I inspected a room with 100,000 BTU natural gas furnace and 36,000 BTU hot water tank in a 6X6X8 room. No exterior ventilation for combustion air. Door to room was trimmed at bottom allowing house air to enter for combustion air. I am going to recommend an exterior vent added for combustion air. My question is: There is currently an exterior vent with ducting into the return air plenum. Should I recommend the return air plenum be sealed from exterior vent and exterior vent be allowed to add air into small utility room for combustion air? Thank you.
|
|
#2
|
||||
|
||||
|
Quote:
Freedom Express Inspections LLC CMOR Thermography Certified Level 11 #2097 freedomexpressinspections.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F Professional Home Inspector State License # 130 Reporting system by Home Inspector Pro Serving the State of Okla. |
|
#3
|
|||
|
|||
|
I agree with Charley, recommend that the lack of adequate combustion air be corrected by a Pro in the field. Hard to believe the original local inspector missed this during the installation process.
You may be dealing with a replacement installation, where the contractor took it upon himself to make some changes. We see that a lot in my area of the country. |
![]() |