Default AC clearance

Opinions of dryer vent and sump pump discharge behind AC at right.
Attached Thumbnails
ac-clearance-hpim7350.jpg   ac-clearance-hpim7358.jpg   ac-clearance-hpim7359.jpg  



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
Need a home inspection in Montana? Check out InterNACHI's listing of Montana certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 9/16/10, 8:38 AM
Kenneth Dolin's Avatar
Kenneth Dolin Kenneth Dolin is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Palm Beach County, Florida
Posts: 502
Default Re: AC clearance

Not exactly the most well thought out installation thats for sure. The dryer vent could cause future maintenance problems with discharging lint onto the condensing unit coil, but I am not sure if there is any other major concern, Is this new construction?



Ken Dolin
Kenco Home Inspections
WWW.Kenco.org
State of Florida Licensed Home Inspector HI 59
Reply With Quote
  #3  
Old 9/16/10, 9:16 AM
David P. OKeefe's Avatar
David P. OKeefe David P. OKeefe is offline
InterNACHI Member
 
Join Date: May 2008
Location: Delmar,, NY
Posts: 974
Default Re: AC clearance

The AC disconnect should not be directly behind the unit.



David

InterNACHI #08051301
NYS Lic. #16000038229
NYS DEC Cert # T4865884
518-505-8305
HouseAbout Home Inspections
HouseAbout on Facebook
NY Capital Region Chapter InterNACHI


Reply With Quote
  #4  
Old 9/16/10, 1:56 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: AC clearance

Quote:
Originally Posted by dokeefe View Post
The AC disconnect should not be directly behind the unit.

They are offset a little to the side and I was able to reach them without climbing over or removig anything.

IRC TABLE E4001.5 DISCONNECTING MEANS
Air-conditioning condensing units and heat pump units.
A readily accessible disconnect within sight from unit as the only allowable means.


ELECTRICAL DEFINITIONS
ACCESSIBLE,READILY. Capable of being reached quickly
for operation, renewal or inspections, without requiring those
to whom ready access is requisite to climb over or remove
obstacles or to resort to portable ladders, etc.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #5  
Old 9/16/10, 4:59 PM
matthew berman matthew berman is offline
New User
 
Join Date: Jan 2003
Posts: 1
Please Note: matthew berman is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: AC clearance

most mfg. instructions state 10 to 12 inches clear space around the unit for servicing and cleaning and good air flow
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Walking surface and wall clearance dbucknavich Exterior Inspections 9 5/27/08 6:07 AM
Clearance Testing tfarmer Ancillary Inspection Services & Additional Topics 15 2/26/08 5:41 PM
Range Clearance dsmith6 Interior Inspections 18 1/7/07 9:55 PM
Service panel clearance wwarner Electrical Inspections 13 8/12/06 12:07 PM
Siding to Ground Clearance tneumann Exterior Inspections 14 2/8/06 11:48 PM


All times are GMT -4. The time now is 10:03 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts