and multi family apartments and condos.
• Zinsco sold their manufacturing plants to Sylvania who then marketed them under the Sylvania brand until finally closing down.
• MAJOR PROBLEMS: We have found the breakers do not trip under normal over-load conditions. We have pumped up to 60 Amps into a 15 Amp breaker before it will trip. [COLOR=blue !important][COLOR=blue !important]FIRE [COLOR=blue !important]HAZARD[/COLOR][/COLOR][/COLOR]!
We have found the buss bars are made of aluminum material and corrode quite easily. I have equated it to perhaps different levels of quality in the aluminum they used.
When these buss bars corrode they can present a real hazard and we have experienced the panels going in a "Melt Down" condition. MAJOR HAZARD!!
• CONCLUSIONS: Replace any Zinsco or Sylvania brand panels. They are a hazard.
Consider using the Cutler [COLOR=blue !important][COLOR=blue !important]Hammer[/COLOR][/COLOR] brand "CH" style. These are a little more expensive, but have all COPPER buss bars and offer a "Lifetime Guarantee" (free replacement of BRANCH circuit breakers)
Good Luck!!
Reply With Quote
  #5  
Old 4/30/10, 7:07 PM
John E. Mullarkey John E. Mullarkey is offline
InterNACHI Member
 
Join Date: Oct 2009
Location: Sarasota, Fl
Posts: 349
Default Re: Zinsco panels

Well done! Zinsco is the kiss of death.
Reply With Quote
  #6  
Old 4/30/10, 7:42 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,925
Default Re: Zinsco panels

I'll counter that!

Your full of crap!

I just did one of these an hour ago.

If you tested it and it is OK, it's OK.

Hi's are not required to test for this stuff. If you did and it is OK your recommendation is just a bunch of crap.

Advise the client of what you know and let it be.

I see these panels and pay close attention to them. If they are working fine at the time of inspection, they are fine as far as I am concerned.

There has been no recall on these things.

Can't you find something significant to work on?



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #7  
Old 4/30/10, 9:00 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Zinsco panels

Quote:
Originally Posted by dandersen View Post
I'll counter that!

Your full of crap!

I just did one of these an hour ago.

If you tested it and it is OK, it's OK.

Hi's are not required to test for this stuff. If you did and it is OK your recommendation is just a bunch of crap.

Advise the client of what you know and let it be.

I see these panels and pay close attention to them. If they are working fine at the time of inspection, they are fine as far as I am concerned.

There has been no recall on these things.

Can't you find something significant to work on?
Interesting, I have inspected many Zinsco panels and have found several with scorched bus bars.

want pictures David?

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #8  
Old 5/1/10, 2:43 AM
Tim Spargo's Avatar
Tim Spargo Tim Spargo is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Lancaster, CA
Posts: 2,407
Default Re: Zinsco panels

I've replaced breakers on those many moons ago. Like Gerry said, many are scorched, brittle and falling apart and at the same time they look OK on the surface..

I say bad kitty.



Home Inspections in Palmdale Lancaster California

Tim Spargo
Spec Rite Inspections
Commercial and Residential Inspections
Palmdale Lancaster Santa Clarita CA
661-317-5770








Reply With Quote
  #9  
Old 5/1/10, 11:32 AM
Bobby G. Michael Bobby G. Michael is offline
InterNACHI Member
 
Join Date: Jan 2010
Posts: 187
Default Re: Zinsco panels

Yes, well done.



Alabama Home Inspections
www.thebirminghamhomeinspector.com
Home Inspections in Birmingham, Montgomery, Huntsville, and Tuscaloosa.
Reply With Quote
  #10  
Old 5/1/10, 1:29 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,925
Default Re: Zinsco panels

Here are mine...

Is this an issue?

I have inspected many of these and have a VERY low % of bad ones (I guess they already got rid of the bad ones).

I pull these apart. (I know that is not required).
I evaluate them ( not required).
I can see what they are doing...

I see no damn reason to call in an electrician when they can't scratch the surface of the evaluation I do.

I see no reason to recommend replacement.
I DO see the need to "advise" that client that they should pay attention to anything that may indicate there is an electrical issue that could be associated with these panels.

If they are such a huge problem, why aren't the recalled on the spot?
Attached Thumbnails
zinsco-panels-dsc09596-horz.jpg   zinsco-panels-ir_2714.jpg  



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #11  
Old 5/1/10, 1:44 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,925
Default Re: Zinsco panels

Yes, it happens.

But until it does, are we required to pull out the crystal ball and report on something that does not exist?

If the "powers that be" can't recall these things and "get them off the street" NOW, why am I expected to do anything about their existence?

I can come up with a half-dozen legal reasons why we should leave these things alone. Just because they fail sometimes, is not a reason to place the burden of hiring an ill equipped electrician for something that has no reasonable suspicion of a problem.

Now, if any of you inspectors in Middle Tennessee and southwest Kentucky want to defer these things, give me a call. At least I will "evaluate" these things.

More than I can say for any electrician.

I guess I just "live life on the edge".
I still drive a Toyota!
Attached Thumbnails
zinsco-panels-zinsco-breakers.jpg  



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #12  
Old 5/1/10, 6:57 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Zinsco panels

Quote:
Originally Posted by dandersen View Post
Now, if any of you inspectors in Middle Tennessee and southwest Kentucky want to defer these things, give me a call. At least I will "evaluate" these things.
I'm with you on this. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #13  
Old 5/1/10, 8:14 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Zinsco panels

Quote:
Originally Posted by jpope View Post
I'm with you on this. . .
I'm not sure I agree with you there Jeff, while I understand Davids take on it (and am more than capable of doing the same)

Shutting off the main, I'll never do if the home is being lived in.
Removing the breakers to check them may actually contribute to the problem.
I'm not licensed as an electrical contractor in FL and feel that dismantling any panel is crossing that line.

BTW: I don't recommend any further evaluation either, I suggest replacement.

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
Need a home inspection in South Dakota? Check out InterNACHI's listing of South Dakota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 5/1/10, 9:54 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,925
Default Re: Zinsco panels

I never recommend "repair" rather "replacement".

Breaker removal (for inspection) is not needed unless there is a hot one.

Electrical arcing is several thousand degrees (at the source), all failing components generate heat when failing.

Any thermal evaluation is sufficient as a reason to recommend replacement.
I just don't go along with replacing it because of it's name tag.

It's just not our job or responsibility.

If someone elects to go beyond SOP and "evaluate" these things is one thing.
But to recommend repair without substance is clearly outside the scope of HI.

Just because the system's design is prone to failure is not reason to damn all panels in existence. I find hundreds of bad breakers because of the same buss connection problems as Zinsco, and they are not Zinsco. Just because I find a bunch of Cuttler-Hammer breakers getting cooked, is not cause to recommend replacement on every Home Inspection.

The long of the story, is that it is not the Home Inspectors Job.
There are some of us out there that can do evaluation on these panels and unless there is reason to call one of us in, there is not reason for the HI to feel responsible.

As I said, I have a "half-dozen" reasons not to mess with this (I exaggerated)...

3. Limitations, Exceptions & Exclusions
3.1. Limitations:

I. An inspection is not technically exhaustive.
II. An inspection will not identify concealed or latent defects.
VIII. An inspection does not determine the life expectancy of the property or any components or systems therein.

3.2. Exclusions:

I. The inspectors are not required to determine:

B. the condition of any component or system that is not readily accessible.
C. the service life expectancy of any component or system.
D. the size, capacity, BTU, performance, or efficiency of any component or system.
E. the cause or reason of any condition.
F. the cause for the need of repair or replacement of any system or component.
G. future conditions.
T. any manufacturer's recalls or conformance with manufacturer installation, or any information included for consumer protection purposes.

II. The inspectors are not required to operate:

F. any electrical disconnect or over current protection devices.

III. The inspectors are not required to:

B. dismantle, open, or uncover any system or component.
C. enter or access any area which may, in the opinion of the inspector, be unsafe.
F. do anything which, in the inspector's opinion, is likely to be unsafe or dangerous to the inspector or others, or damage property, such as, but not limited to: walking on roof surfaces, climbing ladders, entering attic spaces, or negotiating with pets.
K. offer or perform any engineering services.
L. offer or perform any trade or professional service other than home inspection.
Q. inspect on any system or component which is not included in these standards.



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission

Last edited by dandersen; 5/1/10 at 10:01 PM..
Reply With Quote
  #15  
Old 5/1/10, 10:06 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Zinsco panels

Quote:
I just don't go along with replacing it because of it's name tag.
That's where we would differ, I just inspeced an FPE today, guess what, I recommend replacement. last week I inspected a home with PB plumbing, guess what.

No I don't have a Crystal ball but my lawyer tells me I don't need one

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Zinsco panels--do you remove the covers from exterior panels? jfunderburk Electrical Inspections 44 12/22/09 4:29 PM
Kearney vs. Zinsco Service Panels jfunderburk Electrical Inspections 7 12/25/08 1:36 AM
SEC and panels also CEU course material dhostetter Electrical Inspections 3 10/3/08 5:49 PM
Distribution panels bking Electrical Inspections 2 3/11/07 10:29 AM
FPE Panel - Do you open them up? menser Electrical Inspections 11 2/7/06 6:31 PM


All times are GMT -4. The time now is 7:37 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts