Do the registers need to be all open for optimum performance?
If some registers are closed.....Does that make a difference. David |
| Find an InterNACHI certified Connecticut Home Inspector (and anywhere else in North America) |
|
#2
|
||||
|
||||
|
Yes.
|
|
#3
|
||||
|
||||
|
For optimum performance, all registers should be open.
Think of it this way: if ALL the registers were closed, the system would not be putting any conditioned air into the building. And the system would be pushing against a wall, so to speak. The system would be stressed trying to push air that wasn't moving. Performance would be zero. If you open one vent, then a small amount of relief would be present and the system would have to work a little less hard. Open 2, a little more relief. 5, some more, etc. etc. So, it's sort of like a scale from zero (all closed) to optimum (all open). Can you measure the effect of closing one vent? I doubt it. But obviously it's a scale...the more you close, the closer you get to zero efficiency. Trying to 'pump' air that cannot move is more likely to damage the system. “The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com Last edited by jfunderburk; 8/3/09 at 10:52 AM.. |
|
#4
|
||||
|
||||
|
Sounds like a crock to me.
That's why there are return vents and adjustable supply vents. You don't need to have all of them all open for the system to perform properly. Course you definitely don't want all of them all closed either. Erby Crofutt B4U Close Home Inspections Georgetown, Kentucky KY Lic# HI-2041 www.b4uclose.com http://www.kentuckyradon.com Kentucky Home Inspections Kentucky Home Inspectors NACHI02090301 "LIKE" me on Facebook Kentucky Homeowner Resources @ http://www.kentuckyhomeinspections.com BLOG by Erby, The Central Kentucky Home Inspector Join Active Rain HERE |
|
#5
|
|||
|
|||
|
For optimum performance the system needs to be balanced. http://performancehvacsystems.com/link.htm
I did some certifications with Enviromental Engineering Consultants, Ernie was a good guy, he is missed. 1st Inspection Services Bruce M. Graham III Gainesville, FL 32608 352 871 8989 Florida Licensed Home Inspector #HI10 Radon Measurment Technician # R2279 NACHI05091592 ICC 5268478 www.1stinspectionsfl.com www.bungalowstomansions.com Last edited by bgraham; 8/3/09 at 4:20 PM.. |
|
#6
|
|||
|
|||
|
Please Note:
Gary Reecher is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
When you start closing off supplies you affect the operation. One or maybe two may not hurt but eventually you will get to the number that where it seriously affects operation. Example: 2 tons of cooling requires 800 cfm of air flow for proper operation. A 6 inch round pipe is rated for close to 120 cfm airflow. Start closing off enough and you will have reduced airflow. Evaporator coils come in two models. Those with thermostatic expansion valves which maintain a fixed superheat. That is no liquid refrigerant going back to the compressor. The other style is a flow accurator system. This system has a varying superheat. This system with reduced air flow will result in zero superheat condition and liquid refrigerant going back to the compressor. Compressors do not like to try to compress liquid. The liquid refrigerant returning to the compressor will also result in oil foaming. The system should have been designed and sized to cool the entire house. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Someone invite the other Canadian Associations to this NACHI event on Wed please. | gromicko | Canadian Inspectors | 28 | 9/13/06 1:28 PM |
| Turmoil At The Top? | gluck | Canadian Inspectors | 34 | 9/4/06 8:07 AM |
| Inspection agreement question | jthalmann | General Inspection Discussion | 16 | 4/8/06 10:58 PM |