Default Adding a A/C unit

Hi
I had a call today from a guy looking for an inspection. He was wanting to know if he can add a A/C unit to the HVAC unit. I haven't done the inspection yet but am curious how i would verify that? I know i would have to calculate all the window drafts and size and many factors but i am just looking for a ball park. Like, what size unit would it have to be to be able to condition a 2000 sq ft home? or a 1500 sq ft home?
Appreciate

Andy Bishop
Bishop Home Inspections, LLC
269-686-6485
bishophomeinspection@charter.net
Reply With Quote
  #2  
Old 1/3/06, 6:25 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 15,860
Russel Ray .
Default Re: Adding a A/C unit

Quote:
Originally Posted by abishop
Hi
He was wanting to know if he can add a A/C unit to the HVAC unit. I haven't done the inspection yet but am curious how i would verify that?
I haven't run into a furnace yet that couldn't have a cooling condenser added to it.

However, cost is a different story.

If the lineset still has to be run, the cost is going to be greater than if the lineset is already in place.

In South Texas many decades ago, we used to try to get one ton for every 1,000 SF. That was a minimum and rarely worked for the homes with glass walls looking out over the Gulf during the humid heat of summer. Eventually, everyone started using two tons for every 1,000 SF, but that was waaaaaaaay too much for the homes with no windows 10 miles from the coast in the non-humid heat of summer and caused its own problems. As far as size goes, then, I'd let the HVAC tech do those calculations because he should, hopefully, take all that other stuff (siting, roof type, wall insulation, etc.) into consideration.
Reply With Quote
  #3  
Old 1/3/06, 8:45 AM
Andy T. Bishop Andy T. Bishop is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Allegan, MI
Posts: 310
Andy T. Bishop hasn't had much positive or negative feedback
Default Re: Adding a A/C unit

Sorry for the ignorance but what is the lineset and what should i be looking for?

Andy Bishop
Bishop Home Inspections, LLC
269-686-6485
bishophomeinspection@charter.net
Reply With Quote
  #4  
Old 1/3/06, 9:14 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 6,937
Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Adding a A/C unit

Dang....guess it is just me but something like that I refer to a HVAC technician...lol...hate to tell a guy one thing and have a tech who is doing it everyday come in and say the HI was wrong...lol



Paul W. Abernathy,CMI,CEI,CEPE
Electrical Plans Examiner/Engineer I
NEC Code Expert & Consultant

- ICC & IAEI Certified Electrical Inspector
- DHCD Virginia Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- DHCD Virginia Certified Electrical Plans Examiner
- DPOR Virginia CE Provider - Electricians
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

P.S. Check me out on Mike Holts 2008 Exam Prep DVD Series.
Reply With Quote
  #5  
Old 1/3/06, 10:45 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 2,834
David A. Andersen .
Default Re: Adding a A/C unit

As Russell indicated there is no way to size an air conditioner in accordance with the square footage of the house. Some contractors can do this based on information which is common knowledge to them such as common type construction for your particular geographical area etc. but there are too many factors involved for you as a home inspector to make that determination.

The issues that you may want to relate to the client is that an air-conditioning coil must be placed on top of the furnace (or down airstream in a horizontal furnace), this requires modifying the existing air ducts for a proper fit. A condensate line to remove water produced by the air conditioner must be routed to a drain or to the exterior of the house. An auxiliary drain pan should also be placed under the furnace as there is unlikely one there for the furnace (if the furnace is located in a finished space or above a finished space). The line set, which is two copper pipes (one that is insulated) must be piped to the outdoor condensing unit. This may require some creative installation as the piping must be installed inside a wall chase or up the side of the building (if on the outside of the building, the refrigerant lines can be installed inside of a false gutter downspout for aesthetics). The outside condensor unit requires a concrete pad, an HVAC disconnect /circuit which must be run from the main electrical panel to the exterior wall where the condensing unit will be located. This requires additional breakers in the main electrical subpanel. The capacity of the unit will be determined by the particular equipment utilized. This is a high amperage circuit requiring substantial current capacity.

The cost of this installation will be affected most by the retrofit requirements running electrical and refrigeration piping to the indoor furnace and main electrical panel.

As posted, any project like this should be referred to the people that will likely be doing the work as there are many variations and unforeseen problems that may be involved in the application. Years ago I could give you an estimate, but today I wouldn't even go there, or try. All the clients want a ballpark estimate but "I won't even attempt a guess".
Reply With Quote
  #6  
Old 1/3/06, 11:38 AM
Doug Edwards,  CMI's Avatar
Doug Edwards, CMI Doug Edwards,  CMI is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Pace (Pensacola), FL
Posts: 2,971
Doug Edwards,  CMI .
Default Re: Adding a A/C unit

If you are not familiar with what a line set is you are already in way over your head for doing HVAC calculations. I know how and I would still refer this to a licensed HVAC contractor.
Reply With Quote
  #7  
Old 1/3/06, 11:57 AM
Andy T. Bishop Andy T. Bishop is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Allegan, MI
Posts: 310
Andy T. Bishop hasn't had much positive or negative feedback
Default Re: Adding a A/C unit

I understand this is above and beyond the scope, i just was more curious than anything. I want to learn more and more as you can never know to much.
David...........you told me EXACTLY what i wanted to hear.
Thanks
Reply With Quote
  #8  
Old 1/3/06, 10:41 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 2,834
David A. Andersen .
Default Re: Adding a A/C unit

Welcome!
Reply With Quote
  #9  
Old 1/5/06, 1:12 PM
jrupert jrupert is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Grove City, OH
Posts: 47
jrupert hasn't had much positive or negative feedback
Default Re: Adding a A/C unit

Don’t forget that effective 1-1-2006 units not meeting 10 seer efficiency rating can no longer be manufactured, and 10 seer units may not be available. The new Fed law requires the unit to be at least 13 seer, this translates to quite a $$ dollar increase in customer cost and the size of the equipment is larger for both the indoor evaporator coil and the out door condensing unit. If the house does not have a newer furnace, he may be required to replace what he has to a smaller stature unit to accommodate the larger more efficient evaporator coil.

Refer him to a local HVAC company and avoid looking unprofessional by giving him wrong information



John Rupert
Accurate Property Inspections
Solitaire Heating & Cooling
CSG Training (HVAC Training & Consulting)
Reply With Quote
  #10  
Old 1/5/06, 1:35 PM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 15,860
Russel Ray .
Default Re: Adding a A/C unit

Quote:
Originally Posted by jrupert
Don’t forget that effective 1-1-2006 units not meeting 10 seer efficiency rating can no longer be manufactured, and 10 seer units may not be available. The new Fed law requires the unit to be at least 13 seer
Can someone post a link to that, or the information itself, so that I can put it in my Interactive Report System Version 2? Thanks.
Reply With Quote
  #11  
Old 1/5/06, 1:40 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 3,174
Michael R. Boyett .
Default Re: Adding a A/C unit

Here's a short thread I started a few weeks ago on the old board regarding the new requirements. Just fyi...http://www.nachi.org/bbsystem/viewto...highlight=seer
Reply With Quote
  #12  
Old 1/5/06, 1:46 PM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 15,860
Russel Ray .
Default Re: Adding a A/C unit

That says:

Quote:
. . . beginning January 23, 2006. Any less efficient unit made prior to this date can still be sold, installed, and repaired, but no additional ones can be manufactured.
I suspect there is information at the DOE web site. If no one else gets there first, I'll find a link this evening or tomorrow.
Reply With Quote
  #13  
Old 1/5/06, 1:55 PM
jrupert jrupert is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Grove City, OH
Posts: 47
jrupert hasn't had much positive or negative feedback
Default Re: Adding a A/C unit

http://www.mindfully.org/Energy/2004...ules3apr04.htm

http://www.howellsac.com/webapp/GetPage?pid=226

http://www.contractingbusiness.com/2...e/False/11710/

Yes the actual date manufactures are required to stop manufacturing is Jan 23rd, but they are currently changing over to the new systems now effective Jan 1.

The lower seer can be sold but not made. Stock here in Ohio should run out in July



John Rupert
Accurate Property Inspections
Solitaire Heating & Cooling
CSG Training (HVAC Training & Consulting)
Reply With Quote
  #14  
Old 1/5/06, 10:36 PM
gmartin2 gmartin2 is offline
New User
 
Join Date: Nov 2005
Location: duluth, mn
Posts: 28
gmartin2 hasn't had much positive or negative feedback
Please Note: gmartin2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Adding a A/C unit

Say Fellows;

Hows' about a Custom Aire forced air furnace serial# c-5672. Age? (1oo,oooBTU)

Geo
Reply With Quote
  #15  
Old 1/6/06, 2:11 PM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 15,860
Russel Ray .
Default Re: Adding a A/C unit

Well, what I can find is that Custom Aire was manufactured by Lear Siegler, which last manufactured in 1975 and is now out of business. So it looks like yours was manufactured in 1972, union week ending May 6 (Saturday).
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
New Geo unit neat system cbottger HVAC 14 4/14/08 3:48 PM
Help with unit size rcarter HVAC 4 2/1/07 5:55 PM
Need Assistance on A/C Unit pcarter HVAC 9 6/21/06 8:23 AM