Default AC condenser undersized - HI said nothing - to blame?

Some opinions please.

An agent at an inspection the other day tells me the plight of a family member of hers...

Bought a home, 80's construction. Alum. Dual Pane Windows. 2 story nearly 3200 sf, with basement, which isn now finished. Originally unfinished basement.

Not sure of Furnace size, but, the Condensing Coil was sized at 2 tons

She asks me what I think as she advised her family member to get 3 estimates, notify the HI of the oversight and "discuss". From what I gathered of the conversation, it sounded like estimates were obtained and this was headed to small claims. This is in an area that is regularly getting in the high 90's on a daily basis and the upper floor is not cooling below the low 80's

Anyway, my response was that:
HI's don't generally determine sizing of units, but it's fairly obvious that 2 tons is undersized for this structure. We advise if the unit is "functioning", not properly sized.

I also asked if the structure had additions. "Yes, the basement was converted" BINGO!

I indicated that although I felt on one hand that an experienced HI would notice that the unit was very undersized, I would have also inquired if this converted basement was permitted, as the space is likely to have threw off whatever calcs were originally thought of.

To me, this one is sooo undersized, I would have commented on it. But, do we say something about a 2 ton unit on a 1500 sf house... 2000 sf house? I mean, GEESH a 2 ton unit on a home over 3000 sf, in a hot area?

You get my picture.

I would think that if this one ends up in Small Claims, the HI gets fried there, unless he had something indicating a need for a 3rd party to come look at the AC unit by COE. I was told there wasn't, but haven't seen the report.



Home Inspections in Palmdale Lancaster California

Tim Spargo
Spec Rite Inspections
Commercial and Residential Inspections
Palmdale Lancaster Santa Clarita CA
661-317-5770








Reply With Quote
Need a home inspection in Idaho? Check out InterNACHI's listing of Idaho certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 7/24/10, 6:13 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,923
Default Re: AC condenser undersized - HI said nothing - to blame?

Is the system zoned?

Where is the house?

Quote:
Not sure of Furnace size, but, the Condensing Coil was sized at 2 tons
Are we sure about this?

How is the duct designed?

Where is it located?

Did they add the basement to this system?

How many and where are the returns?

How many and where are the supply registers.

Where is the thermostat?

What is the duct Air Leakage Rate?

What is the Duct Insulation rating?

What is the construction of the duct?

Where are the TAB duct dampers located? What dampers?!

Is the Barometric Damper properly adjusted?

What is the negative static return air duct pressure.

What is the friction loss design pressure of the duct design?

What is the CFM capacity of the furnace?

How much Insulation in the attic, walls and under the basement floor? What is the R-Value of each?

What is the U-Value of the windows?

What is the orientation of the house?

Is it shaded? To what extent?

How many ACH/hr does the house have?

What is the CFM of ventilation (mechanical)?

What is the normal building static pressures?

Where is the Neutral Plane?

Where in the house are they uncomfortable, what season?

Just a few questions then, I can take a stab at a "wild *** guess" from here!

And Lastly, why does she think a Home Inspector has ANYTHING to do with ANY of this?!



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission

Last edited by dandersen; 7/24/10 at 6:18 PM..
Reply With Quote
  #3  
Old 7/24/10, 6:15 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: AC condenser undersized - HI said nothing - to blame?

Quote:
Originally Posted by tspargo View Post
Some opinions please.

An agent at an inspection the other day tells me the plight of a family member of hers...

Bought a home, 80's construction. Alum. Dual Pane Windows. 2 story nearly 3200 sf, with basement, which isn now finished. Originally unfinished basement.

Not sure of Furnace size, but, the Condensing Coil was sized at 2 tons

She asks me what I think as she advised her family member to get 3 estimates, notify the HI of the oversight and "discuss". From what I gathered of the conversation, it sounded like estimates were obtained and this was headed to small claims. This is in an area that is regularly getting in the high 90's on a daily basis and the upper floor is not cooling below the low 80's

Anyway, my response was that:
HI's don't generally determine sizing of units, but it's fairly obvious that 2 tons is undersized for this structure. We advise if the unit is "functioning", not properly sized.

I also asked if the structure had additions. "Yes, the basement was converted" BINGO!

I indicated that although I felt on one hand that an experienced HI would notice that the unit was very undersized, I would have also inquired if this converted basement was permitted, as the space is likely to have threw off whatever calcs were originally thought of.

To me, this one is sooo undersized, I would have commented on it. But, do we say something about a 2 ton unit on a 1500 sf house... 2000 sf house? I mean, GEESH a 2 ton unit on a home over 3000 sf, in a hot area?

You get my picture.

I would think that if this one ends up in Small Claims, the HI gets fried there, unless he had something indicating a need for a 3rd party to come look at the AC unit by COE. I was told there wasn't, but haven't seen the report.
Once it gets to court the HI lost....

Hard spot to be in, technically I would say the HI is not liable for the undersized AC..................
Reply With Quote
  #4  
Old 7/24/10, 6:42 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,908
Default Re: AC condenser undersized - HI said nothing - to blame?

Home Inspectors do not calculate heat,electric or A/C systems.
Reply With Quote
  #5  
Old 7/24/10, 6:43 PM
Tim Spargo's Avatar
Tim Spargo Tim Spargo is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Lancaster, CA
Posts: 2,407
Default Re: AC condenser undersized - HI said nothing - to blame?

Quote:
Originally Posted by dandersen View Post
Is the system zoned?

Where is the house? Southern UT

Are we sure about this? Size? Yes

How is the duct designed? Unknown

Where is it located? Main Floor in Garage

Did they add the basement to this system? YEP!!! after the fact

How many and where are the returns? Air Handler is main/middle floor, return likely there, which is poorly placed anyway. But I'm ASSuming too much

What is the CFM capacity of the furnace? Unknown to me

What is the U-Value of the windows? Unsure, but they're aluminum... not great I'm sure


Where in the house are they uncomfortable, what season? Second floor is uncomfortably HOT... 80+ deg...

Just a few questions then, I can take a stab at a "wild *** guess" from here!

And Lastly, why does she think a Home Inspector has ANYTHING to do with ANY of this?!
<---- Scary, I agree. My thought too. But David, are there realistically any scenarios where a 2 ton AC would be sufficiently sized in a region that gets hot like that?

The other parts I did delete, I wasn't really told any more than that. But I realize that there are a lot of variable that you are pointing out!


BK... I agree there too! From the sound of it, he's already lost!



Home Inspections in Palmdale Lancaster California

Tim Spargo
Spec Rite Inspections
Commercial and Residential Inspections
Palmdale Lancaster Santa Clarita CA
661-317-5770








Reply With Quote
  #6  
Old 7/24/10, 6:45 PM
Tim Spargo's Avatar
Tim Spargo Tim Spargo is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Lancaster, CA
Posts: 2,407
Default Re: AC condenser undersized - HI said nothing - to blame?

Quote:
Originally Posted by belliott View Post
Home Inspectors do not calculate heat,electric or A/C systems.
I agree.

But, I posted this as the 2 ton size of the condensing coil vs a 3200 sf house in a hot area...

Just puttin' in out there for thought.



Home Inspections in Palmdale Lancaster California

Tim Spargo
Spec Rite Inspections
Commercial and Residential Inspections
Palmdale Lancaster Santa Clarita CA
661-317-5770








Reply With Quote
  #7  
Old 7/24/10, 6:53 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,950
Default Re: AC condenser undersized - HI said nothing - to blame?

If the inspector has a pre-inspection agreement describing the SOP he will use signed by him and the client, has no advertising promising to "exceed" the SOP, and inspected/reported in accordance with the SOP....he has not problem, whatsoever.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
  #8  
Old 7/24/10, 6:56 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: AC condenser undersized - HI said nothing - to blame?

Quote:
Originally Posted by tspargo View Post
I agree.

But, I posted this as the 2 ton size of the condensing coil vs a 3200 sf house in a hot area...

Just puttin' in out there for thought.
Why are you "puttin' it out there" at all? It's beyond the SOP period.

Yes, we all exceed the SOP at various times for various reasons, but "missing" something that is outside the SOP should be the NORM.



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #9  
Old 7/24/10, 7:09 PM
Tim Spargo's Avatar
Tim Spargo Tim Spargo is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Lancaster, CA
Posts: 2,407
Default Re: AC condenser undersized - HI said nothing - to blame?

Good Points, as I've said, I agree with our "duties".



Home Inspections in Palmdale Lancaster California

Tim Spargo
Spec Rite Inspections
Commercial and Residential Inspections
Palmdale Lancaster Santa Clarita CA
661-317-5770








Reply With Quote
  #10  
Old 7/24/10, 7:32 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,950
Default Re: AC condenser undersized - HI said nothing - to blame?

The SOP is the SOP.

The reason home inspections run close to $400 instead of $4,000 is because they are quick (three-hour) non-invasive and unscientific observations. It doesn't really matter who you are...less than a complete Manual J calculation for sizing the unit and ductwork is a guess. Calling out an undersized unit as a material defect is outside the scope of a home inspection.

I think you were wrong to tell the client that it was "obvious enough" for the HI to call out.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
  #11  
Old 7/24/10, 7:51 PM
Tim Spargo's Avatar
Tim Spargo Tim Spargo is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Lancaster, CA
Posts: 2,407
Default Re: AC condenser undersized - HI said nothing - to blame?

Wrong? Maybe, maybe not? I can assure you that I let it be known that an inspection is not to determine the size/adequacy of appliances like this.

After all, this was at a HI I was performing, I had a vested interest in explaining such things.

But, just as I would comment about a 30 gal water heater in a 5 bedroom 3.5 bath home, if I noticed that a 2 ton unit was serving a 3200sf home, I'd probably make mention of it, especially if there were alterations/additions to the property. Do I have to? Nope.



Home Inspections in Palmdale Lancaster California

Tim Spargo
Spec Rite Inspections
Commercial and Residential Inspections
Palmdale Lancaster Santa Clarita CA
661-317-5770








Reply With Quote
  #12  
Old 7/24/10, 8:49 PM
Joe Farsetta's Avatar
Joe Farsetta Joe Farsetta is offline
ESOP Committee Member
 
Join Date: Oct 2002
Location: Pearl River, NY
Posts: 4,115
Default Re: AC condenser undersized - HI said nothing - to blame?

In most states, the sole person LEGALLY qualified to calculate the size of an HVAC system is a PE.

This is far beyond the scope of a home inspection. Providing the HI colored between the lines, he should be okay.

David Anderson provides an excellent range of questions that are considered when evaluating the needs of a dwelling and sizing the HVAC properly. While he may have the wherewithall to comment intelligently, a majority of inspectors simply do not.

I can almost guarantee that what David rattled off the top of his head were things not learned in any HI class...
Reply With Quote
  #13  
Old 7/24/10, 8:59 PM
Tim Spargo's Avatar
Tim Spargo Tim Spargo is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Lancaster, CA
Posts: 2,407
Default Re: AC condenser undersized - HI said nothing - to blame?

Quote:
Originally Posted by jfarsetta View Post
In most states, the sole person LEGALLY qualified to calculate the size of an HVAC system is a PE.

This is far beyond the scope of a home inspection. Providing the HI colored between the lines, he should be okay.

David Anderson provides an excellent range of questions that are considered when evaluating the needs of a dwelling and sizing the HVAC properly. While he may have the wherewithall to comment intelligently, a majority of inspectors simply do not.

I can almost guarantee that what David rattled off the top of his head were things not learned in any HI class...

Good point Joe.. David's list may and parts of this post may be a good reply some day...



Home Inspections in Palmdale Lancaster California

Tim Spargo
Spec Rite Inspections
Commercial and Residential Inspections
Palmdale Lancaster Santa Clarita CA
661-317-5770








Reply With Quote
Need a home inspection in Idaho? Check out InterNACHI's listing of Idaho certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 7/24/10, 9:42 PM
David Garton's Avatar
David Garton David Garton is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Northern CA.
Posts: 277
Default Re: AC condenser undersized - HI said nothing - to blame?

Quote:
Originally Posted by tspargo View Post
Wrong? Maybe, maybe not? I can assure you that I let it be known that an inspection is not to determine the size/adequacy of appliances like this.

After all, this was at a HI I was performing, I had a vested interest in explaining such things.

But, just as I would comment about a 30 gal water heater in a 5 bedroom 3.5 bath home, if I noticed that a 2 ton unit was serving a 3200sf home, I'd probably make mention of it, especially if there were alterations/additions to the property. Do I have to? Nope.
I would probably do the same thing Tim but that's just my opinion



David Garton
Eagle Eye Inspection Services
david@yubacityhomeinspection.com
http://yubacityhomeinspection.com
Licensed Building Contractor
Serving Yuba City, CA. and the surrounding areas
(530) 415-1269
Reply With Quote
  #15  
Old 7/24/10, 11:16 PM
Mark Thorman Mark Thorman is offline
Unmoderated Guest
 
Join Date: Mar 2008
Posts: 392
Please Note: Mark Thorman is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: AC condenser undersized - HI said nothing - to blame?

Quote:
Originally Posted by tspargo View Post
Wrong? Maybe, maybe not? I can assure you that I let it be known that an inspection is not to determine the size/adequacy of appliances like this.

How many inspectors include the size of a system in the report.

www.MauiHomeInspections.com
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues for Inspectors 50 4/20/08 1:26 AM
HVAC condenser clearances cfolsom Inspecting HVAC Systems 7 11/22/07 3:03 PM
What is a 'condenser' dryer ?? rcooke Canadian Inspectors 9 9/9/07 7:02 PM
oily reside on condenser valve Mel Olinsky Inspecting HVAC Systems 2 7/13/07 7:01 PM