Default 1 condensate line......

one primary condensate line for 2 individual air handler units. First unit condensate tied into second unit condensate line through a T valve. This would essentially make one condensate line for 2 units. If the line gets plugged after the second unit, then both units would have to drain using the secondary line, correct? Have never seen this before so am wondering if this is a big violation or no big deal.
Reply With Quote
  #2  
Old 11/4/07, 12:56 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 7,707
Send a message via Yahoo to jfunderburk
Default Re: 1 condensate line......

I've seen it once before and I can't find a code against it. As long as the pans are equipped with a float switch or 2nd drain, I'd let it go. Be sure to test the float switches, however, to make sure they actually work--I've seen them fail to turn off the condenser.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #3  
Old 11/4/07, 7:18 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: 1 condensate line......

Quote:
Originally Posted by jfunderburk
I've seen it once before and I can't find a code against it. As long as the pans are equipped with a float switch or 2nd drain, I'd let it go. Be sure to test the float switches, however, to make sure they actually work--I've seen them fail to turn off the condenser.
I don't see a issue with the condensate line, so long as they are clear (able to see thru them) to prevent clogging. I've seen many that are brown and need cleaning ASAP.

Joe's got a point regarding the testing of the float switch in the secondary pan. I find many that do not operate as intended.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Condensate line. jlybolt Inspecting HVAC Systems 10 3/21/07 10:05 PM
Size of supply line aobrien Inspecting HVAC Systems 7 1/2/07 1:40 PM
Condensation drain vent abishop Inspecting HVAC Systems 9 8/4/06 2:59 PM
condensate line into gutter? hspinnler Inspecting HVAC Systems 2 6/13/06 10:25 PM
TPRV line and condensate line marriage ccarrington Plumbing Inspections 3 4/29/06 8:59 AM


All times are GMT -4. The time now is 7:52 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts