Talking AC Units Cooled By Well Water

I got a call from a guy about an inspection that I have set up for Wednesday afternoon. He states that there are 3 A/C units present, all original from 1980 something and that there are water hoses running from one of the wells on the property to the units. I am assuming this is a cooling set up but I have yet to inspect something like what he described. Has anyone seen this set up at an inspection that could give me some advice on things that I should be looking for other than the obvious. This guy is pretty cool and he understands that I am not an A/C professional but he would appreciate anything that I could tell him, other than the units are at the end of their expected life in years.
Reply With Quote
  #2  
Old 8/25/08, 8:04 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 8,526
Brian E. Kelly .
Default Re: AC Units Cooled By Well Water

Are they swamp coolers?





For my next trick I will need a volunteer

ps some of the opinions I have posted here may or may not be factually based.




AZ Cert # 39975
AZ Pest # 050898
Reply With Quote
  #3  
Old 8/25/08, 8:09 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,897
Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: AC Units Cooled By Well Water

"water cooled condensers". What you describe is what an hvac tech will know by slang as a "pump and dump" system. People nowadays favor calling it a geothermal system (that term might be more familiar to home inspectors), but it's essentially just a water cooled condensing coil versus the traditional large air cooled condensing coil. This may be straight AC, or it may be a heat pump. The quality of the water sorely effects the lifespan and the operating efficiency of the condensing coil heat exchanger.
Reply With Quote
  #4  
Old 8/25/08, 9:18 PM
PAUL J. MAGRONE PAUL J. MAGRONE is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: ORLANDO, FL
Posts: 192
PAUL J. MAGRONE is generally well trusted
Talking Re: AC Units Cooled By Well Water

I believe that they are for cooling the units too. Thanks for the quality of water mention because I would not have thought of that. What would you suggest if these units are all functioning properly but he wanted to remove the hoses because they are above ground from what he is describing. These are old units but I want to advise him properly. What should I look for in inspecting the units other than operating them as usual?
Reply With Quote
  #5  
Old 8/26/08, 1:07 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,452
Charley L. Bottger .
Default Re: AC Units Cooled By Well Water

Paul as Mark stated they are probably water cooled condensers from the well source but being the non-trusting sole that I am I do not necessarily believe what I am told by someone going on hear say. The units could also be glycol not likely but could be. I would determine the cooling medium on site. Water cooled condensers are high maintenance required to be acidized periodically to reduce corrosion if not, they will create high head pressure similar to a matted over air cooled condenser.

Its late had a 5k home with 4 A/C units and furnaces today Good night all and you too John Boy



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #6  
Old 8/26/08, 6:22 AM
PAUL J. MAGRONE PAUL J. MAGRONE is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: ORLANDO, FL
Posts: 192
PAUL J. MAGRONE is generally well trusted
Default Re: AC Units Cooled By Well Water

Thank you. I appreciate the heads up.
Reply With Quote
  #7  
Old 8/26/08, 12:28 PM
Bruce M. Graham, III's Avatar
Bruce M. Graham, III Bruce M. Graham, III is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Gainesville, FL
Posts: 1,319
Bruce M. Graham, III is well trusted Bruce M. Graham, III is well trusted Bruce M. Graham, III is well trusted Bruce M. Graham, III is well trusted
Default Re: AC Units Cooled By Well Water

look here www.waterfurnace.com
could be water source heatpumps.



Bungalows to Mansions
Professional Inspection Services, LLC
Bruce M. Graham III
Gainesville, FL 32608
352 871 8989
NACHI05091592
ICC 5268478
www.bungalowstomansions.com
Reply With Quote
  #8  
Old 8/26/08, 3:16 PM
David W. Shockley David W. Shockley is offline
InterNACHI Member
 
Join Date: Jun 2007
Location: Orlando, FL
Posts: 2
David W. Shockley hasn't had much positive or negative feedback
Post Re: AC Units Cooled By Well Water

The new geothermal units drop copper pipe 300 ft in the ground where the base of the copper line has a torpedo shaped end. The refrigerant is cooled by the cold water that the torpedo is set in. I recently inspected/installed many of these units for Disney. They save about 70% on A/C bills. The old style geothermal used the actual well water while the new ones use the temperature of the water only. There were problems regarding the water quality on some older units in some areas of Florida. The cost for installing one is about $3000 more than an electrical unit. The copper lines run around $2200 alone. I am not sure of how it is hooked up but the geothermal units are capable of producing hot water for the home as well. Does anyone know how this works? The homes I inspected had small electric hot water heaters for back up only.
Reply With Quote
  #9  
Old 8/26/08, 5:33 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,452
Charley L. Bottger .
Default Re: AC Units Cooled By Well Water

Quote:
Originally Posted by dshockley
The new geothermal units drop copper pipe 300 ft in the ground where the base of the copper line has a torpedo shaped end. The refrigerant is cooled by the cold water that the torpedo is set in. I recently inspected/installed many of these units for Disney. They save about 70% on A/C bills. The old style geothermal used the actual well water while the new ones use the temperature of the water only. There were problems regarding the water quality on some older units in some areas of Florida. The cost for installing one is about $3000 more than an electrical unit. The copper lines run around $2200 alone. I am not sure of how it is hooked up but the geothermal units are capable of producing hot water for the home as well. Does anyone know how this works? The homes I inspected had small electric hot water heaters for back up only.
David that was the point I was pressing the cooling medium can and does vary between MFG's all doing the same thing changing the state of Freon from a hot vapor to a liquid does not matter how it is done. In my reports I just state the type of cooling medium and no way to do this unless on site.

As for producing hot water for domestic use, why not the compressor produces a hot vapor and could be routed through an heat exchanger designed for the use. I have not observed a unit of this nature but knowing the refrigeration principal I could trace the lines and tell you what was happening at the different stages and or configuration.



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #10  
Old 8/26/08, 8:07 PM
Gary T. Heller's Avatar
Gary T. Heller Gary T. Heller is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Peoria, AZ
Posts: 188
Gary T. Heller is often very helpful Gary T. Heller is often very helpful
Default Re: AC Units Cooled By Well Water

Many years ago in Arizona we had a few residential package units with a device we called a pre-cooler. The idea was to spray water over the condenser to cool it and gain some saving from a compressor that didn't have to work as hard. I was never a fan of putting water on a DX unit coil for two reasons. First the water in AZ is very hard and it had a tendency to dirty up the condenser and the second reason was because I always felt the gas changed state in a different area of the condenser than it would with just air cooling. I don't want to get deep into thermo dynamics but if I ran across one now it would be interesting to see the condenser through a thermal imaging camera.
Reply With Quote
  #11  
Old 8/26/08, 8:32 PM
Greg Bell's Avatar
Greg Bell Greg Bell is offline
InterNACHI Member
 
Join Date: Oct 2002
Location: Titusville, FL
Posts: 2,636
Greg Bell .
Default Re: AC Units Cooled By Well Water

Hi Paul,

I see these units all the time around here. They do last much longer than a unit that uses freon. They also have the added benefit of being a 24 hour a day sprinkler system. Most of these are also a package unit.



Greg Bell
Titusville, Fl
02111507

Serving Central Florida
Reply With Quote
  #12  
Old 8/26/08, 9:20 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,452
Charley L. Bottger .
Default Re: AC Units Cooled By Well Water

Quote:
Originally Posted by gbell
Hi Paul,

I see these units all the time around here. They do last much longer than a unit that uses freon. They also have the added benefit of being a 24 hour a day sprinkler system. Most of these are also a package unit.
Hi Greg clue me in are you stating the units you see do not use Freon but water as the medium explain please.



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #13  
Old 8/26/08, 9:23 PM
Greg Bell's Avatar
Greg Bell Greg Bell is offline
InterNACHI Member
 
Join Date: Oct 2002
Location: Titusville, FL
Posts: 2,636
Greg Bell .
Default Re: AC Units Cooled By Well Water

HI Charley

I was wrong.

http://cgi.ebay.com/CENTRAL-AC-Unit,...80822181r28423

http://images.google.com/imgres?imgu...IA:en%26sa%3DN



Greg Bell
Titusville, Fl
02111507

Serving Central Florida

Last edited by gbell; 8/27/08 at 12:17 AM.
Reply With Quote
  #14  
Old 8/26/08, 10:33 PM
Colin Cutler Colin Cutler is offline
New User
 
Join Date: Aug 2008
Posts: 7
Colin Cutler hasn't had much positive or negative feedback
Please Note: Colin Cutler is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: AC Units Cooled By Well Water

Hey Paul, Typically, you would have a temperture differential from your incoming water temp to your outgoing water temp. Depending on the water temp coming in I would think there is some type of regulating valve to restrict flow to get around a 10 degree differential, aside from that look for your differential in air temp.
Reply With Quote
  #15  
Old 8/27/08, 12:01 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,452
Charley L. Bottger .
Default Re: AC Units Cooled By Well Water

Quote:
Originally Posted by gbell
HI Charley

Yes they use water and not freon. Most of them that I see are over 30 years old.

http://cgi.ebay.com/CENTRAL-AC-Unit,...80822181r28423

http://images.google.com/imgres?imgu...IA:en%26sa%3DN
Hello again Greg
I am still confused what I was reading in your links just tells me that the condenser is water cooled not that the unit does not use freon. Have you actually opened up one of these units. Just trying to find out if someone else is using a system I have never heard of, still young enough to learn up here in the sticks
Thanks for your response



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off