Default AC Splits Yea or Nay

Do you take AC splits as part of your inspection protocol?





For my next trick I will need a volunteer

ps some of the opinions I have posted here may or may not be factually based.




AZ Cert # 39975
AZ Pest # 050898
Reply With Quote
  #2  
Old 4/18/06, 10:29 PM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 5,824
Dale Duffy .
Default Re: AC Splits Yea or Nay

Quote:
Originally Posted by bkelly2
Do you take AC splits as part of your inspection protocol?
Nope....
Reply With Quote
  #3  
Old 4/19/06, 1:39 AM
Mark A. Timpani's Avatar
Mark A. Timpani Mark A. Timpani is offline
InterNACHI Member
 
Join Date: May 2004
Location: Tucson, AZ
Posts: 1,413
Mark A. Timpani is almost always very helpful Mark A. Timpani is almost always very helpful Mark A. Timpani is almost always very helpful Mark A. Timpani is almost always very helpful Mark A. Timpani is almost always very helpful Mark A. Timpani is almost always very helpful
Default Re: AC Splits Yea or Nay

yes..




"Be Proud of Your Home, Go With Pride!"
'Not just a Home Inspection, but an Education'

Pride Property Inspections provides professional Home Inspections throughout Tucson and Southern Arizona including Pima, Cochise, Pinal, Santa Cruz, Graham counties.

Reply With Quote
  #4  
Old 4/19/06, 2:23 AM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 8,523
Brian E. Kelly .
Default Re: AC Splits Yea or Nay

Dale do you bring an AC guy?





For my next trick I will need a volunteer

ps some of the opinions I have posted here may or may not be factually based.




AZ Cert # 39975
AZ Pest # 050898
Reply With Quote
  #5  
Old 4/19/06, 2:24 AM
Joe D. Funderburk's Avatar
Joe D. Funderburk Joe D. Funderburk is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Rock Hill, SC
Posts: 2,087
Joe D. Funderburk is very trusted source of information Joe D. Funderburk is very trusted source of information Joe D. Funderburk is very trusted source of information Joe D. Funderburk is very trusted source of information Joe D. Funderburk is very trusted source of information Joe D. Funderburk is very trusted source of information Joe D. Funderburk is very trusted source of information Joe D. Funderburk is very trusted source of information
Send a message via Yahoo to jfunderburk
Default Re: AC Splits Yea or Nay

How do you take a split?



Joe Funderburk
Alpha & Omega Home Inspections, LLC
Hickory Grove, SC
NACHI ID: NACHI05120170
www.aohomeinspection.com
Reply With Quote
  #6  
Old 4/19/06, 8:45 AM
David P. Valley's Avatar
David P. Valley David P. Valley is online now
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 6,369
David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute
Default Re: AC Splits Yea or Nay

Quote:
Originally Posted by jfunderburk
How do you take a split?
Simply obtain a temperature reading of the return register and the supply register. You want to see a 12 to 15 degree difference.
Reply With Quote
  #7  
Old 4/19/06, 9:41 AM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 5,824
Dale Duffy .
Default Re: AC Splits Yea or Nay

Quote:
Originally Posted by bkelly2
Dale do you bring an AC guy?
Hi Brian,

No, every technician which has either serviced mine or customers has said it really has no bearing on how the equipment might really be functioning unless a temp reading is taken at the unit, and I have never seen a technician even take a reading from a register.

I do check the supply temp for readings in the 50's which tells me it is operating correctly.

You know the way they build here, there could be ducts separated, uninsulated, or nobody has had the equipment serviced in years, which is generally the reason one is not producing the correct temps.

I have found the systems just designed poorly, under sized, two story homes with 12 foot ceilings with both returns on the second floor, the second floor very cool and you cannot bring the temp down normally on the first because of the design.

As a matter of fact, an entire subdivision is suing a builder here in Chandler for that very reason...wrong conditioning design of every home.

So a temperature split of 14-22 degrees makes no difference if the equipment is producing 65 degree air and returning 80 something degrees, it's just not working or designed right.
Reply With Quote
  #8  
Old 4/19/06, 10:05 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 2,834
David A. Andersen .
Default Re: AC Splits Yea or Nay

If you are using a thermometer to take your split, it is worthless.
Reply With Quote
  #9  
Old 4/19/06, 2:48 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 8,523
Brian E. Kelly .
Default Re: AC Splits Yea or Nay

Dale interesting, so if it is 115 F outside you look for 50's F? Seems like the unit would be working prettty hard.





For my next trick I will need a volunteer

ps some of the opinions I have posted here may or may not be factually based.




AZ Cert # 39975
AZ Pest # 050898
Reply With Quote
  #10  
Old 4/19/06, 3:04 PM
Doug Edwards,  CMI's Avatar
Doug Edwards, CMI Doug Edwards,  CMI is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Pace (Pensacola), FL
Posts: 2,970
Doug Edwards,  CMI .
Default Re: AC Splits Yea or Nay

There are so many reasons why this method DOES NOT do what so many inspectors think it does I can't even begin to list them. There are literally a hundred variables that come into play. Like David said, if you are taking a dry bulb temperature you are wasting your time trying to determine if the system is working properly. I know this is what a lot of the HI books out there all say is the method for checking an HVAC , but it is just plain wrong.
Reply With Quote
  #11  
Old 4/19/06, 3:26 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 8,523
Brian E. Kelly .
Default Re: AC Splits Yea or Nay

Doug even more interesting. I am in the temp split camp, as that is how I was taught, and that was a question on the NHIE. I was taught that if he splits are not correct (taken at the inlet and outlet of the unit) then the system should be evaluated by a HVAC technician.

As a generalist HI I am all ears if there is a better way to test the AC. But if it involves specialized equipment, psychometric charts, and/or engineering, I will pass.





For my next trick I will need a volunteer

ps some of the opinions I have posted here may or may not be factually based.




AZ Cert # 39975
AZ Pest # 050898
Reply With Quote
  #12  
Old 4/19/06, 4:18 PM
Blaine Wiley Blaine Wiley is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Rotonda West, FL
Posts: 2,381
Blaine Wiley is very trusted source of information Blaine Wiley is very trusted source of information Blaine Wiley is very trusted source of information Blaine Wiley is very trusted source of information Blaine Wiley is very trusted source of information Blaine Wiley is very trusted source of information Blaine Wiley is very trusted source of information Blaine Wiley is very trusted source of information Blaine Wiley is very trusted source of information Blaine Wiley is very trusted source of information Blaine Wiley is very trusted source of information
Send a message via MSN to bwiley
Default Re: AC Splits Yea or Nay

I take them across the coil and look for 14 to 22 degrees. It gives an indication of how the system is working. In and of itself, it is not an accurate measurement, but it can be used with other visual clues to give the inspector a better idea about the condition of the system.
Reply With Quote
  #13  
Old 4/19/06, 4:34 PM
Joe D. Funderburk's Avatar
Joe D. Funderburk Joe D. Funderburk is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Rock Hill, SC
Posts: 2,087
Joe D. Funderburk is very trusted source of information Joe D. Funderburk is very trusted source of information Joe D. Funderburk is very trusted source of information Joe D. Funderburk is very trusted source of information Joe D. Funderburk is very trusted source of information Joe D. Funderburk is very trusted source of information Joe D. Funderburk is very trusted source of information Joe D. Funderburk is very trusted source of information
Send a message via Yahoo to jfunderburk
Default Re: AC Splits Yea or Nay

Quote:
Originally Posted by jfunderburk
How do you take a split?
I was only kidding. Should have used a different smiley.



Joe Funderburk
Alpha & Omega Home Inspections, LLC
Hickory Grove, SC
NACHI ID: NACHI05120170
www.aohomeinspection.com
Reply With Quote
  #14  
Old 4/19/06, 5:41 PM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 5,824
Dale Duffy .
Default Re: AC Splits Yea or Nay

Quote:
Originally Posted by bkelly2
Dale interesting, so if it is 115 F outside you look for 50's F? Seems like the unit would be working prettty hard.
Like others said....to many variables.

The only way to really test them is with gauges and instruments like the techs use.

If it's 115 outside and the unit is producing 62 degree air from a duct system numerous feet long in a attic 155 degrees, chances are it's doing the best it can.

Very seldom have I run across anyone who said the system was serviced in the last 12 months like the manufacturers recommend...so I naturally recommend it before the close of escrow, if the buyers disregard my advice...oh well.....
Reply With Quote
  #15  
Old 4/19/06, 6:12 PM
jmichalski's Avatar
jmichalski jmichalski is offline
Active Poster
 
Join Date: Aug 2004
Location: Souderton, PA
Posts: 2,572
jmichalski is often very helpful jmichalski is often very helpful jmichalski is often very helpful
Please Note: jmichalski is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: AC Splits Yea or Nay

I have seen many say that splits are worthless but no explanation of the position.

Anyone?

For what it's worth, I also take the temps at several registers (clients like to see the data relative to the other rooms). If it takes me only 3 minutes to do - and the clients like to play with the laser thermometer, then so be it.
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
Horizontal furnace in the foundation crawlspace kswift HVAC 43 7/24/06 10:26 PM


All times are GMT -4. The time now is 5:49 PM.


1 2 3 4 5 6 7 8 9 10 11 12