Had a 5 yo high end home yesterday with a seal attic design. I do not see a lot of those around here, but the ones I have seen ave always either had electric heat pumps or the specialty gas furnaces with the dual PVC vent that provides both inlet and outlet of combustion air.
This home had what I would call typical Carrier 80 AFUE gas furnaces with only the exhaust vented to the outside. The combustion air would have to be made up from the attic and therefore the living area in this design. I also have a concern about the foam touching the metal flue pipe - not a fire concern, but could the heat in that area lead to moisture problems under the foam? Trying to determine if this is a concern or not. Something just does not seem right about it, but I don't want to make an issue out of it without facts to back me up. Professional Inspector Level I Infrared www.AbsoluteInspections.net www.homeinspectorsplanotx.com www.homeinspectorsmckinney.com Absolute Inspections, LLC 972-463-0887 Last edited by kweiss; 3/8/11 at 9:11 AM.. |
| Need a home inspection in Idaho? Check out InterNACHI's listing of Idaho certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
Here is a picture of the setup. Also, the house was built this way - not modified - no insulation was installed in the floor as is typical for this design.
Professional Inspector Level I Infrared www.AbsoluteInspections.net www.homeinspectorsplanotx.com www.homeinspectorsmckinney.com Absolute Inspections, LLC 972-463-0887 |
|
#3
|
|||
|
|||
|
IMO, this furnace should have an intake routed to the outside of the home. Some manufacturers allow for a wall vent placed in the furnace room for the intake of air, but I always prefer air intake from the outside. As always, refer to manufacturer's recommendations.
CMI, CPI, KS #0110-0094 Termite #16601 KS Radon #KS-MS-0027 BBB A+ Accredited Business Serving the Greater Kansas City Metro Area Eastern Kansas/Western Missouri http://www.metrospeckc.com "If opportunity doesn't knock, build a door"--Milton Berle |
|
#4
|
||||
|
||||
|
How is this attic vented, since it is allowing moisture into it from the living space, below?
James H. Bushart Professional Building Analyst, BPI Missouri, Kansas and Arkansas 314-803-2167 |
|
#5
|
||||
|
||||
|
Not vented. It is a sealed foamed in attic design.
Just spoke with an AC contractor I have worked with over the years - he agrees that it is at the very least not meeting the manufacturer installation guidelines and should be looked at. Will call it out as such. Professional Inspector Level I Infrared www.AbsoluteInspections.net www.homeinspectorsplanotx.com www.homeinspectorsmckinney.com Absolute Inspections, LLC 972-463-0887 |
|
#6
|
||||
|
||||
|
Quote:
A design that was undoubtedly approved by an official and that probably "meets code" but is a bad idea. When you allow moisture to enter a "sealed" space, it must have a place to escape. James H. Bushart Professional Building Analyst, BPI Missouri, Kansas and Arkansas 314-803-2167 |
|
#7
|
||||
|
||||
|
Quote:
“The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#8
|
||||
|
||||
|
Quote:
I am going to call it out and have them at least check it out. Performing those types of calculations are beyond my scope and I would rather have a licensed specialist sign off on it than take a chance. Otherwise it was a pretty nice house with few issues. I called the client and explained it to him as well as put it in the report. Professional Inspector Level I Infrared www.AbsoluteInspections.net www.homeinspectorsplanotx.com www.homeinspectorsmckinney.com Absolute Inspections, LLC 972-463-0887 |
|
#9
|
||||
|
||||
|
Quote:
I disagree With James as the furnace will draw from the home and unless the home has excessive moisture then I do not see how the attic will end up with elevated moisture . The furnace exhaust goes to the out side so much of the air drawn from the home will now end up out side .... Roy Recommend further evaluation by a qualified person Need help on inspection call my cell 613-827-2011 I like email Roycooke@hotmail.com Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun. |
|
#10
|
||||
|
||||
|
Roy,
You may be right in a small attic in the winter, but I really do not see it during the summer. You return would have to really leak bad in the attic to pull out enough moisture. Which pulling attic air is not a good idea anyway |
|
#11
|
||||
|
||||
|
Combustion air can only be drawn from the attic when it is adequately ventilated with a source of outside air. That's common sense. Think about how much air would leave this sealed attic with a negative pressure in the area below it.
We all know how a lack of return in a room can create a positive pressure...and the reverse is also true when a room has a supply duct closed, blocked or improperly sized. A sealed attic is a sealed attic. This is a sealed attic ceiling, not a sealed attic, with no vent and with uncontrolled communication of air between it and the area below it. Inside of it is a fossil fuel powered device dependent upon combustion air to properly burn with no outside source for that air. Enough of negative pressure in this attic, considering the short flue with the possibility of very cold ambient air, could even possibly draw flue gases back into the attic and into an of negative pressure area below it. I'd write it up. James H. Bushart Professional Building Analyst, BPI Missouri, Kansas and Arkansas 314-803-2167 Last edited by jbushart; 3/8/11 at 1:45 PM.. |
|
#12
|
||||
|
||||
|
Quote:
Freedom Express Inspections LLC CMOR Thermography Certified Level III #8486 freedomexpressinspections.com www.oklahomathermalinfraredimaging.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F State License # 130 Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging |
|
#13
|
||||
|
||||
|
Other than the last sentence being stretched, Charlie, what do you think is wrong with what Bushart said?
|
| Need a home inspection in Idaho? Check out InterNACHI's listing of Idaho certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#14
|
||||
|
||||
|
Sealing the underside of the roof does not seal the attic.
There are air bypasses throughout the house in direct communication with the attic. Mechanical fans can pull moist air from the crawlspace through them, and vice versa...why cannot they, in a room with negative pressure, create a negative pressure in a similarly connected attic space? Not only that...but when there is leaking ductwork in the attic creating a positive pressure and everything is "sealed" above it...where else can this warm air go but into the cooler bypasses, some running along the colder exterior? If this were a brand new construction I would anticipate issues and advise, accordingly. If it were an existing structure, I would be looking for and expecting to find problems caused by this set up. I have seen a water heater in a laundry room have the gases sucked out of the flue and into the living space when the clothes dryer was turned on. I have created negative pressures in bedrooms (with no returns) by simply closing the supply vent and running the air handler. How hard is it to create a negative pressure in an unventilated attic space...and what dangers might be derived from mechanical equipment relying upon a consistent source of fresh air to properly operate? James H. Bushart Professional Building Analyst, BPI Missouri, Kansas and Arkansas 314-803-2167 Last edited by jbushart; 3/8/11 at 3:55 PM.. |
|
#15
|
||||
|
||||
|
Quote:
I did not see that there was a crawl space and if we surmise that there is a crawl space how about if this crawl spaced is not vented . Where does the air for the furnace come from . If the dryer is put on now we have increased the lack of air and add the kitchen vent . I live with my other post ,It needs a supply from the out side and needs to be evaluated by a qualified person . These type of discusions are important to help teach and help all ,to improve me and other Homies ... Roy Need help on inspection call my cell 613-827-2011 I like email Roycooke@hotmail.com Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| AC duct not sealed | Lisa Bloemer | Inspecting HVAC Systems | 18 | 9/12/08 11:00 AM |
| Is inadequate roof or attic ventilation a defect? | gliebig | Exterior Inspections | 85 | 1/16/08 6:56 PM |
| Spray Foam to the Rescue ? | mcyr | Structural Inspections | 3 | 3/27/07 7:29 PM |