The disconnect for AC is rated at 60 amps. The AC is rated at 30 amp min. and 35 amp max. Does the disconnect need to be a low amp breaker?
Thanks! Mid America Property Inspections, Inc. Shawnee, KS 66217 Give us 5% of your confidence and we will earn the other 95% NACHI # 05110992 Cert # IAC2-00-7835 KHIRB # 0110-0008 KS-Termite Cert. # 18933 M0-Termite Cert. # N05033 |
| Find an InterNACHI certified Rhode Island Home Inspector (and anywhere else in North America) |
|
#2
|
|||
|
|||
|
Please Note:
Gary Reecher is a non-member guest and is in no way affiliated with InterNACHI or its members.
Yes it needs to be fused or breaker to 35 amps.
|
|
#3
|
|||
|
|||
|
It can work as is if the breaker feeding the disconnect is sized appropriately.
____________________________________________ "An Education, not just an Inspection" Larry Kage, CMI Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond. ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
|
|
#4
|
||||
|
||||
|
Thanks!
Mid America Property Inspections, Inc. Shawnee, KS 66217 Give us 5% of your confidence and we will earn the other 95% NACHI # 05110992 Cert # IAC2-00-7835 KHIRB # 0110-0008 KS-Termite Cert. # 18933 M0-Termite Cert. # N05033 |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Electric Panel | dmozzillo | Electrical | 26 | 1/26/09 1:18 PM |
| Exterior Service Disconnect Clearances? | rcramer | Electrical | 18 | 7/28/07 1:12 PM |
| A/C Disconnect question | rslocum | HVAC | 15 | 9/21/06 12:16 AM |
| 100 Amp Meter, 200 Amp Disconnect | jweinberg | Electrical | 8 | 8/15/06 12:32 PM |
| Disconnect and Main panel | srowe | Electrical | 10 | 6/13/06 7:49 PM |