Since someone mentioned that this thread was dead, I thought I would post a question. What is wrong with this picture?Slide14.JPG



Sincerely,
Charles M. Bellefontaine

Bellman Group, Inc.
877-316-0600 Extension #802
Click Here to Join our Email Newsletter

Get Illinois Home Inspector Pre-License Education and
Continuing Education at www.bellmangroup.com

Low cost professional report writing with a contact
management system. www.myreportwriter.com
Reply With Quote
  #2  
Old 12/15/06, 12:45 AM
kmcmahon kmcmahon is offline
Active Poster
 
Join Date: Apr 2004
Location: Stevens Point, WI
Posts: 223
kmcmahon is generally well trusted
Please Note: kmcmahon is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: AC Question

The filter is not installed.....bwhahahaha!!
Reply With Quote
  #3  
Old 12/15/06, 1:04 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,452
Charley L. Bottger .
Default Re: AC Question

Quote:
Originally Posted by cbellefontaine
Since someone mentioned that this thread was dead, I thought I would post a question. What is wrong with this picture?Attachment 7785
I see two possibilities but will hold my answer until Saturday and give someone else the chance to answer.
Reply With Quote
  #4  
Old 12/15/06, 4:23 AM
kfonoimoana's Avatar
kfonoimoana kfonoimoana is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Laie, Hi
Posts: 49
kfonoimoana has had a little positive feedback
Default Re: AC Question

My guess is the looped lines may have something to do with at least one of the two?
Reply With Quote
  #5  
Old 12/15/06, 7:28 AM
Bruce M. Graham, III's Avatar
Bruce M. Graham, III Bruce M. Graham, III is online now
InterNACHI Member
 
Join Date: Sep 2005
Location: Gainesville, FL
Posts: 1,319
Bruce M. Graham, III is well trusted Bruce M. Graham, III is well trusted Bruce M. Graham, III is well trusted Bruce M. Graham, III is well trusted
Default Re: AC Question

oil trap.



Bungalows to Mansions
Professional Inspection Services, LLC
Bruce M. Graham III
Gainesville, FL 32608
352 871 8989
NACHI05091592
ICC 5268478
www.bungalowstomansions.com
Reply With Quote
  #6  
Old 12/15/06, 9:30 AM
ccbrands1 ccbrands1 is offline
Active Poster
 
Join Date: Jan 2006
Posts: 220
ccbrands1 hasn't had much positive or negative feedback
Please Note: ccbrands1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: AC Question

excess length of the line set have anything to do with it?
Reply With Quote
  #7  
Old 12/15/06, 10:07 AM
Greg Veal Greg Veal is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Woodstock, GA
Posts: 444
Greg Veal is generally well trusted
Default Re: AC Question

Uno,
The Ref.L/S may be left coiled like that, because the distance between the Evap. Coil and the outdoor Condenser is too close. Equip. Manuf. requires min. lenghth between equipment (usually 20-25').
Note - the coiled Ref.L/S should be hung Horizontally to avoid oil trap.

Dos,
What else do you think ?? (Mastic, Insulation, filter, Hum. By-pass)
Reply With Quote
  #8  
Old 12/15/06, 11:12 AM
Anthony J. Jewell Anthony J. Jewell is offline
InterNACHI Member
 
Join Date: Dec 2006
Location: Yorktown Heights, NY
Posts: 20
Anthony J. Jewell .
Default Re: AC Question

Sometimes the ref. lines are precharged (Approx 25 ft.) from the maufacturer and maybe the installer didn't know what to do with the excess? But I really don't know the answer.
Reply With Quote
  #9  
Old 12/15/06, 3:51 PM
cbellefontaine's Avatar
cbellefontaine cbellefontaine is offline
InterNACHI Member
 
Join Date: Dec 2006
Location: Bolingbrook, IL
Posts: 65
cbellefontaine has had a little positive feedback
Send a message via MSN to cbellefontaine
Default Re: AC Question

I was shooting for the extra line set left in the vertical position.
Greg and Bruce did recognize that the oil may be trapped in the bottom of the loops when the unit is not operating. This increases the chance of the oil getting to the compressor. I suggest that the extra coils be left horizontal instead of vertical.

Charley, I am curious on what else you saw in the photo.
I have a bunch more photos if you guys are interested.



Sincerely,
Charles M. Bellefontaine

Bellman Group, Inc.
877-316-0600 Extension #802
Click Here to Join our Email Newsletter

Get Illinois Home Inspector Pre-License Education and
Continuing Education at www.bellmangroup.com

Low cost professional report writing with a contact
management system. www.myreportwriter.com
Reply With Quote
  #10  
Old 12/15/06, 4:25 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,452
Charley L. Bottger .
Default Re: AC Question

[quote=cbellefontaine]I was shooting for the extra line set left in the vertical position.
Greg and Bruce did recognize that the oil may be trapped in the bottom of the loops when the unit is not operating. This increases the chance of the oil getting to the compressor. I suggest that the extra coils be left horizontal instead of vertical.

Charles: I know this is not Saturday but the question has already been answered.

Oil trap a definite concern I would rate this as a poor install. Never did like pre-charged line sets to begin with hard to make the install professional in appearance and to the client whom knows very little to nothing about HVAC appearance is everything. My two concerns were the oil trap and the loops in general.

I do not agree with two of your statements you stated the oil may be trapped when the unit is not in operation my take is that the oil is trapped all of the time in operation or shut down. If you do not have proper suction velocity to carry the oil back to the compressor it remains trapped.
That is why we install P-traps in the suction line on the outlet side of the evaporator when the condensing unit set above the A-coil such as on the roof so as to create the velocity to return the oil back to the compressor and not be trapped within the A-coil and reduce the cooling capacity of the coil. Enough Enough.

Your second statement was that it increases the chance of the oil getting back to the compressor surely you meant decreases the chance.
Reply With Quote
  #11  
Old 12/15/06, 4:37 PM
cbellefontaine's Avatar
cbellefontaine cbellefontaine is offline
InterNACHI Member
 
Join Date: Dec 2006
Location: Bolingbrook, IL
Posts: 65
cbellefontaine has had a little positive feedback
Send a message via MSN to cbellefontaine
Default Re: AC Question

Thanks Charley for keeping me on my toes. Nice post.



Sincerely,
Charles M. Bellefontaine

Bellman Group, Inc.
877-316-0600 Extension #802
Click Here to Join our Email Newsletter

Get Illinois Home Inspector Pre-License Education and
Continuing Education at www.bellmangroup.com

Low cost professional report writing with a contact
management system. www.myreportwriter.com
Reply With Quote
  #12  
Old 12/15/06, 4:43 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,452
Charley L. Bottger .
Default Re: AC Question

[quote=cbellefontaine]
I have a bunch more photos if you guys are interested

Post all of the pic you have good training for HI'S Try to use the pic that could be visibly observed without invasive procedures.

We have some excellent HVAC guys hangout on this board. Robert O'Connor, David Anderson, Greg Veal they can all jump on your Pic's As for my self I just try to stir the pot and keep the thinking moving forward.
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
Sump Pit/Pump Question Joey D'Adamo Plumbing 4 11/26/08 2:04 PM
Interesting Question? jmckenna1 Misc. Discussion 9 11/25/07 2:13 PM
WA State Legislative update hmiller Legislation, Licensing & Legal Issues 153 5/5/07 12:55 AM
WA Structural Pest Inspector Law hmiller Legislation, Licensing & Legal Issues 18 4/1/07 3:10 AM
Rule of Thumb A/C sizing question from Practice Exam gliebig HVAC 9 5/25/06 2:38 AM


All times are GMT -4. The time now is 5:17 PM.


Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics