Hi,

I am new to HI industry. Just completed an inspection in Pensecola Florida. There were two 2 ton (all electric) units in a new three story -duplex.
In the attic, the plenum had a A/C duct with a louver. The louver wasn't sealed all the way, and cold air was discharging into the attic. It seemed to me,that this should have been sealed (capped) off. Can anyone explain if this is common? Thanks.
Reply With Quote
  #2  
Old 9/9/08, 3:58 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is online now
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 4,193
Send a message via Yahoo to jfunderburk
Default Re: AC duct not sealed

Picture?



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #3  
Old 9/9/08, 4:48 PM
Gerry Beaumont's Avatar
Gerry Beaumont Gerry Beaumont is online now
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 5,964
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: AC duct not sealed

Quote:
Originally Posted by Lisa Bloemer
Hi,

I am new to HI industry. Just completed an inspection in Pensecola Florida. There were two 2 ton (all electric) units in a new three story -duplex.
In the attic, the plenum had a A/C duct with a louver. The louver wasn't sealed all the way, and cold air was discharging into the attic. It seemed to me,that this should have been sealed (capped) off. Can anyone explain if this is common? Thanks.
Was this a sealed or vented attic?

Regards

Gerry



Virtue is more to be feared than vice, because its excesses are not subject to the regulation of conscience.
Adam Smith (1723-1790)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106
Reply With Quote
  #4  
Old 9/9/08, 5:27 PM
Lisa Bloemer Lisa Bloemer is offline
New User
 
Join Date: Sep 2008
Posts: 3
Please Note: Lisa Bloemer is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: AC duct not sealed

Here are two photos of the opened duct. The attic had foam insulation throughout it extending to the soffit. No space for soffit air circulation. Is this considered okay? I thought insulation should never be over soffit vent area.
Attached Thumbnails
ac-duct-not-sealed-.c-duct-louver.jpg   ac-duct-not-sealed-ac-duct-louver-open-plenum.jpg  
Reply With Quote
  #5  
Old 9/9/08, 6:33 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 3,930
Default Re: AC duct not sealed

That is a balancing damper and the duct to it is missing!

Any air leak (regardless of size)results in the same volume of unconditioned air being drawn into the conditioned house.

First you loose the conditioned air, then you replace it with unconditioned air that loads the system (beyond capacity in many cases).

Also the building goes into a negative atmospheric pressure that draws all kinds of potential natural pollutants (radon, mold spores).



David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Certified Level II Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620

Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #6  
Old 9/9/08, 7:06 PM
Mark Nahrgang's Avatar
Mark Nahrgang Mark Nahrgang is online now
InterNACHI Member
 
Join Date: Apr 2007
Location: Saint Peters, MO
Posts: 4,482
Default Re: AC duct not sealed

Since they sprayed the roof, could it be that they converted the attic to "conditioned space"? Instead of the traditional vented unconditioned. You mentioned that they insulated over the vents...
Reply With Quote
  #7  
Old 9/9/08, 8:11 PM
Mark Thorman Mark Thorman is offline
Unmoderated Guest
 
Join Date: Mar 2008
Posts: 193
Please Note: Mark Thorman is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: AC duct not sealed

Did you check air flow to all the resisters and was there a register in every room?

www.mauihomeinspections.com
Reply With Quote
  #8  
Old 9/9/08, 11:01 PM
Brian A. MacNeish Brian A. MacNeish is online now
Active Poster
 
Join Date: Apr 2007
Posts: 2,437
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: AC duct not sealed

Quote:
Originally Posted by mnahrgang
Since they sprayed the roof, could it be that they converted the attic to "conditioned space"? Instead of the traditional vented unconditioned. You mentioned that they insulated over the vents...
Looks and sounds like they did indeed create (or try to create) a conditioned attic. This duct take off should be sealed but being unsealed is not as big a problem as some may think.
Reply With Quote
  #9  
Old 9/10/08, 12:47 AM
cbottger's Avatar
cbottger cbottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,738
Default Re: AC duct not sealed

Quote:
Originally Posted by Brian A. MacNeish
Looks and sounds like they did indeed create (or try to create) a conditioned attic. This duct take off should be sealed but being unsealed is not as big a problem as some may think.
I don't necessarily agree but I will bite your take please---)))



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #10  
Old 9/10/08, 9:08 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 3,930
Default Re: AC duct not sealed

I'm waiting also!

To start with, you don't put a supply into a closed space without a return or it will pressurize the space forcing air through the walls/roof to the exterior which is an efficiency concern.
If you blow conditioned air into the attic where does the displaced air go?

Two HVAC systems for three floors, and now they're going to air condition the attic in Florida? Yeah, right!

How many CFM are you getting through that closed four-inch takeoff? Not enough to cool the attic, that's for sure. The result is you still have hot air in the attic and you're forcing it around the ceiling penetrations and into the walls of the house. That sounds like good planning and design.

These new energy standards are really screwing things up.

By the way, I'm not directing this at you Lisa.




David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Certified Level II Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620

Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #11  
Old 9/10/08, 9:43 AM
Brian A. MacNeish Brian A. MacNeish is online now
Active Poster
 
Join Date: Apr 2007
Posts: 2,437
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: AC duct not sealed

Quote:
Originally Posted by dandersen
I'm waiting also!

To start with, you don't put a supply into a closed space without a return or it will pressurize the space forcing air through the walls/roof to the exterior which is an efficiency concern.
If you blow conditioned air into the attic where does the displaced air go?

Two HVAC systems for three floors, and now they're going to air condition the attic in Florida? Yeah, right!

How many CFM are you getting through that closed four-inch takeoff? Not enough to cool the attic, that's for sure. The result is you still have hot air in the attic and you're forcing it around the ceiling penetrations and into the walls of the house. That sounds like good planning and design.

These new energy standards are really screwing things up.

By the way, I'm not directing this at you Lisa.

This is a conditioned attic, sealed off from the exterior by spray foam. The amount of air leaking around this small closed damper may be what...8-10-15 CFM in a system of 1000-2000 CFM......not a big deal and it is into a conditioned space. Jeez, a 4" duct is only rated to carry 40 CFM in good designs.

Residential duct systems are usually unsealed and not even close to good spec'd work seen in commercial, etc. I have seen studies from Home Energy magazine and others that claim that 20-40% of the air moving through the air handler does not come from or get to the intended grills/diffusers.....the ducts are generally so leaky!!!!! So to me this is not a big flaw but still should be sealed.....I just wouldn't hang a big, red flag on it!

As to pressurizing the attic......I wonder if you could even measure the effect with a micromanometer that this small a leak would have!!(unless it was a quite small space) Since the attic is sealed, any pressure would send air into the house through ceiling penetrations.......conditioned air from above....sounds familiar!!! Other items such as poor duct design (no returns in bedrooms with 2-3 supplies), other duct leaks, wind pressures and stack effect will cause much larger pressure imbalances/variations than this small amount of leakage.

Unlike other duct leakage in unconditioned attics, this air is lost to or returned from the conditioned space. How much efficiency would be gained if this were sealed?
Reply With Quote
  #12  
Old 9/10/08, 10:02 AM
cbottger's Avatar
cbottger cbottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,738
Default Re: AC duct not sealed

Quote:
Originally Posted by Brian A. MacNeish
This is a conditioned attic, sealed off from the exterior by spray foam. The amount of air leaking around this small closed damper may be what...8-10-15 CFM in a system of 1000-2000 CFM......not a big deal and it is into a conditioned space. Jeez, a 4" duct is only rated to carry 40 CFM in good designs.

Residential duct systems are usually unsealed and not even close to good spec'd work seen in commercial, etc. I have seen studies from Home Energy magazine and others that claim that 20-40% of the air moving through the air handler does not come from or get to the intended grills/diffusers.....the ducts are generally so leaky!!!!! So to me this is not a big flaw but still should be sealed.....I just wouldn't hang a big, red flag on it!

As to pressurizing the attic......I wonder if you could even measure the effect with a micromanometer that this small a leak would have!!(unless it was a quite small space) Since the attic is sealed, any pressure would send air into the house through ceiling penetrations.......conditioned air from above....sounds familiar!!! Other items such as poor duct design (no returns in bedrooms with 2-3 supplies), other duct leaks, wind pressures and stack effect will cause much larger pressure imbalances/variations than this small amount of leakage.

Unlike other duct leakage in unconditioned attics, this air is lost to or returned from the conditioned space. How much efficiency would be gained if this were sealed?
The original poster never really stated that it was a conditioned attic everyone is just assuming that it was because of the spray foam sounds to me that someone had good intentions gone bad as one can see those balancing dampers are not a positive shut off and do have a good amount of air blowing bye not just 10 or 15 cfm
No the world is not going to come to an end because of it I would handle it just as any other item in need of repair



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #13  
Old 9/10/08, 6:14 PM
Lisa Bloemer Lisa Bloemer is offline
New User
 
Join Date: Sep 2008
Posts: 3
Please Note: Lisa Bloemer is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: AC duct not sealed

Thanks for all your help. This is the first time I've posted and glad to see the support. Especially so quickly.. I will definately bookmark this as open favorite tab.

No, don't think it's a conditioned attic. I think someone left the seal off this return. I haven't seen this before with louver not capped.

Unlikely they built return for adding attitional living space in attic for later time. This is a duplex condo.. Not much space for adding. Living areas had 14 - 20' ceilings.. so attic was chopped /divided.

Yes, they did have adequate registers in every room and house was very cold and air flow was good throughout.

The attic was large, unfinished and not cool at all. I was dripping wet while up there.. It did appear to be lost energy at most.

Still not sure why they foamed entire overhang. Yes, There are soffit vents on the outside.. But they were four stories high... so I wasn't able to see inside if foam covered them or not. Should I assume they were..and write it up as suspcious for proper ventilation. There was no other area where air flow could escape the attic... am I missing something?

The place is brand new.. had many many problems with missing significant caulking throughout in everybath/kitchen countertops.. several cracked tiles on floor and marble in shower areas.. damaged spa intake, master sink cracked, shower shelf broken and not secure on wall, torn screens, carpet unattached on top step, several cosmetic marks, stains, damages on sheetrock throughout every room, missing caulking exterior siding on ground and floor levels, Two GFCI's didn't operate... actually very surprised the amount issues for a new "Move In Ready" condo. Is this normal for new construction?

Also had a vent connection going from Water Heater/AC closet extending through roof. Can figure out what that is for either.. All electric appliances.. No fuel at all going to building.. Can you comment on that as well? See photos attached.

The Realtor / Condo Assoc Rep said "He" checked everything and it was all working fine and ready to go.. Owner (my friend) wanted someone to walk through with them as safeguard to what Realtor said. Realtor is pushing for quick sale.. Buyers are wanting repairs before signing on line..
Lisa
Attached Thumbnails
ac-duct-not-sealed-duct-discharges-into-water-heater.-ac-unit-closet.jpg   ac-duct-not-sealed-duct-extends-thru-roof.jpg  
Reply With Quote
  #14  
Old 9/10/08, 9:10 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 3,930
Default Re: AC duct not sealed

They plan for gas but use electric instead because of the increased cost of fuel.

That's what's happening around here anyway.



David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Certified Level II Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620

Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #15  
Old 9/10/08, 10:28 PM
Mark Reusch Mark Reusch is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Simpsonville, SC
Posts: 463
Send a message via Yahoo to mreusch
Default Re: AC duct not sealed

Quote:
Originally Posted by mnahrgang View Post
Since they sprayed the roof, could it be that they converted the attic to "conditioned space"? Instead of the traditional vented unconditioned. You mentioned that they insulated over the vents...
I was under the impression if an attic was sprayed that the rafters should be covered as well. Seems to me the to fully seal an attic space the trusses or refters would have to be sealed as well. If I am wrong or confused about this does anyone have some information about this ?
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Reduced return air duct mmorgan HVAC 4 6/6/07 8:39 PM
Moving cold air duct abishop HVAC 0 10/31/06 1:08 PM
Strange Duct in Crawl Space jfunderburk Structural 3 1/11/06 1:02 AM


All times are GMT -4. The time now is 3:17 PM.


Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts