Our SOP states that we should not run an air conditioner when the air temp is below 60F because it could cause damage. Can anyone explain what kind of damage can occur?
Reply With Quote
Need a home inspection in North Dakota? Check out InterNACHI's listing of North Dakota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 12/25/11, 1:01 PM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,110
Default Re: AC Question

Quote:
Originally Posted by rdrangstveit View Post
Our SOP states that we should not run an air conditioner when the air temp is below 60F because it could cause damage. Can anyone explain what kind of damage can occur?
I think you meant to say 65° Fahrenheit!

  1. operate equipment or systems if the exterior temperature is below 65° Fahrenheit, or when other circumstances are not conducive to safe operation or may damage the equipment.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #3  
Old 12/25/11, 2:49 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: AC Question

As a result of liquid migration the refrigerant in a closed loop system migrates to the coldest area of the system which when below 60 degrees or what ever your SOP dictates is the exterior condenser the liquid refrigerant has the capability of entering the oil sump of the compressor and when the unit is activated the liquid refrigerant and the oil can be pumped through the discharge valves of the compressor and create damage as the valves within the compressor are designed to pump vapor not liquid. These type of valves are not used on a scroll type compressors there are no valves to damage. Thus the only possible damage than can occur to a scroll compressor is if the oil is pumped out of its reservoir and does not readily return to the reservoir which is highly unlikely unless the the line set between the A-coil and the exterior condenser is lengthy or the A-coil is located within a basement below the exterior condensing unit



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging

Last edited by cbottger; 12/25/11 at 2:53 PM..
Reply With Quote
  #4  
Old 12/25/11, 4:51 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,798
Default Re: AC Question

Couldn't have said that any better Charley.

Merry Christmas to you.
Reply With Quote
  #5  
Old 12/25/11, 8:03 PM
Roy Drangstveit's Avatar
Roy Drangstveit Roy Drangstveit is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Prior Lake, MN
Posts: 149
Default Re: AC Question

Thanks Charley,
I needed to explain the reason for not testing under 65 to a client.
This helps a lot.
Also yesterday when we went to church, it was very mild here, about 40 degrees The church was packed & the air condioners were running full blast.
Do you think they may have been damaged?

Roy
Reply With Quote
  #6  
Old 12/25/11, 8:19 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: AC Question

Here's more info at recent discussion.

http://www.nachi.org/forum/f20/wordi...ratures-66893/



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #7  
Old 12/26/11, 12:14 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: AC Question

Quote:
Originally Posted by rdrangstveit View Post
Also yesterday when we went to church, it was very mild here, about 40 degrees The church was packed & the air condioners were running full blast.
Do you think they may have been damaged?
I would bet my red hat that the units in your Church were not damaged. Most units but not all on a church are set up with colder weather operation. Crankcase heaters and suction line accumulators and possible oil separators on the discharge line.

To many HI's are under the impression that if one operates the unit below 60 degrees F. that the unit is going to disappear in a cloud of smoke. All they under stand is what is written in a book. I can state after 40 years of operating thousands of residential units and some at 10 degrees F I have never damaged one



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #8  
Old 12/26/11, 7:49 AM
Linas Dapkus's Avatar
Linas Dapkus Linas Dapkus is offline
InterNACHI Member
 
Join Date: Feb 2011
Location: Home
Posts: 2,187
Default Re: AC Question

Quote:
Originally Posted by kwood View Post
I think you meant to say 65° Fahrenheit!

  1. operate equipment or systems if the exterior temperature is below 65° Fahrenheit, or when other circumstances are not conducive to safe operation or may damage the equipment.
I think Mr. cmi meant to say: to type the "degree" symbol, on a Mac it's shift+option+8 and on a PC it's Alt+0176.
Reply With Quote
  #9  
Old 12/26/11, 8:01 AM
ROBERT V. YOUNG's Avatar
ROBERT V. YOUNG ROBERT V. YOUNG is online now
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal.
Posts: 5,050
Default Re: AC Question

Quote:
Originally Posted by kwood View Post
I think you meant to say 65° Fahrenheit!

  1. operate equipment or systems if the exterior temperature is below 65° Fahrenheit, or when other circumstances are not conducive to safe operation or may damage the equipment.
I have seen 60 degrees Fahrenheit to Kevin.
I questioned it myself and saw it referenced several times 2 weeks ago.
To be on the safe side Kevin I state my standards of safe operational practices is 6o degrees Fahrenheit to my clients.
Also explaining that 65 degrees is also referenced in some literature.
That it will be noted in limitations and that I will inspect the system when the ambient temperature rises above 65 for free.
JMO



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816
Reply With Quote
  #10  
Old 12/26/11, 8:06 AM
ROBERT V. YOUNG's Avatar
ROBERT V. YOUNG ROBERT V. YOUNG is online now
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal.
Posts: 5,050
Default Re: AC Question

Quote:
Originally Posted by cbottger View Post
As a result of liquid migration the refrigerant in a closed loop system migrates to the coldest area of the system which when below 60 degrees or what ever your SOP dictates is the exterior condenser the liquid refrigerant has the capability of entering the oil sump of the compressor and when the unit is activated the liquid refrigerant and the oil can be pumped through the discharge valves of the compressor and create damage as the valves within the compressor are designed to pump vapor not liquid. These type of valves are not used on a scroll type compressors there are no valves to damage. Thus the only possible damage than can occur to a scroll compressor is if the oil is pumped out of its reservoir and does not readily return to the reservoir which is highly unlikely unless the the line set between the A-coil and the exterior condenser is lengthy or the A-coil is located within a basement below the exterior condensing unit
Great explanation Mr. Bottger.
Text book.
In the vault it goes.



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816
Reply With Quote
  #11  
Old 12/26/11, 8:24 AM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,110
Default Re: AC Question

Thanks Linus!



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #12  
Old 1/4/12, 7:31 AM
Kenneth H. Levine Kenneth H. Levine is offline
InterNACHI Member
 
Join Date: Sep 2011
Posts: 4
Default Re: AC Question

When the temp outside is too cold the pressure in the condenser (outside section) is very low. In addition usually there is not a enough heat load on the evaporator (inside section) this causes a low pressure there as well. The combinatioin of low pressure in the inside coil and outside coil will not let the refrigerant in the evaporator completely turn into a vapor. if you get liquid refrigerant back to the compressor it slugs through the compressor valves damaging them and it washes the oil out of the compressor as well causing lack of lubrication. we all know what happens when you don't have oil in a car engine.
Reply With Quote
  #13  
Old 1/4/12, 8:15 AM
ROBERT V. YOUNG's Avatar
ROBERT V. YOUNG ROBERT V. YOUNG is online now
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal.
Posts: 5,050
Default Re: AC Question

Kenneth.
Look at post #3.
I think it is an excellent narrative about refrigerant and low temperature operations.
You are doing a better job then myself at the moment in understanding then creating a narrative for the condition.
Mr. Bottger explanation should influence you.
Good for you Mr. Levine.



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816
Reply With Quote
Need a home inspection in North Dakota? Check out InterNACHI's listing of North Dakota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 1/4/12, 8:40 PM
Jeff Merritt Jeff Merritt is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Chicago, IL
Posts: 1,162
Default Re: AC Question

I just tell them the oil is too thick and cold,may damage the compressor, and I don't want to buy a new one.

But I like Charlie's explanation.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Four Point Inspection Question (Electrical) khunt Florida Inspectors 43 12/18/11 4:26 PM
Sump Pit/Pump Question Joey D'Adamo Plumbing Inspections 4 11/26/08 1:04 PM
Question for all... Bob Hopton-Jones General Inspection Discussion 9 4/6/07 7:43 AM
Basement Bathroom Venting Question Sean M. Jeric Plumbing Inspections 4 3/20/07 11:56 PM


All times are GMT -4. The time now is 10:05 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts