Question AC condenser fan ran when thermostat was in heat mode on "fan" setting

In my most recent inspection I turned the thermostat on its "fan" setting in heat mode with the temperature setting well below the air temperature to take a control reading for CO, and noticed the AC condenser fan was running.

The thermostat did have "heat", "off", and "cool" settings. The AC condenser was relatively old, manufactured in 1992.

There was cool air coming out of the condenser and the coolant line was not noticeably cold, but I found it alarming, given that even the unseasonably warm air temperature was still in the mid 50sF.

The heat mode operated normally when the thermostat fan setting was on "auto" and the mercury tipped over almost right on the air temperature.

I've never come across anything like this. Anybody know what was going on? Thermostat malfunction or improper wiring, or AC condenser issue?
Reply With Quote
Need a home inspection in Florida? Check out InterNACHI's listing of Florida certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 11/25/11, 10:31 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: AC condenser fan ran when thermostat was in heat mode on "fan" setting

Sounds as if ya had a heat pump with a gas secondary furnace. Hard to tell from here what ya had. If no heat pump ya got thermostat wiring problems.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #3  
Old 11/26/11, 12:56 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,925
Default Re: AC condenser fan ran when thermostat was in heat mode on "fan" setting

Bad thermostat sub-base.



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #4  
Old 11/26/11, 6:28 AM
ROBERT V. YOUNG's Avatar
ROBERT V. YOUNG ROBERT V. YOUNG is online now
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal.
Posts: 5,050
Default Re: AC condenser fan ran when thermostat was in heat mode on "fan" setting

Do you have photos of the HVAC?



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816
Reply With Quote
  #5  
Old 11/27/11, 1:22 AM
Frank L. Bartlo Frank L. Bartlo is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: SE Michigan
Posts: 236
Default Re: AC condenser fan ran when thermostat was in heat mode on "fan" setting

Appeared to be a typical 80% efficiency gas, forced air furnace of a relatively modern design for a 1993 manufacture date (Bryant). Probably thermostat issues.
Reply With Quote
  #6  
Old 11/27/11, 8:56 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: AC condenser fan ran when thermostat was in heat mode on "fan" setting

Quote:
Originally Posted by fbartlo View Post
Appeared to be a typical 80% efficiency gas, forced air furnace of a relatively modern design for a 1993 manufacture date (Bryant). Probably thermostat issues.
I have a 80% gas furnace on my own home with a heat pump outside don't assume anything



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Radiated Heat dhuxted Interior Inspections 31 10/3/10 1:49 PM
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues for Inspectors 50 4/20/08 1:26 AM
What is a 'condenser' dryer ?? rcooke Canadian Inspectors 9 9/9/07 7:02 PM
Radiant Ceiling Heat hhull Interior Inspections 9 7/26/07 8:19 AM


All times are GMT -4. The time now is 10:03 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts