Default What is an acceptable differental tmp

is between 10 and 15 good?



Gary Porter

GLP's Home and Mold Inspections
321-239-0621

Certified Commercial Mold Inspector

Serving Orlando, Kissimmee, Winter Park, Winter Springs, Oviedo, Titusville, Celebration, Harmony, Avalon, Windermere, Deltona, Debary, Sanford
Orange County, Seminole County, Volusia County, Osceola County

www.homeandmoldinspections.com
Reply With Quote
  #2  
Old 9/18/07, 2:59 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,468
Default Re: What is an acceptable differental tmp

I like to see 14 to 22 or so but many things can affect that including humidity and outside temperature.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #3  
Old 9/18/07, 3:01 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 13,934
Default Re: What is an acceptable differental tmp

Quote:
Originally Posted by gporter
is between 10 and 15 good?
Yep ,
I am happy 10 to twenty .
Others think we are doing it wrong.
........... Cookie



If I can answer any questions please send me email Roycooke@hotmail.com

On an inspection and need immediate help call my cell 613-827-2011
Reply With Quote
  #4  
Old 9/18/07, 3:35 PM
gporter's Avatar
gporter gporter is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Orlando, fl
Posts: 3,283
Default Re: What is an acceptable differental tmp

Thanks



Gary Porter

GLP's Home and Mold Inspections
321-239-0621

Certified Commercial Mold Inspector

Serving Orlando, Kissimmee, Winter Park, Winter Springs, Oviedo, Titusville, Celebration, Harmony, Avalon, Windermere, Deltona, Debary, Sanford
Orange County, Seminole County, Volusia County, Osceola County

www.homeandmoldinspections.com
Reply With Quote
  #5  
Old 9/18/07, 4:10 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,686
Default Re: What is an acceptable differental tmp

Do you have a dart board?
Any number will do. It changes hourly and daily anyway.
A dry bulb temperature differential may work pretty accurately in Arizona because the relative humidity is low and changes are slight, but I would be far from comfortable with guessing about it in Florida.
Reply With Quote
  #6  
Old 9/18/07, 4:12 PM
W. Michael Chris's Avatar
W. Michael Chris W. Michael Chris is offline
InterNACHI Member
 
Join Date: May 2005
Location: Santa Clara, UT
Posts: 1,115
Default Re: What is an acceptable differental tmp

This is how I break it down:

Less than 12ºF - inadequate differential. Recommend servicing.
12-14ºF - considered marginal operation. Recommend servicing.
14-16ºF - considered acceptable.
16-18ºF - good operation.
18-20ºF - very adequate operation.
20-22ºF - slightly excessive differential.
22-24ºF - excessive differential - air path may be restricted.

Hope this helps.



Mike Chris, Santa Clara, Utah
NACHI: #05051385
HouseNspect@gmail.com
www.housenspect.com
activerain

"A man's home is his castle . . . until the queen arrives."
Reply With Quote
  #7  
Old 9/18/07, 6:31 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 13,934
Default Re: What is an acceptable differental tmp

Quote:
Originally Posted by wchris1
This is how I break it down:

Less than 12ºF - inadequate differential. Recommend servicing.
12-14ºF - considered marginal operation. Recommend servicing.
14-16ºF - considered acceptable.
16-18ºF - good operation.
18-20ºF - very adequate operation.
20-22ºF - slightly excessive differential.
22-24ºF - excessive differential - air path may be restricted.

Hope this helps.
Can that not vary example Home temp is 65% or the home temp is 90%.

......... Cookie



If I can answer any questions please send me email Roycooke@hotmail.com

On an inspection and need immediate help call my cell 613-827-2011
Reply With Quote
  #8  
Old 9/18/07, 7:01 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: What is an acceptable differental tmp

I agree with Mike's breakdown.

Regardless of inside or outside temps (assuming summer conditions, not winter), the system should cool the air passing the coils to a difference of 16 to 20 degrees.

I have recently discovered that the IR camera gives very accurate information on these temps. You can actually see the air (through thermal imaging) moving into, and out of the system.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #9  
Old 9/18/07, 9:12 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 3,874
Default Re: What is an acceptable differental tmp

Please Lord is this thread subject going to start again I am going to set back and watch this one



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #10  
Old 9/18/07, 9:33 PM
wsiegel wsiegel is offline
Active Poster
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 2,542
Please Note: wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What is an acceptable differental tmp

I would say that about 90% of the time I dont even report the temperature drop. If you have dirty sir handler coils, a dirty filter, damaged ducts, or dirty coil fins on a conenser unit, the machine is now no longer functioning as intended and needs to be cleaned / serviced. I get a look of surprise on a lot of the realtor faces when I tell them I will not report the drop. I tell tem that first they need to clean the system and then test the drop. These machines are made to run with clean filters, coils and non damaged ducts.
Reply With Quote
  #11  
Old 9/18/07, 9:34 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,686
Default Re: What is an acceptable differental tmp

It appears you are both in an arid environment.

Quote:
You can actually see the air (through thermal imaging) moving into, and out of the system.
I am sorry for being such an *****, but you can not determine BTU capacity through dry bulb temp measurements and you can not see air with the BCAM.

Flir makes a CAM that can see gas, but it does not operate in the same range as the BCAM.

You may be able to see moisture temps in the air, but if you have that much moisture in the air, dry bulb temps are more than worthless as an HVCA evaluation.

I sure wish someone with a masters degree in thermodynamics would get in here and shed some new light on this subject because my posts are about as obtuse as the damn latent heat your trying to measure with a dry bulb sensing device.

Quote:
Regardless of inside or outside temps (assuming summer conditions, not winter), the system should cool the air passing the coils to a difference of 16 to 20 degrees.
How can you say this? I expected more from you Jeff. You really dive into things. NACHI is now global. You can't be telling someone from the South East (and places like that) that they can be doing these things! The only way you can tell what the unit is doing is by tapping into the refrigerant system! Yes, it is outside of HI SOP. It is also a violation of the Clean Air Act and you could be fined or go to jail! Why do so many SOP's and State Laws say HVAC evaluation is outside of what we do? Because it is illegal to do it without certification!

Does anyone know what a high efficiency HVAC unit is?
Basically, it is a 2.5 ton compressor in a 3 ton condensing unit.
Larger coils lower head pressure, thus lower amp draw.
Units run longer with less of an amp draw.
Small units work on latent heat long before that can effect the sensible temperature.
You just can't say that you need a 20 degree delta T. The unit is running at capacity, but because of OUTDOOR conditions, it has a lot of work to do before it can effect the dry bulb air temp inside the house.

A gas or electric heater is a sensible heat device.
You get a predetermined BTU output from natural, propane, oil and electric. Refrigerant systems don't work anything like this! It is very VERY dependant on outdoor air temps (not referring to geothermal).
Reply With Quote
  #12  
Old 9/18/07, 9:35 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 18,917
Default Re: What is an acceptable differental tmp

Funny Charley. ha. ha. I'll join ya.
Any cold one's.

Marcel
Reply With Quote
  #13  
Old 9/18/07, 9:48 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 3,874
Default Re: What is an acceptable differental tmp

Quote:
Originally Posted by mcyr
Funny Charley. ha. ha. I'll join ya.
Any cold one's.

Marcel
Going to need more than one this could get long and nasty again.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #14  
Old 9/18/07, 9:56 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: What is an acceptable differental tmp

Quote:
Originally Posted by mcyr
Funny Charley. ha. ha. I'll join ya.
Any cold one's.

Marcel
Great idea Marcel. Might be a good show again.
Reply With Quote
  #15  
Old 9/19/07, 12:43 AM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,852
Default Re: What is an acceptable differental tmp

Quote:
Originally Posted by mcyr
Funny Charley. ha. ha. I'll join ya.
Any cold one's.

Marcel
An excellent idea Marcel, don't mind if I do.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Receptacles not having acceptable blade retention jtedesco1 Electrical Inspections 12 1/28/12 9:40 AM
Acceptable roof rafter repairs ldapkus Exterior Inspections 14 7/17/06 12:49 PM
Acceptable truss? dbucknavich Structural Inspections 21 5/24/06 6:34 PM
acceptable? jweinberg Electrical Inspections 24 3/2/06 10:45 AM


All times are GMT -4. The time now is 1:25 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts