Default AC Drain

What are your thoughts on this set up?

Attachment 14069



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com

Last edited by nbhi; 7/8/08 at 9:42 AM..
Reply With Quote
  #2  
Old 8/21/07, 10:00 PM
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 11,733
Default Re: AC Drain

Should have a trap.



"Never ever threaten anyone in Camoflage"
Tim Wilson

"Not everyone follows the same path"
Governor Sanford, musings on the Appalachian Trail
Reply With Quote
  #3  
Old 8/21/07, 10:23 PM
rcooke rcooke is offline
Banned for Violating COE
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 9,381
Please Note: rcooke is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: AC Drain

Quote:
Originally Posted by bkelly2
Should have a trap.
I wonder is a trap required when it is open at the top of the T?

........... Cookie
Reply With Quote
  #4  
Old 8/21/07, 10:36 PM
Brian A. MacNeish Brian A. MacNeish is offline
Active Poster
 
Join Date: Apr 2007
Posts: 2,382
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: AC Drain

Quote:
Originally Posted by bkelly2
Should have a trap.
And the "T" should be taken out and replaced with solid closed piping. The hole in the plenum for the drain should be sealed as are the openings for the refrigerant lines just above. Both of these items are allowing conditioned air leakage to the mechanical room.

In residential duct systems, research has found that 20-30%+ of the air moving through the fan or air handling unit (AHU) does not come from or get to areas for which it was designed!! This is one reason why some rooms/areas may be hard to heat or cool. The HVAC unit may be properly sized for the building but if air isn't moving properly......the system ain't gonna do its job.

I have rarely (and I mean RARELY) seen sealed and insulated residential ducts in my area for air conditioning systems! If anyone has access to HOME ENERGY magazine, check the articles about duct leakage and sealing. Their website is: http://www.homeenergy.org/ . It appears to be all subscription nowadays. A quick search showed over 40 articles with "duct leakage" mentioned.
Reply With Quote
  #5  
Old 8/22/07, 2:40 AM
Scott Gilligan,  CMI's Avatar
Scott Gilligan, CMI Scott Gilligan,  CMI is online now
InterNACHI Member
 
Join Date: May 2007
Location: Philadelphia, PA
Posts: 1,321
Send a message via AIM to sgilligan1 Send a message via MSN to sgilligan1 Send a message via Yahoo to sgilligan1
Default Re: AC Drain

This is the first time I have seen anything but PVC used for a condensate drain line. I wonder, since the lack of constant flow of water would cause that galvenized T fitting to rust and clog the line. Why use copper and a galvenized fitting? There is too much potential for corrosion in my opinion.
Reply With Quote
  #6  
Old 8/22/07, 2:47 AM
Ted Allen Ted Allen is offline
Active Poster
 
Join Date: Oct 2003
Posts: 3,156
Please Note: tallen is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: AC Drain

Quote:
Originally Posted by nbhi
What are your thoughts on this set up?

Attachment 14069
I think it is fine... It meets all the requirments that I can think of right now, but I could be wrong, I would need to check the code, and I suggest you do the same.
Reply With Quote
  #7  
Old 8/22/07, 2:48 AM
Ted Allen Ted Allen is offline
Active Poster
 
Join Date: Oct 2003
Posts: 3,156
Please Note: tallen is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: AC Drain

Quote:
Originally Posted by bkelly2
Should have a trap.
I have a feeling that the trap is conceiled in that box, but if not BK is absolutly correct.


Pictures are soooo hard to analize..
Reply With Quote
  #8  
Old 8/22/07, 2:51 AM
Ted Allen Ted Allen is offline
Active Poster
 
Join Date: Oct 2003
Posts: 3,156
Please Note: tallen is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: AC Drain

Quote:
Originally Posted by bkelly2
Should have a trap.
I have a feeling that the trap is conceiled in that box, but if not BK is absolutly correct.



9-12 days left. I just don't know............
Reply With Quote
  #9  
Old 8/22/07, 6:23 AM
Gary Schering, II's Avatar
Gary Schering, II Gary Schering, II is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Hamilton, OH
Posts: 695
Default Re: AC Drain

There is no cap on the T, allowing air to enter or escape unit. Without dismantling the pump, I am speculating there is no trap.



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
  #10  
Old 8/22/07, 12:06 PM
sparksnmore sparksnmore is offline
Active Poster
 
Join Date: Oct 2006
Posts: 156
Please Note: sparksnmore is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: AC Drain

Quote:
Originally Posted by nbhi
What are your thoughts on this set up?

Attachment 14069
1) Old galvanized fittings are so hard to remove without destroying the "A" coil's drain pan.

2) The tee is good for a clean-out but could have a plug installed. (many are left open)

3) Copper pipe used for condensate drain lines sweat.

4) No trap necessary and no reason for one unless it's connected to the sanitary sewer and then it would need an air gap.
Reply With Quote
  #11  
Old 8/22/07, 12:54 PM
Scott A. Figert Scott A. Figert is offline
InterNACHI Member
 
Join Date: Apr 2006
Location: Cecil, Oh
Posts: 163
Default Re: AC Drain

A trap is always necessary! As the air is pushed thru the A-coil it can create a vacuum on the drain at the tee or from the drain line itself. As a vacuum is created the condesate water may not run out, it may then build up & overflow in the A-coil pan down into the furnace or duct work, rusting & rotting where ever it goes. This is the same way a power washer with a soap injector works.
If draining to a sewer drain, an open drain system is required.
If draining to the outside, a closed line is OK. Installing an air vent is a good idea after the trap, but not before.
With that system you also have a galvanized to copper connection. These 2 metals corrode each other.



Scott A. Figert
www.sfigert.com
www.nachi.org NACHI #06042595
Figert Building Inspection, Ltd.
(419) 399-4472 Office & Home Sweet Home

Last edited by sfigert; 8/22/07 at 12:58 PM..
Reply With Quote
  #12  
Old 8/22/07, 3:36 PM
sparksnmore sparksnmore is offline
Active Poster
 
Join Date: Oct 2006
Posts: 156
Please Note: sparksnmore is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: AC Drain

Quote:
Originally Posted by sfigert
A trap is always necessary! As the air is pushed thru the A-coil it can create a vacuum on the drain at the tee or from the drain line itself. As a vacuum is created the condesate water may not run out, it may then build up & overflow in the A-coil pan down into the furnace or duct work, rusting & rotting where ever it goes. This is the same way a power washer with a soap injector works.
If draining to a sewer drain, an open drain system is required.
If draining to the outside, a closed line is OK. Installing an air vent is a good idea after the trap, but not before.
With that system you also have a galvanized to copper connection. These 2 metals corrode each other.
With all due respect;

On the thousands of systems I've ever seen or installed in the last 40 some years, the air pressure blowing out actually helps the condensate water drain out faster and better.

The only time a trap is needed other than what i mentioned above is IF the drain stub is on the negative pressure side of an evaporator coil where the blower is sucking air through and a suction is created, drawing the condensate backwards up the pipe.

Maybe this is a local thing but there are NO traps on any AH's/furnaces around my part of the country with the exception of a few mentioned above.
Most of the condensate drains are just terminated on top of a floor drain, there are very few indirect drains with air gaps or in the case of second floor/attic units most terminate outside.

Last edited by sparksnmore; 8/22/07 at 3:41 PM..
Reply With Quote
  #13  
Old 8/25/07, 9:28 PM
Michael D. Thomas Michael D. Thomas is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Evanston, IL
Posts: 639
Default Re: AC Drain

"The IPC specifies that the piping material for the condensate drainpipe should be cast iron, galvanized steel, copper, crosslinked polyethylene, polybutylene, polyethylene, ABS, PVC, or PVC pipe or tubing. All components shall be selected for the pressure and temperature rating of the installation. The UPC species that the condensate drain piping shall be constructed of material specified in Chapter 7, which deals with sanitary drainage. Therefore, all condensate drainage piping shall be the same as that for sanitary drainage. One problem with this is that the smallest drainage pipe is 1¼ inch, and many times the condensate drain pipe is ¾ inch or 1 inch. If this is the case, water tubing or pipe must be used."

http://www.psdmagazine.com/ASPE_memb...CodeUpdate.pdf

All manufacturers I've encountered require a trap on a condensate drain under positive pressure, if you see an untrapped discharge, check the manufacturer's instructions; an untrapped positive pressure condensate drain is exhausting cooled air to wherever the drain is discharging. The secondary should be trapped for the same reason - some AC techs suggest using mineral oil for the trap seal on the secondary as the oil does not evaporate.

This, from is from the Trane web site, is typical:

"A properly functioning (and properly designed) condensate trap provides for discharge of water from the cooling coil drain pan, while the water seal (the water level maintained in the trap) prevents the flow of ambient air into or out of the air handler. Several problems result from improperly trapped systems, some of which can severely impact indoor air quality. Our discussion will center on negative pressure systems, since trap failure in a positive pressure environment simply results in air being exhausted through the drain line."

That we see it done otherwise "all the time" does not make it "right".

Last edited by mthomas2; 8/25/07 at 9:49 PM..
Reply With Quote
  #14  
Old 8/27/07, 3:52 PM
sparksnmore sparksnmore is offline
Active Poster
 
Join Date: Oct 2006
Posts: 156
Please Note: sparksnmore is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: AC Drain

That is very interesting but at the same time very strange because there are at least a couple of million 3/4" un-trapped condensate drains around here.

None of the HVAC installers would ever think of putting an unnecessary trap on a condensate line.
keep in mind most all are terminating inside, close to the air handler/furnace on top of a basement floor drain.

I've yet to see any manufacturer's instructions that ever suggested installing an unnecessary trap albeit I've not installed every brand, only a few so that leaves many I haven't seen.

Yes, a little cold air is lost but percentage wise it's just a tiny drop in the bucket compared to several 6/7" pipes discharging the air.
I mean, you can't force very much air through a 3/4" pipe no matter how hard you try.
Reply With Quote
  #15  
Old 8/27/07, 11:22 PM
Brian A. MacNeish Brian A. MacNeish is offline
Active Poster
 
Join Date: Apr 2007
Posts: 2,382
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: AC Drain

Quote:
Originally Posted by sparksnmore
Yes, a little cold air is lost but percentage wise it's just a tiny drop in the bucket compared to several 6/7" pipes discharging the air.
I mean, you can't force very much air through a 3/4" pipe no matter how hard you try.
Sparks:

Remember that residential duct systems, in general, leak a hell of a lot of air- 20-30% by a few estimates and some research!! By contrast, well designed and installed engineered systems that undergo air leakage testing as part of the commissioning process (I used to do this) fail at 3-5% air leakage (depending on the specifier).........the contractor is then back to sealing all ducts again......a bad thing. In residential, any leak of 2-3+ cfm should be addressed since it's a larger % of a smaller airflow in the 7-800 to 1500-2000 cfm residential range versus 5-15,000 cfm in commercial and similar sized buildings.

We should be setting our sights higher, maybe doing some re-training and if all else fails (I'm sure you've heard this before), read the instructions.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Child eviscerated by pool drain mthomas2 Ancillary Services & Additional Topics 26 7/16/07 5:27 PM
Air leak from floor drain yolhovsky Plumbing 5 2/24/07 7:43 AM
French drain tied into main drain rwashington Plumbing 6 2/17/07 12:04 AM
Exposed drain and plumbers putty tneumann Plumbing 19 4/27/06 11:57 PM
Washer Secondary Drain roconnor Plumbing 7 4/2/06 2:02 PM


All times are GMT -4. The time now is 3:49 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts