Default AC ducting without plastic sheathing

Can some one tell me the effects that occur when the plastic sheathing on flex ducting disintegrates. Leaving just the insulation covering the duct. I would really appreciate any help.
Reply With Quote
  #2  
Old 4/21/06, 11:07 AM
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 5,447
Default Re: AC ducting without plastic sheathing

Further deterioration at an accelerated pace.



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
  #3  
Old 4/21/06, 11:32 AM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: AC ducting without plastic sheathing

Quote:
Originally Posted by mbutters
Can some one tell me the effects that occur when the plastic sheathing on flex ducting disintegrates. Leaving just the insulation covering the duct. I would really appreciate any help.
Hi all,

the big problem here is that when the outer jacket is missing or damaged moisture will start to condense against the insullation turning into one big sponge trapping water, when this reaches its maximum capacity it will start to drip ruining ceilings etc.

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #4  
Old 4/21/06, 11:21 PM
Michael H. Butters Michael H. Butters is offline
InterNACHI Member
 
Join Date: Jun 2004
Location: Forney, TX
Posts: 28
Default Re: AC ducting without plastic sheathing

Thanks for the help gentlemen. I appreciate it. Why do the flex ducts have to be suspended from the rafters? As opposed to laying on the floor of the attic.
I had a home owner ask me. The reason I came up with was...
The insulation will not provide full coverage.
Also, the ducting may not get full airflow through it.
Are there any other reasons I should know about?
Reply With Quote
  #5  
Old 4/22/06, 9:19 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,559
Default Re: AC ducting without plastic sheathing

Quote:
Originally Posted by mbutters
Why do the flex ducts have to be suspended from the rafters? As opposed to laying on the floor of the attic.
I didn't know they did. Now I'll have to go back and correct thousands of inspections or hope that I don't get sued.

I think you're confusing ducts in the crawl space with ducts in the attic. Ducts in the crawl space should be suspended instead of laying on the ground. Ducts in the attic can lay on the attic floor, crawl up the walls, hand from the roof, whatever.



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #6  
Old 4/22/06, 3:33 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,722
Default Re: AC ducting without plastic sheathing

I believe SMACNA, ASHRAE and the duct manufacturers have specific guidelines regarding duct supports to prevent kinking and I also believe many HI's don't know what to look for. I know I don't, other than supports needed every 5' and I do find kinked and obstructed flex duct occasionally. I think I'll try to find a good CE course on HVAC including ductwork.

Last edited by mboyett; 4/22/06 at 4:27 PM..
Reply With Quote
  #7  
Old 4/23/06, 9:47 AM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,722
Default Re: AC ducting without plastic sheathing

Here is the "Air Diffusion Council" installation instructions for flex duct. It appears to be the same instructions that ATCO, the largest mfg of flex duct, includes with their ducts. See figures 10 & 14:
http://www.flexibleduct.org/download/ADC~Inst.pdf
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Use of ThermoPly without underlying structural sheathing? koconnor Structural Inspections 12 10/16/07 8:52 PM
Gas changes for plastic vents in Canada rcooke Canadian Inspectors 0 7/30/07 3:15 PM
plastic piping? Scott Schultz Plumbing Inspections 5 3/28/07 2:40 AM
Exterior sheathing adooley Exterior Inspections 8 2/16/07 10:42 PM
Hart & Cooley plastic furnace vent apfaff Inspecting HVAC Systems 2 8/15/06 4:20 AM


All times are GMT -4. The time now is 11:17 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts