#31
|
||||
|
||||
|
Quote:
Robert O'Connor, PE Consulting Engineer & Inspector LIU CW Post Adjunct Professor NACHI Education Committee www.reporthost.com/-rjo I am absolutely amazed sometimes by how much thought goes into doing things wrong ... |
|
#32
|
||||
|
||||
|
So do I.
|
|
#33
|
||||
|
||||
|
Quote:
As a rough guide many HVAC specialists will check that the larger suction/return line feels very cold (like a cold can from the fridge) and that the smaller liquid/supply line feels very warm. A considerably greater temperature rise than 15 to 20 degrees, which is the split commonly used to roughly check the temperature drop across the indoor coil (after it's been running for a while, and as long as it's not extremely humid or dry). See the attached diagram from the old TOD for a pretty good schematic of an AC system, with some very rough system temperatures. Any HVAC specialist worth his salt wouldn't even hesitate grabbing the gages and thermometer to check superheat/subcooling ... but that is well beyond a typical home inspection. Robert O'Connor, PE Consulting Engineer & Inspector LIU CW Post Adjunct Professor NACHI Education Committee www.reporthost.com/-rjo I am absolutely amazed sometimes by how much thought goes into doing things wrong ... |
|
#34
|
|||
|
|||
|
Please Note:
cgoyette is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
yes you are correct. |
|
#35
|
||||
|
||||
|
Quote:
I have to go get my HI CE tonight and I think this thread will grow by the next time I look. Good Luck Freedom Express Inspections LLC CMOR Thermography Certified Level III #8486 freedomexpressinspections.com www.oklahomathermalinfraredimaging.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F State License # 130 Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging Last edited by cbottger; 9/20/07 at 4:42 PM.. |
|
#36
|
||||
|
||||
|
Call me when you guys are in town, Im buyin. I'll show you guys some differential temp down here in DECEMBER.
A -MARK HOME INSPECTIONS, INC. |
|
#37
|
||||
|
||||
|
Quote:
Freedom Express Inspections LLC CMOR Thermography Certified Level III #8486 freedomexpressinspections.com www.oklahomathermalinfraredimaging.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F State License # 130 Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging |
|
#38
|
||||
|
||||
|
Quote:
http://www.grinchmusical.com/?gclid=...FQ5YgAodjwoM6A ADAIR INSPECTION 972-487-5634 Commercial-Residential-Construction-EIFS-Infrared Thermography TREC # 4563 EDI: EIFS-MA TX # 39 2008 US Member of the Year life is the random lottery of events followed by numerous narrow escapes accept the good |
|
#39
|
|||
|
|||
|
Please Note:
cgoyette is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
man that was hilarious...I clicked the link but looked away and then heard the song...still laughing!!~! |
|
#40
|
|||
|
|||
|
Please Note:
Gary Reecher is a non-member guest and is in no way affiliated with InterNACHI or its members.
The link below will give you a chart to use. You'll need an electronic thermometer that can measure both dry and wet bulb temperatures in the return and a thermometer to measure the supply air temperature. If the return air dry bulb temp is 76 and the wet bulb temp is 76 then the temp drop across the evaporator will be 6.5 degrees. Some will gawk why so low of a temperature drop, but at those db and wb temps the water would be almost fog. But it is a good chart to use. Target Temperature Split for Airflow
|
|
#41
|
||||
|
||||
|
When someone takes a temperature at the return air grill or at a supply air register using an IR thermometer such as a Raytek, they are NOT measuring the temperature of the "air" but rather the temperature of the metal grill/register. That seems to be the thing that keeps getting missed in this never-ending saga of temperature splits. The IR thermometer can not and will not measure the "latent" heat in the air. You need a sling or electronic psychrometer to get the Wet bulb temp. I think David said that earlier. The latent heat can add as much as 20% to the "sensible heat" and if it isn't detected can skew the hell out of this mystical 20 degree split everyone seems to be looking for. I do not remember who said it but trying to determine if the system is performing by using this method is like trying to determine the horsepower of your truck engine by measuring the temperature of the exhaust gases. Before anyone goes into a conniption fit over my use of the word "heat", everything in HVAC is "relative" and is about the transfer of HEAT from one place to another.
"War is an ugly thing, but not the ugliest of things; the decayed and degraded state of moral and patriotic feeling which thinks nothing is worth a war, is worse. A man who has nothing which he cares more about than he does about his personal safety is a miserable creature who has no chance at being free, unless made and kept so by the exertions of better men than himself." - John Stuart Mill |
|
#42
|
||||
|
||||
|
To illustrate I took some pics at the closest supply register and at the return air grill. Note the significant difference in the two temps and also note the humidity at the two. If you really want to get into the physics of it, note that the humidity is "higher" at the supply registers than at the return. I also went and took the readings at the furtherest register and they were pretty consistant to the closest.
"War is an ugly thing, but not the ugliest of things; the decayed and degraded state of moral and patriotic feeling which thinks nothing is worth a war, is worse. A man who has nothing which he cares more about than he does about his personal safety is a miserable creature who has no chance at being free, unless made and kept so by the exertions of better men than himself." - John Stuart Mill Last edited by dedwards; 2/17/08 at 3:56 PM.. |
|
#43
|
|||
|
|||
|
Please Note:
cgoyette is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Very educational, thank you. Greenie Curt |
|
#44
|
||||
|
||||
|
Quote:
Common AC design parameters are return air of 75°F @ 50% RH, which gives you 62°F WB, and a target TD of 19.3°F. Or 70°F @ 50% RH, which gives you 58°F WB, and a target TD of 18.7°F Even for 75°F @ 70% RH, which gives you 68°F WB, it's a target TD of 14°F ... and those are not considered comfortable indoor conditions (but possible if just starting up the system on a muggy day). P.S. Dave ... if you ran the examples with more realistic numbers (0% RH just isn't realistic) you won't see those kinds of differences. Although I understand the point you were trying to make, which is that humidity is a big factor. Just something to keep in mind if your indoor conditions are at the extremes of humidity levels (either very dry or very humid). JMO Robert O'Connor, PE Consulting Engineer & Inspector LIU CW Post Adjunct Professor NACHI Education Committee www.reporthost.com/-rjo I am absolutely amazed sometimes by how much thought goes into doing things wrong ... Last edited by roconnor; 9/23/07 at 1:16 AM.. |
|
#45
|
||||
|
||||
|
Quote:
Thank you Gary! A very productive approach to this subject. That is why this subject should be rehashed. The only problem, a wet bulb temp is needed and there are Inspectors that will consider spending $10k on IR, and there are those that won't kick in for a CHEAP hygrometer for $35 (but still feel the need to "evaluate" HVAC performance). |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Receptacles not having acceptable blade retention | jtedesco1 | Electrical Inspections | 12 | 1/28/12 9:40 AM |
| Acceptable roof rafter repairs | ldapkus | Exterior Inspections | 14 | 7/17/06 12:49 PM |
| Acceptable truss? | dbucknavich | Structural Inspections | 21 | 5/24/06 6:34 PM |
| acceptable? | jweinberg | Electrical Inspections | 24 | 3/2/06 10:45 AM |