Some AC units require max. fuse or circuit breaker size of 25 amp. With 25 amp. disconnect fuses and #10 wire, is a 30 amp. breaker in the panel box acceptable?
Question #2: With an AC unit requiring max. fuse or circuit breaker size of 25 amp. is using 30 amp. disconnect fuses, #10 wire, and a 30 amp. breaker in the panel box acceptable? Thanks. |
| Find an InterNACHI certified New Jersey Home Inspector (and anywhere else in North America) |
|
#2
|
||||
|
||||
|
Please Note:
rmaday is a non-member guest and is in no way affiliated with InterNACHI or its members.
No, the disconnects are generally not overcurrent proitection.
No, max size is 25 amp. |
|
#3
|
|||
|
|||
|
Thanks Rick.
The reason for question #2 is I don't recall seeing any 25 amp. breakers. |
![]() |