Default 1 condensate line......

one primary condensate line for 2 individual air handler units. First unit condensate tied into second unit condensate line through a T valve. This would essentially make one condensate line for 2 units. If the line gets plugged after the second unit, then both units would have to drain using the secondary line, correct? Have never seen this before so am wondering if this is a big violation or no big deal.
Reply With Quote
  #2  
Old 11/4/07, 12:56 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,826
Send a message via Yahoo to jfunderburk
Default Re: 1 condensate line......

I've seen it once before and I can't find a code against it. As long as the pans are equipped with a float switch or 2nd drain, I'd let it go. Be sure to test the float switches, however, to make sure they actually work--I've seen them fail to turn off the condenser.



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #3  
Old 11/4/07, 7:18 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,020
Default Re: 1 condensate line......

Quote:
Originally Posted by jfunderburk
I've seen it once before and I can't find a code against it. As long as the pans are equipped with a float switch or 2nd drain, I'd let it go. Be sure to test the float switches, however, to make sure they actually work--I've seen them fail to turn off the condenser.
I don't see a issue with the condensate line, so long as they are clear (able to see thru them) to prevent clogging. I've seen many that are brown and need cleaning ASAP.

Joe's got a point regarding the testing of the float switch in the secondary pan. I find many that do not operate as intended.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Condensate line. jlybolt HVAC 10 3/21/07 10:05 PM
Size of supply line aobrien HVAC 7 1/2/07 1:40 PM
Condensation drain vent abishop HVAC 9 8/4/06 2:59 PM
condensate line into gutter? hspinnler HVAC 2 6/13/06 10:25 PM
TPRV line and condensate line marriage ccarrington Plumbing 3 4/29/06 8:59 AM


All times are GMT -4. The time now is 5:10 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts