View Poll Results: Do you remove the cover from an exterior Zinsco panel?
Yes 44 68.75%
No 16 25.00%
What's a Zinsco? 4 6.25%
Voters: 64. You may not vote on this poll

Reply
 
LinkBack Thread Tools
  #31  
Old 8/14/09, 11:27 PM
Tim Spargo's Avatar
Tim Spargo Tim Spargo is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Lancaster, CA
Posts: 519
Default Re: Zinsco panels--do you remove the covers from exterior panels?

Having seen a few arcs in my time Tom, additional ideas to share and improve safety are much welcomed.

Tim



Tim Spargo

Home Inspection Lancaster CA, Palmdale CA Antelope Valley





Reply With Quote
Find an InterNACHI certified Massachusetts Home Inspector (and anywhere else in North America)
  #32  
Old 9/21/09, 12:50 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,827
Send a message via Yahoo to jfunderburk
Default Re: Zinsco panels--do you remove the covers from exterior panels?

Quote:
Originally Posted by pabernathy View Post
Tell Joe Hi for me Tom.....he misses me...

No, they are not bound by OSHA. However, It is always stressed to them to be as safe as possible as their life may depend on it.
Paul, your statement is not entirely correct. Business owners are not bound by OSHA. All employees are, however. So if you have employees in your company, your company is most definitely regulated by OSHA.



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #33  
Old 9/21/09, 5:08 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,827
Send a message via Yahoo to jfunderburk
Default Re: Zinsco panels--do you remove the covers from exterior panels?

Wise advice here and here for those of you with families that depend on you staying alive.



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #34  
Old 9/21/09, 11:07 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Zinsco panels--do you remove the covers from exterior panels?

This is getting silly now....look those that feel comfortable can remove the cover, those that do not don't remove it....enough said.



Paul W. Abernathy,CMI,CEI,CEPE
NEC® Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #35  
Old 9/22/09, 3:10 AM
Mark E. Northrup's Avatar
Mark E. Northrup Mark E. Northrup is offline
InterNACHI Member
 
Join Date: Dec 2008
Location: Oregon
Posts: 214
Default Re: Zinsco panels--do you remove the covers from exterior panels?

I hav had one arc on me when replacing the cover. I learned that it is very dangerous when working with them.
After i changed my shorts. I realized that the panel can come in contact with the buss. But I still remove them to see if they conceal further problems. In this area some electricans tell home owners to leave them installed.



House 2 Home LLC
503-602-1420
HomePros@House2HomeLLC.ORG
Protecting Peace of Mind One House at a Time
Reply With Quote
  #36  
Old 9/22/09, 10:33 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Zinsco panels--do you remove the covers from exterior panels?

Quote:
Originally Posted by jfunderburk View Post
Paul, your statement is not entirely correct. Business owners are not bound by OSHA. All employees are, however. So if you have employees in your company, your company is most definitely regulated by OSHA.
Sure if you take it as an all inclusive statement. However, the majority of HI's are self employed and one man shops.....ofcourse when dealing with "companies" with employee's.



Paul W. Abernathy,CMI,CEI,CEPE
NEC® Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #37  
Old 10/3/09, 2:09 AM
Russell Spriggs's Avatar
Russell Spriggs Russell Spriggs is offline
InterNACHI Member
 
Join Date: Nov 2003
Location: Coeur d'Alene, ID area
Posts: 3,643
Default Re: Zinsco panels--do you remove the covers from exterior panels?

"Although removing the deadfront cover of the panel box for inspection is a service we commonly provide to our clients, it is NOT a part of a home inspection as per our national Standards of Practice (www.nachi.org/sop ). Under certain conditions, we will not remove the panel cover for a courtesy inspection. These conditions include, but are not limited to: rainy, snowy or wet conditions; wet floors or grounds; any blockage within 3 feet of the panel box; distractions within sight or hearing; panel boxes mounted in whole or in part either below the waist or above the shoulder in height; any panel box which may be older than 30 years of age; any situation in which the panel box cover may not be safely and securely re-attached, once removed; and any conditions in which the inspector does not feel safe for him/herself, or anyone else. One or more of these conditions were encountered during this inspection, and there was no visual inspection of the interior of this panel box. If the inspector feels that there is reason for the cover to be removed and the panel inspected, it will be so stated in another line item entry."
Reply With Quote
  #38  
Old 11/9/09, 10:12 AM
Philippe G. Heller Philippe G. Heller is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Ramona, CA
Posts: 18
Default Re: Zinsco panels--do you remove the covers from exterior panels?

Inspecting any panel is probably the most dangerous part of our job (along with getting on the roof).

After performing thousands of inspections, I came up with a tool to help inspectors with panels. I don't want to come across like I'm taking advantage of this thread. But I truly feel that this can help inspectors safely inspect electric panels. Of course, nothing beats following best-practices for inspecting panels such as NEVER RESTING THE PANEL COVER ON YOUR HEAD, proper clothing, paying attention, and taking your time.

zinsco-panels-do-you-remove-covers-exterior-panels-panelpal-002.jpg

Check out www.panelpal.com and post your reply.

Be safe out there.

Last edited by pheller; 11/10/09 at 9:33 PM.. Reason: Added Picture
Reply With Quote
  #39  
Old 11/20/09, 7:44 PM
Brian K. Smith Brian K. Smith is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Ripon,CA
Posts: 126
Default Re: Zinsco panels--do you remove the covers from exterior panels?

Quote:
Originally Posted by jpope View Post
(edited due to mis-quoted content)

I've seen a few Zinscos in my time, probably more than most other inspectors. There is only one panel design that has the problem he speaks of;



Don't remove the covers if you feel it's unsafe, but don't rely on bad information.

I remove all my covers and 30% of the hi I do up here are Zinscos.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Kearney vs. Zinsco Service Panels jfunderburk Electrical 7 12/25/08 2:36 AM
SEC and panels also CEU course material dhostetter Electrical 3 10/3/08 6:49 PM
Distribution panels bking Electrical 2 3/11/07 11:29 AM
FPE Panel - Do you open them up? menser Electrical 11 2/7/06 7:31 PM


All times are GMT -4. The time now is 4:37 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts