Default Air Return question

2001 modular home with a 1992 Coleman furnace. (down-flow)
Problems:
1)No return air grill(s) found.....
2)No furnace filters found....

Take a look at the photo's and give me your advise.
Attached Thumbnails
air-return-question-100_6584.jpg   air-return-question-100_6585.jpg   air-return-question-100_6637.jpg  
Reply With Quote
Need a home inspection in Massachusetts? Check out InterNACHI's listing of Massachusetts certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 10/3/12, 8:06 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 52,616
Default Re: Air Return question

The unit is probably centrally located. The return air is the grill you are looking at in your pic. I assume the door is provided with louvers.

Pretty common in modulars.

The filter is either in the door you took off, is missing or is supposed to be behind the cover in your pic.

What are you showing in pic 2?

If that is B vent it needs 1" clearance to combustibles.



As a Professional Home Inspector, I support the privacy of my clients.

For more information click Trustyourinspector.ORG


www.InspectraPro.com
www.MinnesotaHomeInspector.biz

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Call me

Reply With Quote
  #3  
Old 10/3/12, 8:31 PM
Jim Horton's Avatar
Jim Horton Jim Horton is offline
InterNACHI Member
 
Join Date: Feb 2004
Location: Kokomo, IN
Posts: 529
Default Re: Air Return question

Quote:
Originally Posted by mlarson View Post
The unit is probably centrally located. The return air is the grill you are looking at in your pic. I assume the door is provided with louvers. Yes

Pretty common in modulars.

The filter is either in the door you took off, is missing or is supposed to be behind the cover in your pic.

What are you showing in pic 2? The top of the furnace.

If that is B vent it needs 1" clearance to combustibles. Yes it is a B vent.
It looks to me the large flex duct goes to the roof at the much smaller 2" pvc vent, drawing outside air.
Reply With Quote
  #4  
Old 10/3/12, 9:40 PM
Jim Horton's Avatar
Jim Horton Jim Horton is offline
InterNACHI Member
 
Join Date: Feb 2004
Location: Kokomo, IN
Posts: 529
Default Re: Air Return question

Where r all the HVAC guru's????
Reply With Quote
  #5  
Old 10/3/12, 11:30 PM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is online now
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 12,634
Default Re: Air Return question

were was the condenser ?



Wayne Wilson
East TN Home Inspections LLC
Knoxville, Oak Ridge, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.
865-256-1490

http://site.myhomeinspection.net

Reply With Quote
  #6  
Old 10/3/12, 11:48 PM
Jim Horton's Avatar
Jim Horton Jim Horton is offline
InterNACHI Member
 
Join Date: Feb 2004
Location: Kokomo, IN
Posts: 529
Default Re: Air Return question

Quote:
Originally Posted by wwilson3 View Post
were was the condenser ?
Not sure I understand what you are getting at?
Attached Thumbnails
air-return-question-100_6586.jpg  
Reply With Quote
  #7  
Old 10/4/12, 2:09 AM
Mike Hazelwood's Avatar
Mike Hazelwood Mike Hazelwood is offline
InterNACHI Member
 
Join Date: Mar 2007
Location: Bakersfield, Ca
Posts: 569
Default Re: Air Return question

The top cover grill should have the air filter. The top of the unit contains the blower (pulling air from the living area). More than likely that unit is located in the laundry room, correct? No closet door covering the unit, correct? If so, then door should be louvered/vented. The door or wall between the laundry room and living area should also be vented as to pull air from the living area.




Mike Hazelwood
Bakersfield, California
calpro@calproinspections.com
www.calproinspections.com

Last edited by mhazelwood; 10/4/12 at 2:13 AM..
Reply With Quote
  #8  
Old 10/4/12, 7:29 AM
Jim Horton's Avatar
Jim Horton Jim Horton is offline
InterNACHI Member
 
Join Date: Feb 2004
Location: Kokomo, IN
Posts: 529
Default Re: Air Return question

Quote:
Originally Posted by mhazelwood View Post
The top cover grill should have the air filter. The top of the unit contains the blower (pulling air from the living area). More than likely that unit is located in the laundry room, correct? No closet door covering the unit, correct? If so, then door should be louvered/vented. The door or wall between the laundry room and living area should also be vented as to pull air from the living area.
Yes, correct on all accounts.
Reply With Quote
  #9  
Old 10/4/12, 7:43 AM
Jim Horton's Avatar
Jim Horton Jim Horton is offline
InterNACHI Member
 
Join Date: Feb 2004
Location: Kokomo, IN
Posts: 529
Default Re: Air Return question

I've got the answers for the initial two questions, with your guys input, thank you.

On the top of the furnace, Is this a correct installation where the (larger)flex duct going to the (smaller) pvc pipe through the roof?

And as Michael pointed out about the 1" clearance. I can see where I need to call this out,

If that flex duct is drawing outside air through that small hole in the roof, with no rain cap, then why not just do away with the flex duct?
Reply With Quote
  #10  
Old 10/4/12, 11:30 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: North Central Okla
Posts: 8,094
Default Re: Air Return question

I was out of town and on a roof last evening I am struggling with the thought that the 2 inch is outside air looks like a standard plumbing vent.

I need to know what the flex duct connects to at the furnace or does it. Down flow furnace with supply registers in the floor and the return on the front of the furnace that flex duct makes no sense



http://www.oklahomathermalinfraredimaging.com/
http://www.freedomexpressinspections.com/
Master HVAC Mechanic Retired
Level III Thermographer # 8486 Infraspection Institute
CMI Certified Master Inspector
Residential/Commercial Inspections
Moisture Intrusion Expert Witness
580-268-3340
Reply With Quote
  #11  
Old 10/4/12, 11:38 AM
Jim Horton's Avatar
Jim Horton Jim Horton is offline
InterNACHI Member
 
Join Date: Feb 2004
Location: Kokomo, IN
Posts: 529
Default Re: Air Return question

Quote:
Originally Posted by cbottger View Post
I was out of town and on a roof last evening I am struggling with the thought that the 2 inch is outside air looks like a standard plumbing vent.

I need to know what the flex duct connects to at the furnace or does it. Down flow furnace with supply registers in the floor and the return on the front of the furnace that flex duct makes no sense
I agree with all you say as that is what my thoughts were. The flex duct connects to a flange at the top of the furnace, I assume for the return air.

It does not look right but I (like you) cannot understand why it was done this way. Puzzling???
Reply With Quote
  #12  
Old 10/4/12, 11:46 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: North Central Okla
Posts: 8,094
Default Re: Air Return question

Surley the flex is part of the return could you see where it terminated above the furnace or did it just disappear into an attic area



http://www.oklahomathermalinfraredimaging.com/
http://www.freedomexpressinspections.com/
Master HVAC Mechanic Retired
Level III Thermographer # 8486 Infraspection Institute
CMI Certified Master Inspector
Residential/Commercial Inspections
Moisture Intrusion Expert Witness
580-268-3340
Reply With Quote
  #13  
Old 10/4/12, 11:55 AM
Jim Horton's Avatar
Jim Horton Jim Horton is offline
InterNACHI Member
 
Join Date: Feb 2004
Location: Kokomo, IN
Posts: 529
Default Re: Air Return question

Quote:
Originally Posted by cbottger View Post
Surley the flex is part of the return could you see where it terminated above the furnace or did it just disappear into an attic area
Cathedral ceiling with no attic.
Reply With Quote
Need a home inspection in Massachusetts? Check out InterNACHI's listing of Massachusetts certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 10/4/12, 12:13 PM
Jim Horton's Avatar
Jim Horton Jim Horton is offline
InterNACHI Member
 
Join Date: Feb 2004
Location: Kokomo, IN
Posts: 529
Default Re: Air Return question

I just got a call from a local HVAC guy that said he couldn't explain why it is the way it is but he could fix it by having the flex duct mounted above the door header with a new register instead of up through the roof.
That sounds like a plan.
What do you think Charley?
Reply With Quote
  #15  
Old 10/4/12, 12:32 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: North Central Okla
Posts: 8,094
Default Re: Air Return question

Quote:
Originally Posted by jhorton1 View Post
Cathedral ceiling with no attic.
I understand that but where does the flex duct go when it leaves the furnace connection/flange



http://www.oklahomathermalinfraredimaging.com/
http://www.freedomexpressinspections.com/
Master HVAC Mechanic Retired
Level III Thermographer # 8486 Infraspection Institute
CMI Certified Master Inspector
Residential/Commercial Inspections
Moisture Intrusion Expert Witness
580-268-3340
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Supply vs. Return Register Placement cevans Inspecting HVAC Systems 12 2/27/10 12:29 PM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 10:24 AM
air return question. AdamAdam Inspecting HVAC Systems 5 12/3/06 3:48 PM

All times are GMT -4. The time now is 12:06 AM.
no new posts