Default Academic Question

At my inspection today I advised my client that I couldn't start the A/C because of the temperature outside.
He had a large freezer running in the garage and wondered why the freezer operated quite well at low temperature but the A/C could not. It was an unheated attached garage and the temperature, while somewhat above ambient, was still close to the freezing mark. The freezer had been in the garage for several years.
Does anyone know why you can operate freezers in cold temperatures but not A/C?
Reply With Quote
  #2  
Old 2/29/08, 3:09 PM
iniquette's Avatar
iniquette iniquette is offline
InterNACHI Member
 
Join Date: Jan 2008
Location: Markesan, WI
Posts: 1,795
Send a message via ICQ to iniquette
Default Re: Academic Question

I believe the freezer is ok because it was running before temperature drop, and was not idle. The A/C is not running so the oil settles in the compressor. Then you start it up and no oil on parts that need it. I suspect you could run the A/C at low temperature if you had it on before it got cold and just left it run. i could be wrong or just not explaining it correctly, but that has always been my logic. Hope that helps. Anyone correct me if I am wrong.



Ian Niquette
Square One Home Inspection
Markesan WI 53946
www.squareonehomeinspection.com
Active Rain Network
INACHI Awards Portal
Want To Exchange Links?



What we've got here is......failure......to communicate.....
Reply With Quote
  #3  
Old 2/29/08, 3:14 PM
Richard A. Moran, 2nd Richard A. Moran, 2nd is offline
InterNACHI Member
 
Join Date: Jun 2007
Location: Clarksville, MD
Posts: 151
Default Re: Academic Question

That makes perfect sense. A heat pump [ which as we all know is an AC that goes both ways ] has a sump heater to keep it's juices flowing in the winter. Now if he turns off his freezer and the compressor oil freezes that is another story.....

Dick



Dick Moran
True Blue Home Inspections
A Div of RAM2, LLC.
Clarksville, MD
240-832-6838
MD Home Inspector License 29927
Reply With Quote
  #4  
Old 2/29/08, 3:45 PM
Adam Veitenheimer Adam Veitenheimer is offline
Active Poster
 
Join Date: Dec 2007
Location: Philadelphia
Posts: 210
Please Note: Adam Veitenheimer is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Academic Question

Also you have to take into consideration that the freezer should be insulated keeping the cold in and apparently the cold out also, so that combined with the fact that it has been running, everything should be ok, hope he doesnt get a blown fuse or power outage for too long of a time...
Reply With Quote
  #5  
Old 2/29/08, 4:20 PM
iniquette's Avatar
iniquette iniquette is offline
InterNACHI Member
 
Join Date: Jan 2008
Location: Markesan, WI
Posts: 1,795
Send a message via ICQ to iniquette
Default Re: Academic Question

Quote:
Originally Posted by Adam Veitenheimer
Also you have to take into consideration that the freezer should be insulated keeping the cold in and apparently the cold out also, so that combined with the fact that it has been running, everything should be ok, hope he doesnt get a blown fuse or power outage for too long of a time...
\


????????????????????????????????



Ian Niquette
Square One Home Inspection
Markesan WI 53946
www.squareonehomeinspection.com
Active Rain Network
INACHI Awards Portal
Want To Exchange Links?



What we've got here is......failure......to communicate.....
Reply With Quote
  #6  
Old 2/29/08, 4:28 PM
Scott Gilligan,  CMI's Avatar
Scott Gilligan, CMI Scott Gilligan,  CMI is offline
InterNACHI Member
 
Join Date: May 2007
Location: Philadelphia, PA
Posts: 1,828
Send a message via AIM to sgilligan1 Send a message via MSN to sgilligan1 Send a message via Yahoo to sgilligan1
Default Re: Academic Question

Quote:
Originally Posted by Adam Veitenheimer
Also you have to take into consideration that the freezer should be insulated keeping the cold in and apparently the cold out also, so that combined with the fact that it has been running, everything should be ok, hope he doesnt get a blown fuse or power outage for too long of a time...
Do you have any clue what are you talking about?
Reply With Quote
  #7  
Old 2/29/08, 6:58 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Academic Question

Quote:
Also you have to take into consideration that the freezer should be insulated keeping the cold in and apparently the cold out also, so that combined with the fact that it has been running, everything should be ok, hope he doesnt get a blown fuse or power outage for too long of a time...
Totally in left field

Quote:
Now if he turns off his freezer and the compressor oil freezes that is another story.....
Totally in left field

Quote:
I believe the freezer is ok because it was running before temperature drop, and was not idle. The A/C is not running so the oil settles in the compressor. Then you start it up and no oil on parts that need it. I suspect you could run the A/C at low temperature if you had it on before it got cold and just left it run. i could be wrong or just not explaining it correctly, but that has always been my logic. Hope that helps. Anyone correct me if I am wrong.
Guys we need some serious refigeration training here.

Oil in the compressor does not freeze

The major concern about an A/C unit in low ambient temps without crank case heaters is the fact that Freon Migrates to the coldest area of the system which happens to be the compressor where the oil is stored. When you start the compressor that has liquid freon mixed with the oil, the liquid freon can and will damage the valves in the compressor and will also cause the oil to pump out of the compressor. I can go on and on about this but am trying to keep it simple.

BTW refrigerators only have oz.s of freon V/S pounds in a A/C unit and do not have liquid migration as they are not a split system. There has to be two areas with different temps in order to have liquid migration.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging

Last edited by cbottger; 2/29/08 at 7:12 PM..
Reply With Quote
  #8  
Old 2/29/08, 7:01 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Academic Question

Adam the coils are outside the unit, not inside with the food.
Reply With Quote
  #9  
Old 2/29/08, 7:02 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Academic Question

The original question is very good though ,hmmmm
Reply With Quote
  #10  
Old 2/29/08, 7:12 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,620
Default Re: Academic Question

Quote:
Originally Posted by jallingham
At my inspection today I advised my client that I couldn't start the A/C because of the temperature outside.
He had a large freezer running in the garage and wondered why the freezer operated quite well at low temperature but the A/C could not. It was an unheated attached garage and the temperature, while somewhat above ambient, was still close to the freezing mark. The freezer had been in the garage for several years.
Does anyone know why you can operate freezers in cold temperatures but not A/C?
I live in a cold area and my freezer is in my garage .
My garage is insulated and has never gone below freezing it is fastened to the home . -20 F and the garage is at 34.
I talked to a repair mechanic and he said the efficiency on the freezer goes down but it does no seem to effect the operation.
Mine is only 20 years and works well .

Roy Cooke



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #11  
Old 2/29/08, 7:18 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Academic Question

Well they remove heat from the air right, so maybe there is something to them running all the time.
Kinda like a running car with no battery.
Ok till you turn it off.
Reply With Quote
  #12  
Old 2/29/08, 7:20 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Academic Question

Quote:
Originally Posted by rcooke
I live in a cold area and my freezer is in my garage .
My garage is insulated and has never gone below freezing it is fastened to the home . -20 F and the garage is at 34.
I talked to a repair mechanic and he said the efficiency on the freezer goes down but it does no seem to effect the operation.
Mine is only 20 years and works well .

Roy Cooke
Wrong Roy you live in a refrigerator. BTW welcome back



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #13  
Old 2/29/08, 7:24 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Academic Question

Damn I thought it was Marcel.
Hi Roy
Gosh you guys post the same way.
Should call both of you Roycel
Reply With Quote
  #14  
Old 2/29/08, 7:26 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Academic Question

Quote:
Originally Posted by relliott
Adam the coils are outside the unit, not inside with the food.
Yes they are Bob both inside and outside



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #15  
Old 2/29/08, 7:28 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Academic Question

Yeah get all tech on me.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Got a letter from ASHI's President today. gromicko General Inspection Discussion 55 12/12/10 11:51 PM
Interesting Question? jmckenna1 Miscellaneous Discussion for Inspectors 9 11/25/07 1:13 PM
Academic Question jallingham Electrical Inspections 10 3/29/06 9:16 PM


All times are GMT -4. The time now is 10:05 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts