Default Re: Acceptable Furnace Install in Sealed (foamed) attic

Quote:
Originally Posted by cbottger View Post
Your thinking, I thought I could smell wood burning. You don't have the equipment for that.

Yes I stand by my statement a normally operating central system that is a closed loop system will not put a home in the negative or positive situation by its self. I did not say anything about dryers and or exhaust fans removing air from the home.

LOL. I don't blame you for trying to save face by "standing by" a statement that you never made. We'll just keep this to ourselves.

By the way...to most folks.... operating the dryer or exhaust fan, opening or closing a door to a room, or opening and closing vents....would be considered "normal conditions" under which a "normal operating" heating and cooling system would create different levels of positive and negative pressure in different parts of the house.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167

Last edited by jbushart; 3/8/11 at 6:18 PM..
Reply With Quote
Need a home inspection in Oklahoma? Check out InterNACHI's listing of Oklahoma certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #32  
Old 3/8/11, 6:20 PM
kweiss's Avatar
kweiss kweiss is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Rowlett, TX
Posts: 1,060
Default Re: Acceptable Furnace Install in Sealed (foamed) attic

All the petty arguing and name calling on a post I started and have my name and links attached to is not appreciated. This is a PUBLIC forum and that behavior does nothing to create a positive PROFESSIONAL image for the profession that I take very seriously and use to make my living. Take it somewhere else.

Thanks to those that gave serious replies. I reported the issues, they have been verified by a licensed HVAC professional and my clients are extremely happy with my service.

If this is what one can expect from fellow members of what is supposed to be a PROFESSIONAL organization, I am going to have to give serious thought to continuing any association with INACHI. It is a shame that there cannot simply be constructive and PROFESSIONAL discussion about topics that could be learning opportunities for everyone involved.




Kevin Weiss

Professional Inspector
Level I Infrared
www.AbsoluteInspections.net
www.homeinspectorsplanotx.com
www.homeinspectorsmckinney.com
Absolute Inspections, LLC
972-463-0887
Reply With Quote
  #33  
Old 3/8/11, 6:24 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,956
Default Re: Acceptable Furnace Install in Sealed (foamed) attic

Quote:
Originally Posted by kweiss View Post
All the petty arguing and name calling on a post I started and have my name and links attached to is not appreciated. This is a PUBLIC forum and that behavior does nothing to create a positive PROFESSIONAL image for the profession that I take very seriously and use to make my living. Take it somewhere else.

Thanks to those that gave serious replies. I reported the issues, they have been verified by a licensed HVAC professional and my clients are extremely happy with my service.

If this is what one can expect from fellow members of what is supposed to be a PROFESSIONAL organization, I am going to have to give serious thought to continuing any association with INACHI. It is a shame that there cannot simply be constructive and PROFESSIONAL discussion about topics that could be learning opportunities for everyone involved.
Belong...or not...to whatever association you wish.

When contractors begin their posts by bashing the guy they don't agree with, they get it back in the nuts from me. If that bothers you, I will just have to live with that.

Some guys can't be smart. Instead...they have to show how others are "dumb". It's like the contractor your client calls because you called out a service panel full of double taps who tells your client that you don't know what you're talking about...he sees this all the time and never saw a house burn down, yet....and crap like that.

People who can't take it should not dish it out.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
  #34  
Old 3/8/11, 8:13 PM
James E. Braun, CMI's Avatar
James E. Braun, CMI James E. Braun, CMI is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Jefferson City, MO
Posts: 6,945
Default Re: Acceptable Furnace Install in Sealed (foamed) attic

I have seen negative air created with a clothes dryer several times.
What Charlie is saying is true to some effect. Each and every room would have to have a return vent and the furnace blower would need to be keep running. Also the ductwork in the attic would have to be sealed. We would still have trouble with high moisture into the unvented/unconditioned attic though.
Reply With Quote
  #35  
Old 3/8/11, 10:28 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Acceptable Furnace Install in Sealed (foamed) attic

Quote:
Originally Posted by kweiss View Post
All the petty arguing and name calling on a post I started and have my name and links attached to is not appreciated. This is a PUBLIC forum and that behavior does nothing to create a positive PROFESSIONAL image for the profession that I take very seriously and use to make my living. Take it somewhere else.

Thanks to those that gave serious replies. I reported the issues, they have been verified by a licensed HVAC professional and my clients are extremely happy with my service.

If this is what one can expect from fellow members of what is supposed to be a PROFESSIONAL organization, I am going to have to give serious thought to continuing any association with INACHI. It is a shame that there cannot simply be constructive and PROFESSIONAL discussion about topics that could be learning opportunities for everyone involved.
Kevin we have guys on here putting out false information that he has no clue as to what he is talking about just trying to make himself look big to whom I know not. Some one has to police people like that and some times calling someone a knuckle head is the only way to get their attention sorry you were offended maybe you need to toughen up a bit.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #36  
Old 3/9/11, 4:12 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Acceptable Furnace Install in Sealed (foamed) attic

Quote:
Originally Posted by jbraun View Post
I have seen negative air created with a clothes dryer several times.
What Charlie is saying is true to some effect. Each and every room would have to have a return vent and the furnace blower would need to be keep running. Also the ductwork in the attic would have to be sealed. We would still have trouble with high moisture into the unvented/unconditioned attic though.
With this sealed and insulated attic, the attic is essentaially now conditioned space.......my concern: Is the foam a high density closed cell type that essentially forms an air/vapour barrier? If not, in winter, moisture may diffuse through the foam to reach the roof/wall sheathing.

If this furnace is not a sealed combustion, direct vent unit, there are potential combustion air issues. Simply adding an air supply vent to the exterior will not solve the problem in all conditions.....if the outdoor hood of the supply air ducting is ever in the lee of strong winds, it will actually be sucking air out of the attic, not supplying it! In Canada, the WETT Association has a video taken by a homeowner of smoke emitting from the supply air vent to an airtight wood stove during very high, gusty winds!

If this house is very airtight, by having 2 or more exhaust fans (dryer, range hood, bath fan) on at the same time may create enough negative pressure within the building shell to cause backdrafting.
Reply With Quote
  #37  
Old 3/9/11, 11:18 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,925
Default Re: Acceptable Furnace Install in Sealed (foamed) attic

I have been working a job on a high-efficiency "huge house" sitting on top of a hill.

When there is a fire in the first floor fireplace, smoke gets sucked down an adjacent flu (in the same chimney) from three stories above and discharges smoke into the master bedroom through the fireplace there.

Contractors have yet to come to grips with this new technology without abandoning old construction technique.

Also, last week we had a report hit the newswire were someone's kid had a hamster that died. They replaced the hamster and it died two days later so they got a mouse which died in two hours! Hazmat was dispatched to find high levels of CO2 (enough to kill a small rodent). Not CO, CO2. There was no fossil fuel appliances anywhere in the building. The house was built to high-efficiency standards and obviously a design to ensure rodents will not infest the residence!

We have yet to fully see this high energy efficiency technology rare its ugly head.
As far as this situation is concerned, anyone that spends the effort and money on a high-efficiency home and installs an 80% furnace in this manner is a total idiot. This furnace does not have a supply air connection that can be piped to the exterior.
Installing combustion air vents from the attic to the exterior wipes out the entire principal of insulating the roof versus the ceiling. It will also produce the moisture issues at in the attic as those who misunderstand a sealed attic design pointed out concerning moisture entering attic from the finished space below. Adding vents into the attic is not a proper method of mediation.

If properly installed, a sealed attic will not have any problems with moisture levels from the interior of the house, if these moisture levels are properly maintained and someone doesn't do something else stupid. Improper use of humidifiers, failure to use installed ventilation equipment in bathrooms etc. Buy the way, HVAC equipment does not produce moisture inside the house when installed inside the house unless it's leaking all over the place.

Kevin, I think you did good by reporting what you saw, even though you did not have the tools to determine if this is actually a hazardous condition. This evaluation is not part of home inspection and not your job. In principle, this could be a very hazardous situation if we take into account other conditions built into the house.

Whenever I see a high-efficiency home or building, the hair automatically stands up on the back of my neck!

I have not been doing many home inspections since Thanksgiving, but I have been booked up with building performance issues. Surprisingly the majority of them are high-efficiency homes that are improperly built. Maybe it's just that those homeowners expect more and recognize these problems, however I find it interesting at the ratio of buildings with problems in relation to the efficiency standards that the buildings are built by.
 
 



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #38  
Old 3/9/11, 1:25 PM
James E. Braun, CMI's Avatar
James E. Braun, CMI James E. Braun, CMI is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Jefferson City, MO
Posts: 6,945
Default Re: Acceptable Furnace Install in Sealed (foamed) attic

So how does moisture get keep out of a sealed attic?
I have heard of installing a moisture barrier between the living area and the attic, but my concenr is what does the moisture do when it hits the moisture barrier?
Reply With Quote
  #39  
Old 3/9/11, 1:59 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,620
Default Re: Acceptable Furnace Install in Sealed (foamed) attic

If you do not have High Moisture in the Home then you will not have high moisture in a sealed attic .
Unless you send it there from Dryer Bath vent Ect.
No moisture Barrier on any homes I do if they are older and the ceiling has been painted twice then it is no longer a concern unless there are holes.



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #40  
Old 3/9/11, 2:06 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,925
Default Re: Acceptable Furnace Install in Sealed (foamed) attic

It doesn’t.

What is wrong with that amount of moisture in the attic?
It does nothing to a house that does not have a sealed attic.

A sealed attic is no different than a room in the house without a heat/cooling register (bathrooms, walk-in closets...). It is a buffered space that is insulated from the exterior and there is nothing in the space that will be below the dew point.

A sealed attic is an indirectly heated or cooled space.
The roof is insulated, just as the ceiling in a conventional home (only better, no wiring, plumbing, fire suppression, or vent penetrations).

If you have excessive moisture in the house, you will have excessive moisture in the attic.

You will have excessive moisture in the attic in a conventional home because the ventilation is not designed for the excessive moisture which is outside the design parameters anyway.

I may not be following you ...



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #41  
Old 3/9/11, 9:13 PM
James E. Braun, CMI's Avatar
James E. Braun, CMI James E. Braun, CMI is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Jefferson City, MO
Posts: 6,945
Default Re: Acceptable Furnace Install in Sealed (foamed) attic

I think I understand. You just got to watch how much moisture is entered into the living area with a sealed attic than a vented attic, due to the natural water evaporation that occurs.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AC duct not sealed Lisa Bloemer Inspecting HVAC Systems 18 9/12/08 11:00 AM
Is inadequate roof or attic ventilation a defect? gliebig Exterior Inspections 85 1/16/08 6:56 PM
Spray Foam to the Rescue ? mcyr Structural Inspections 3 3/27/07 7:29 PM


All times are GMT -4. The time now is 10:06 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts