Default Acceptable Furnace Install in Sealed (foamed) attic

Had a 5 yo high end home yesterday with a seal attic design. I do not see a lot of those around here, but the ones I have seen ave always either had electric heat pumps or the specialty gas furnaces with the dual PVC vent that provides both inlet and outlet of combustion air.

This home had what I would call typical Carrier 80 AFUE gas furnaces with only the exhaust vented to the outside. The combustion air would have to be made up from the attic and therefore the living area in this design. I also have a concern about the foam touching the metal flue pipe - not a fire concern, but could the heat in that area lead to moisture problems under the foam?

Trying to determine if this is a concern or not. Something just does not seem right about it, but I don't want to make an issue out of it without facts to back me up.




Kevin Weiss

Professional Inspector
Level I Infrared
www.AbsoluteInspections.net
www.homeinspectorsplanotx.com
www.homeinspectorsmckinney.com
Absolute Inspections, LLC
972-463-0887

Last edited by kweiss; 3/8/11 at 9:11 AM..
Reply With Quote
Need a home inspection in Idaho? Check out InterNACHI's listing of Idaho certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 3/8/11, 9:13 AM
kweiss's Avatar
kweiss kweiss is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Rowlett, TX
Posts: 1,060
Default Re: Acceptable Furnace Install in Sealed (foamed) attic

Here is a picture of the setup. Also, the house was built this way - not modified - no insulation was installed in the floor as is typical for this design.
Attached Thumbnails
acceptable-furnace-install-sealed-foamed-attic-img_1089.jpg  




Kevin Weiss

Professional Inspector
Level I Infrared
www.AbsoluteInspections.net
www.homeinspectorsplanotx.com
www.homeinspectorsmckinney.com
Absolute Inspections, LLC
972-463-0887
Reply With Quote
  #3  
Old 3/8/11, 9:21 AM
Gary Farnsworth Gary Farnsworth is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Olathe, KS
Posts: 3,715
Default Re: Acceptable Furnace Install in Sealed (foamed) attic

IMO, this furnace should have an intake routed to the outside of the home. Some manufacturers allow for a wall vent placed in the furnace room for the intake of air, but I always prefer air intake from the outside. As always, refer to manufacturer's recommendations.



CMI, CPI, KS #0110-0094 Termite #16601
KS Radon #KS-MS-0027
BBB A+ Accredited Business
Serving the Greater Kansas City Metro Area
Eastern Kansas/Western Missouri
http://www.metrospeckc.com
"If opportunity doesn't knock, build a door"--Milton Berle
Reply With Quote
  #4  
Old 3/8/11, 9:40 AM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,956
Default Re: Acceptable Furnace Install in Sealed (foamed) attic

Quote:
Originally Posted by kweiss View Post
Here is a picture of the setup. Also, the house was built this way - not modified - no insulation was installed in the floor as is typical for this design.
How is this attic vented, since it is allowing moisture into it from the living space, below?



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
  #5  
Old 3/8/11, 9:48 AM
kweiss's Avatar
kweiss kweiss is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Rowlett, TX
Posts: 1,060
Default Re: Acceptable Furnace Install in Sealed (foamed) attic

Not vented. It is a sealed foamed in attic design.

Just spoke with an AC contractor I have worked with over the years - he agrees that it is at the very least not meeting the manufacturer installation guidelines and should be looked at.

Will call it out as such.




Kevin Weiss

Professional Inspector
Level I Infrared
www.AbsoluteInspections.net
www.homeinspectorsplanotx.com
www.homeinspectorsmckinney.com
Absolute Inspections, LLC
972-463-0887
Reply With Quote
  #6  
Old 3/8/11, 9:55 AM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,956
Default Re: Acceptable Furnace Install in Sealed (foamed) attic

Quote:
Originally Posted by kweiss View Post
Not vented. It is a sealed foamed in attic design.

Just spoke with an AC contractor I have worked with over the years - he agrees that it is at the very least not meeting the manufacturer installation guidelines and should be looked at.

Will call it out as such.
It will fail if the floor is not sealed, as well. All of the moisture generated from the living space and from the heating/cooling unit will be trapped there and nasty things will thrive and grow. This will happen even if the HVAC unit is removed.

A design that was undoubtedly approved by an official and that probably "meets code" but is a bad idea.

When you allow moisture to enter a "sealed" space, it must have a place to escape.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
  #7  
Old 3/8/11, 10:58 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Acceptable Furnace Install in Sealed (foamed) attic

Quote:
Originally Posted by kweiss View Post
Had a 5 yo high end home yesterday with a seal attic design. I do not see a lot of those around here, but the ones I have seen ave always either had electric heat pumps or the specialty gas furnaces with the dual PVC vent that provides both inlet and outlet of combustion air.

This home had what I would call typical Carrier 80 AFUE gas furnaces with only the exhaust vented to the outside. The combustion air would have to be made up from the attic and therefore the living area in this design. I also have a concern about the foam touching the metal flue pipe - not a fire concern, but could the heat in that area lead to moisture problems under the foam?

Trying to determine if this is a concern or not. Something just does not seem right about it, but I don't want to make an issue out of it without facts to back me up.
I think you'd have to do a rough calculation on the amount of air required by the furnace BTUs. If it's a large attic, the air volume is probably OK. Even though it's a sealed attic, it isn't hermetically sealed. Air still gets in from the living space.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #8  
Old 3/8/11, 11:11 AM
kweiss's Avatar
kweiss kweiss is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Rowlett, TX
Posts: 1,060
Default Re: Acceptable Furnace Install in Sealed (foamed) attic

Quote:
Originally Posted by jfunderburk View Post
I think you'd have to do a rough calculation on the amount of air required by the furnace BTUs. If it's a large attic, the air volume is probably OK. Even though it's a sealed attic, it isn't hermetically sealed. Air still gets in from the living space.
I tend to agree, Joe, the house was big, but the attics were not huge due to the design. The flame color looked okay, but then the door to the attic was open when I was looking.

I am going to call it out and have them at least check it out. Performing those types of calculations are beyond my scope and I would rather have a licensed specialist sign off on it than take a chance. Otherwise it was a pretty nice house with few issues. I called the client and explained it to him as well as put it in the report.




Kevin Weiss

Professional Inspector
Level I Infrared
www.AbsoluteInspections.net
www.homeinspectorsplanotx.com
www.homeinspectorsmckinney.com
Absolute Inspections, LLC
972-463-0887
Reply With Quote
  #9  
Old 3/8/11, 11:15 AM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,620
Default Re: Acceptable Furnace Install in Sealed (foamed) attic

Quote:
Originally Posted by jbushart View Post
It will fail if the floor is not sealed, as well. All of the moisture generated from the living space and from the heating/cooling unit will be trapped there and nasty things will thrive and grow. This will happen even if the HVAC unit is removed.

A design that was undoubtedly approved by an official and that probably "meets code" but is a bad idea.


When you allow moisture to enter a "sealed" space, it must have a place to escape.
I agree it should use outside air .
I disagree With James as the furnace will draw from the home and unless the home has excessive moisture then I do not see how the attic will end up with elevated moisture .
The furnace exhaust goes to the out side so much of the air drawn from the home will now end up out side .... Roy
Recommend further evaluation by a qualified person



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #10  
Old 3/8/11, 12:50 PM
James E. Braun, CMI's Avatar
James E. Braun, CMI James E. Braun, CMI is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Jefferson City, MO
Posts: 6,945
Default Re: Acceptable Furnace Install in Sealed (foamed) attic

Roy,
You may be right in a small attic in the winter, but I really do not see it during the summer. You return would have to really leak bad in the attic to pull out enough moisture. Which pulling attic air is not a good idea anyway
Reply With Quote
  #11  
Old 3/8/11, 1:38 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,956
Default Re: Acceptable Furnace Install in Sealed (foamed) attic

Combustion air can only be drawn from the attic when it is adequately ventilated with a source of outside air. That's common sense. Think about how much air would leave this sealed attic with a negative pressure in the area below it.

We all know how a lack of return in a room can create a positive pressure...and the reverse is also true when a room has a supply duct closed, blocked or improperly sized.


A sealed attic is a sealed attic. This is a sealed attic ceiling, not a sealed attic, with no vent and with uncontrolled communication of air between it and the area below it. Inside of it is a fossil fuel powered device dependent upon combustion air to properly burn with no outside source for that air.

Enough of negative pressure in this attic, considering the short flue with the possibility of very cold ambient air, could even possibly draw flue gases back into the attic and into an of negative pressure area below it.

I'd write it up.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167

Last edited by jbushart; 3/8/11 at 1:45 PM..
Reply With Quote
  #12  
Old 3/8/11, 2:47 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Acceptable Furnace Install in Sealed (foamed) attic

Quote:
Originally Posted by jbushart View Post
Combustion air can only be drawn from the attic when it is adequately ventilated with a source of outside air. That's common sense. Think about how much air would leave this sealed attic with a negative pressure in the area below it.

We all know how a lack of return in a room can create a positive pressure...and the reverse is also true when a room has a supply duct closed, blocked or improperly sized.


A sealed attic is a sealed attic. This is a sealed attic ceiling, not a sealed attic, with no vent and with uncontrolled communication of air between it and the area below it. Inside of it is a fossil fuel powered device dependent upon combustion air to properly burn with no outside source for that air.

Enough of negative pressure in this attic, considering the short flue with the possibility of very cold ambient air, could even possibly draw flue gases back into the attic and into an of negative pressure area below it.

I'd write it up.
I Truly Truly Truly hope no one out there takes this crap to heart as the gospal. This is about as far off the deep end as one can get



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #13  
Old 3/8/11, 3:20 PM
James E. Braun, CMI's Avatar
James E. Braun, CMI James E. Braun, CMI is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Jefferson City, MO
Posts: 6,945
Default Re: Acceptable Furnace Install in Sealed (foamed) attic

Other than the last sentence being stretched, Charlie, what do you think is wrong with what Bushart said?
Reply With Quote
Need a home inspection in Idaho? Check out InterNACHI's listing of Idaho certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 3/8/11, 3:35 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,956
Default Re: Acceptable Furnace Install in Sealed (foamed) attic

Sealing the underside of the roof does not seal the attic.

There are air bypasses throughout the house in direct communication with the attic. Mechanical fans can pull moist air from the crawlspace through them, and vice versa...why cannot they, in a room with negative pressure, create a negative pressure in a similarly connected attic space?

Not only that...but when there is leaking ductwork in the attic creating a positive pressure and everything is "sealed" above it...where else can this warm air go but into the cooler bypasses, some running along the colder exterior?

If this were a brand new construction I would anticipate issues and advise, accordingly. If it were an existing structure, I would be looking for and expecting to find problems caused by this set up.

I have seen a water heater in a laundry room have the gases sucked out of the flue and into the living space when the clothes dryer was turned on. I have created negative pressures in bedrooms (with no returns) by simply closing the supply vent and running the air handler. How hard is it to create a negative pressure in an unventilated attic space...and what dangers might be derived from mechanical equipment relying upon a consistent source of fresh air to properly operate?



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167

Last edited by jbushart; 3/8/11 at 3:55 PM..
Reply With Quote
  #15  
Old 3/8/11, 3:44 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,620
Default Re: Acceptable Furnace Install in Sealed (foamed) attic

Quote:
Originally Posted by jbushart View Post
Sealing the underside of the roof does not seal the attic.

There are air bypasses throughout the house in direct communication with the attic. Mechanical attic fans can pull moist air from the crawlspace through them...why cannot they, in a room with negative pressure, create a negative pressure in a similarly connected attic space?


I did not see that there was a crawl space and if we surmise that there is a crawl space how about if this crawl spaced is not vented .
Where does the air for the furnace come from .
If the dryer is put on now we have increased the lack of air and add the kitchen vent .
I live with my other post ,It needs a supply from the out side and needs to be evaluated by a qualified person .
These type of discusions are important to help teach and help all ,to improve me and other Homies ... Roy



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AC duct not sealed Lisa Bloemer Inspecting HVAC Systems 18 9/12/08 11:00 AM
Is inadequate roof or attic ventilation a defect? gliebig Exterior Inspections 85 1/16/08 6:56 PM
Spray Foam to the Rescue ? mcyr Structural Inspections 3 3/27/07 7:29 PM


All times are GMT -4. The time now is 10:06 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts