Default Re: AC condenser undersized - HI said nothing - to blame?

Quote:
Originally Posted by dandersen View Post
Where here does it say anything about any of that?

I. The inspector shall inspect:

A. the central cooling equipment using normal operating controls.


Then what are we supposed to do with any information we gather when we DO "inspect", i.e., "run" the system?

Why even run the darn thing then if we don't report on any noted deficiencies, and believe me, not cooling properly could be deemed an deficiency, ya think?
Reply With Quote
Need a home inspection in Vermont? Check out InterNACHI's listing of Vermont certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #32  
Old 7/27/10, 4:08 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,686
Default Re: AC condenser undersized - HI said nothing - to blame?

What is proper cooling?

When you turn on a light at a light switch and it doesn't come on:

Do you run to town and get a new lightbulb?

Do you get a voltage meter and test the circuit?

Do you determine if it's a two way switch on a three-way circuit?

Do you dismantle the lighting fixture to see if there are burnt wires or bad connections or if the lightbulb was loose?

Do you dismantle the switch and do an Ohm's test on the device?

If the light does come on:

Do you determine the wattage draw through the circuit in comparison to the lightbulb in the socket?

Do you do a voltage drop test.

Do you check the luminaires and manufacturers data sheet for the lightbulb?

We run the darn thing to see if things turn on...

The extent of our testing is to feel the air and see if it is warmer or cooler than the ambient temperature within the house.

This example may seem far-fetched but it is exactly what a real HVAC analysis does and it is something that home inspectors do not do.



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #33  
Old 7/28/10, 12:48 AM
jhugenroth jhugenroth is offline
InterNACHI Member
 
Join Date: May 2004
Location: Fresno, CA
Posts: 1,152
Please Note: jhugenroth is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: AC condenser undersized - HI said nothing - to blame?

Quote:
Originally Posted by [dandersen[/b
;675689]What is proper cooling?
I would think the example cited above where the upper story was not cooling would be a good example of improper cooling.

Maybe I misunderstood your intent, but it seemed you were disagreeing with Bill Siegel's post about a HI being negligent for not reporting that.
Reply With Quote
  #34  
Old 7/28/10, 7:17 AM
Billy Boerner's Avatar
Billy Boerner Billy Boerner is offline
InterNACHI Member
 
Join Date: Jun 2008
Location: St. Louis, MO
Posts: 7,204
Send a message via Yahoo to bboerner
Default Re: AC condenser undersized - HI said nothing - to blame?

Quote:
Originally Posted by dedwards View Post
I suppose a better question here is, "How many inspectors go over what the inspection covers, to what depth and the limitations of a visual inspection" before they ever start. It only takes a couple of minutes and for me has been a central part of NOT having this kind of misunderstanding. Then further explain that anything beyond that requires the services of a licensed tradesman in that discipline. Then I go over this again at the end when we are finished. Is the inspector in too much of a hurry to get that on site report generated and get to that next inspection and doesn't take the time to make sure the customer understands ALL of the issues with the home? Or does the inspector just provide the customer with a copy of the SOP, which they know the customer will never read, and hope for the best.

It is the easiest thing in the world for an inspector to simply say, not just in writing, but actually SAY to their customer, " I AM NOT QUALIFIED" to make that kind of determination and you will need the services of a licensed HVAC (or electrician, or plumber, etc.) contractor. Trying to appear that we know everything is what is the root cause of this. No one wants to admit they don't know something and it is going to start biting people in the ***, or already has.
One of the greatest post I've ever read here at NACHI.



Bill Boerner
STL Home Inspection Services
Serving St. Louis/Surrounding
(314) 805-2137
billy.boerner@gmail.com
http://www.stlhomeinspector.com


Reply With Quote
  #35  
Old 7/28/10, 2:46 PM
Mark Thorman Mark Thorman is offline
Unmoderated Guest
 
Join Date: Mar 2008
Posts: 392
Please Note: Mark Thorman is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: AC condenser undersized - HI said nothing - to blame?

I'm sorry but I can not understand this cover your xxx at the expense of our clients best interests mentality. If you are a certified inspector or master inspector you should know the minimum system requirements for all the systems of a home. SOP's are weak, the buyer does not need us to come in and just turn stuff on and say it functions, I'm done, pay me. The original post is in regard to a significantly under sized condenser. No technical expertise is needed, just a basic understanding of what it takes to cool a house of that size. Stop defending sub qualified inspectors. Raise the bar and everyone will be happy (except some agents).

www.MauiHomeInspections.com

Last edited by Mark Thorman; 7/28/10 at 8:02 PM..
Reply With Quote
  #36  
Old 7/28/10, 3:09 PM
Tim Spargo's Avatar
Tim Spargo Tim Spargo is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Lancaster, CA
Posts: 2,270
Default Re: AC condenser undersized - HI said nothing - to blame?

Quote:
Originally Posted by Mark Thorman View Post
I'm sorry but I can not understand this cover your xxx at the expense of our clients best interests mentality. If you are a certified inspector or master inspector you should know the minimum system requirements for all the systems of a home. SOP's are weak, the buyer does need us to come in and just turn stuff on and say it functions, I'm done, pay me. The original post is in regard to a significantly under sized condenser. No technical expertise is needed, just a basic understanding of what it takes to cool a house of that size. Stop defending sub qualified inspectors. Raise the bar and everyone will be happy (except some agents).

www.MauiHomeInspections.com
Good Point Mark.

I gave the benefit of the doubt of the sizing when I posted the question/topic. I felt there were more than one reasons to have "punted" this one if I had done the inspection. We can't all agree.

I thought it was a "bit" undersized as well. This topic of "sizing" is a bit tricky, but IMO the example I laid out... wasn't. All things aside, if a home appears un-altered, I would agree that being concerned with the size of a system is beyond a HI. There were other aspects of the post...

All the variables of the system aside... the fact the home had alterations/additions, the poor cooling taking place at the time of inspection coupled with the size of the unit would have had me "punt" this one to an HVAC contractor for review.



Home Inspections in Palmdale Lancaster California

Tim Spargo
Spec Rite Inspections
Commercial and Residential Inspections
Palmdale Lancaster Santa Clarita CA
661-317-5770








Reply With Quote
  #37  
Old 7/28/10, 8:22 PM
Mark Thorman Mark Thorman is offline
Unmoderated Guest
 
Join Date: Mar 2008
Posts: 392
Please Note: Mark Thorman is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: AC condenser undersized - HI said nothing - to blame?

I think Texas has the right idea. If you look at the nachi (and the other nationally recognized inspector association whose name can not be mentioned) and look at the Texas standards. I would hire the Texas inspector first.

Texas:
(b) Cooling equipment other than evaporative coolers.
The inspector shall:
(1) report the type of system(s); and
(2) report as Deficient:
(A) inoperative unit(s);
(B) inadequate cooling as demonstrated by its performance in the reasonable judgment of the inspector;
(C) inadequate access and clearances;
(D) noticeable vibration of the blower fan or condensing fan;
(E) deficiencies in the condensate drain and auxiliary/secondary pan and drain system;
(F) water in the auxiliary/secondary drain pan;
(G) a primary drain pipe that terminates in a sewer vent;
(H) missing or deficient refrigerant pipe insulation;
(I) dirty evaporator or condensing coils, where accessible;
(J) damaged casings on the coils;
(K) a condensing unit lacking adequate clearances or air circulation or that has deficiencies in the condition of fins, location, levelness, or elevation above ground surfaces;
(L) deficiencies in mounting and operation of window or wall units; and
(M) deficiencies in thermostats.

verses Nachi

2.5. Cooling
I. The inspector shall inspect:
A. the central cooling equipment using normal operating controls.
II. The inspector is not required to:
A. determine the uniformity, temperature, flow, balance, distribution, size, capacity, BTU, or supply adequacy of the cooling system.
B. inspect window units, through-wall units, or electronic air filters.
C. operate equipment or systems if exterior temperature is below 60 degrees Fahrenheit, or when other circumstances are not conducive to safe operation, or may damage the equipment.
D. inspect or determine thermostat calibration, cooling anticipation, or automatic setbacks or clocks.
E. examine electrical current, coolant fluids or gases, or coolant leakage.


Who would you hire?

www.MauiHomeInspections.com
Reply With Quote
  #38  
Old 7/28/10, 8:41 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,557
Default Re: AC condenser undersized - HI said nothing - to blame?

(B) inadequate cooling as demonstrated by its performance in the reasonable judgment of the inspector

And how on earth would one determine that on a 70 degree day?



He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father

The democracy will cease to exist when you take away from those who are willing to work and give to those who would not. Thomas Jefferson

Never underestimate the difficulty of changing false beliefs by facts.
- Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
and
Minnesota Home Inspector

Reply With Quote
  #39  
Old 7/28/10, 8:44 PM
Doug Edwards,  CMI's Avatar
Doug Edwards, CMI Doug Edwards,  CMI is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Florida panhandle
Posts: 4,760
Default Re: AC condenser undersized - HI said nothing - to blame?

(B) inadequate cooling as demonstrated by its performance in the reasonable judgment of the inspector

Oh no, that is not subjective statement, especially when the inspector doesn't know s**t from shoe polish of how an HVAC system even works. Most think its black magic or something judging from comments just on this board.



"War is an ugly thing, but not the ugliest of things; the decayed and degraded state of moral and patriotic feeling which thinks nothing is worth a war, is worse. A man who has nothing which he cares more about than he does about his personal safety is a miserable creature who has no chance at being free, unless made and kept so by the exertions of better men than himself."

- John Stuart Mill







Reply With Quote
  #40  
Old 7/28/10, 9:01 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,686
Default Re: AC condenser undersized - HI said nothing - to blame?

Quote:
I would think the example cited above where the upper story was not cooling would be a good example of improper cooling.
It can just as easily be the result of improper building performance and have anything to do with the operation of the HVAC equipment.

Quote:
All the variables of the system aside... the fact the home had alterations/additions, the poor cooling taking place at the time of inspection coupled with the size of the unit would have had me "punt" this one to an HVAC contractor for review.
Actually if I walk into any house that has three floors and one HVAC system, unless it has a computer room to control it it's wrong.

As in most cases, there is insufficient information to formulate any decision here. We can't be speculating without any facts.



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #41  
Old 7/28/10, 9:24 PM
Mark Thorman Mark Thorman is offline
Unmoderated Guest
 
Join Date: Mar 2008
Posts: 392
Please Note: Mark Thorman is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: AC condenser undersized - HI said nothing - to blame?

Quote:
Originally Posted by dedwards View Post
(B) inadequate cooling as demonstrated by its performance in the reasonable judgment of the inspector

Oh no, that is not subjective statement, especially when the inspector doesn't know s**t from shoe polish of how an HVAC system even works. Most think its black magic or something judging from comments just on this board.
Then they should be trained and tested before they can claim to be a Professional Home Inspector.
Reply With Quote
  #42  
Old 7/29/10, 12:12 AM
Dan Bowers, CMI Dan Bowers, CMI is offline
InterNACHI Member
 
Join Date: Oct 2003
Location: Shawnee Mission, KS
Posts: 3,586
Default Re: AC condenser undersized - HI said nothing - to blame?

Quote:
Originally Posted by jfarsetta View Post
In most states, the sole person LEGALLY qualified to calculate the size of an HVAC system is a PE.

This is far beyond the scope of a home inspection. Providing the HI colored between the lines, he should be okay.

I can almost guarantee that what David rattled off the top of his head were things not learned in any HI class...
__________________________________

Joe -

You give a PE too much credit. Most that I know are not qualified to do this. I've lived in 8 states in my life AND have NOT yet seen one where ONLY a PE is legally qualified to calculate the size of an HVAC system.

This may BE the norm where you live (or it may NOT), BUT comments like this from a veteran inspector can really confuse new inspectors if they believe them.
Reply With Quote
  #43  
Old 7/29/10, 12:32 AM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,862
Default Re: AC condenser undersized - HI said nothing - to blame?

My AC is currently not working properly, and I did not perform any "tests" whatsoever to determine this..

The tech is coming out at 08:00 to determine the cause and rectify the situation.

AC is pretty common here in Phoenix and pretty much even someone's Mom can tell if the AC is working or not. It seems other parts of the country AC may be a little trickier to operate.
Reply With Quote
Need a home inspection in Vermont? Check out InterNACHI's listing of Vermont certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #44  
Old 7/29/10, 8:42 AM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,103
Default Re: AC condenser undersized - HI said nothing - to blame?

Heating and air is one of the main items that separate the minimal inspectors from the top rated ones. I think most that participate on this board are looking to be the best in their area while the minimal guy's have their reports done by 4 pm and could care less about anything other than pleasing agents.

What David is saying is technically correct but what he is not saying is how to report things like a "warm upstairs" condition.

I had a similar situation and simply reported the fact that the upstairs was warmer than what I normally see and to have an HVAC tech check it out. I did not state what was wrong even though I knew it had a problem with the zoning panel.

The client ended up getting an entire new system paid for by the seller since the sellers tech had no idea how to repair the zoning panel but knew how to install a new system.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #45  
Old 7/29/10, 10:39 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,686
Default Re: AC condenser undersized - HI said nothing - to blame?

Quote:
The client ended up getting an entire new system paid for by the seller since the sellers tech had no idea how to repair the zoning panel but knew how to install a new system.
Oh my!
Was this one of those professionals we are supposed to defer to?
The one Billy B wants to "sign off" on the job?


Had New construction last week with a zoned system.
No barometric damper.
They looked at me cross eyed when I inquired where it was...



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues for Inspectors 50 4/20/08 2:26 AM
HVAC condenser clearances cfolsom Inspecting HVAC Systems 7 11/22/07 4:03 PM
What is a 'condenser' dryer ?? rcooke Canadian Inspectors 8 9/9/07 8:02 PM
oily reside on condenser valve Mel Olinsky Inspecting HVAC Systems 2 7/13/07 8:01 PM


All times are GMT -4. The time now is 1:37 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts