Default Am I being lied to?

Sorry if this is the wrong forum and I am not an inspector, just a home owner, but feel like I have been alienated and cheated.

I have a lennox heat pump which was installed 3 years ago, I just bought the condo so I was not the owner at install.

There seems to be a major problem with my unit which was not detected by my inspector.

A few rings of coils on my exterior unit are freezing up. the rest of the unit system has been thoroughly checked from ducts to blower to compressor.

I was told by an independant contractor that the unit was installed improperly. The freezing is caused by blockages in the outside coils due to improper or sloppy "brazing?" or soldering (sp?).

Can i call upon the expert opinions here to
1. confirm the diagnosis, that it is caused by a blockage that can only happen thru improper install?
2. If I have any legal rights against the installer
3. That the work to repair is so honerous that buying a new unit is a better solution (as i was told)

Thanks in advance!!!

Noah
Reply With Quote
  #2  
Old 11/12/08, 10:30 AM
Gerry Beaumont's Avatar
Gerry Beaumont Gerry Beaumont is online now
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 5,208
Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Am I being lied to?

Hi Noah,

I am far from an expert, but that doesn't sound right.

Secondly, what part of the country are you in, and what is the outside air temp when the unit is frosting?

Heat pump outside coils normally frost up when in the heating mode, and are designed to defrost themselves.

Regards

Gerry



Virtue is more to be feared than vice, because its excesses are not subject to the regulation of conscience.
Adam Smith (1723-1790)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106
Reply With Quote
  #3  
Old 11/12/08, 10:56 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 2,834
David A. Andersen .
Default Re: Am I being lied to?

1st, HVAC evaluation is not the responsibility of a Home Inspector.

Next, I will assume that you have a Heat Pump.
Where do you live?

The rings: Got a picture?
At what outdoor temp do you see this?
What is the relative humidity?
What were the refrigerant pressures your contractor took?
Where does the frost start to form on the lines? Can you see?

There is a distribution header inside the unit where a feeder tube joins each of the circuits (rings).

Refrigerant temperature and pressure are relative. Temperature goes down proportionally to pressure.

For a heat pump to absorb heat from the outdoor air (OA), it must be colder than the OA (design is about 30 degrees lower than ambient). So at 60 degrees OA, the coil is around freezing. So why should we not see frost?

1. reduced air flow will give the moisture in the air more time to freeze (lower bypass factor).

2. dirty coils reduce air flow.

3. lower air flow reduces refrigerant pressure and coil temps will go well below 0 degrees F.

4. restriction in the liquid refrigerant line (will be in the area of the frost line) can cause low temps due to lower refrigerant pressures. This can be from brazing materials in the line. This however, will cause frost to start in the small refrigerant line before it enters the outdoor unit, not in the coil circuits. No brazing will be done inside the unit.

5. If this unit was installed after electrical/mechanical failure of the previous HVAC unit, "Crap" from the old unit may have contaminated the new unit causing a restriction. There are screens and filters installed before the small tubes feeding the coil to prevent some of this, but other measures must be taken to clean up the contamination of the previous unit. There are HVAC "standards" for cleaning up burn outs. There are testes to determine if the oil in your new unit has been contaminated.


Heat Pumps freeze up in the course of normal operation.
You have not provided any information to support any defect.
Your expert contractor has not provided any proof (temperature differential across the brazed restriction).

There is no sure way to point a finger at any one responsible party for you to take action against because the work was done before your ownership (so you lack the required information).

You need more information and so do I.



David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Certified Infrared Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://thermalimagingscan.com
HVAC Certification EPA Cert#2046620

Link to my Website at: http://www.midtninspections.com/link-submission

Last edited by dandersen; 11/12/08 at 3:05 PM.
Reply With Quote
  #4  
Old 11/12/08, 11:26 AM
Keith Swift, PhD. Keith Swift, PhD. is offline
InterNACHI Member
 
Join Date: Nov 2005
Location: Northridge, CA
Posts: 1,372
Keith Swift, PhD. is very trusted source of information Keith Swift, PhD. is very trusted source of information Keith Swift, PhD. is very trusted source of information Keith Swift, PhD. is very trusted source of information Keith Swift, PhD. is very trusted source of information Keith Swift, PhD. is very trusted source of information Keith Swift, PhD. is very trusted source of information
Default Re: Am I being lied to?

Thanks, David. That was a learning experience for me.



InterNACHI Vice President, InterNACHI Editor-in-Chief, co-founder CalNACHI

Reply With Quote
  #5  
Old 11/12/08, 3:06 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 2,834
David A. Andersen .
Default Re: Am I being lied to?

Any time Keith!



David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Certified Infrared Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://thermalimagingscan.com
HVAC Certification EPA Cert#2046620

Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #6  
Old 11/12/08, 8:51 PM
Keith Swift, PhD. Keith Swift, PhD. is offline
InterNACHI Member
 
Join Date: Nov 2005
Location: Northridge, CA
Posts: 1,372
Keith Swift, PhD. is very trusted source of information Keith Swift, PhD. is very trusted source of information Keith Swift, PhD. is very trusted source of information Keith Swift, PhD. is very trusted source of information Keith Swift, PhD. is very trusted source of information Keith Swift, PhD. is very trusted source of information Keith Swift, PhD. is very trusted source of information
Default Re: Am I being lied to?

Really very informative. Thank you again.



InterNACHI Vice President, InterNACHI Editor-in-Chief, co-founder CalNACHI

Reply With Quote
  #7  
Old 11/12/08, 11:41 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,452
Charley L. Bottger .
Default Re: Am I being lied to?

Good post David I don't beleive I could add to that other than to tell mister Noah that there are many unscrupleous contractors that will try to pursuade one to buy a complete unit rather than repair. Know who you are dealing with.

Funny this post should come along at this time was on an inspection this morning and had a phone call from one of my HVAC friends about a heat pump he was working on, I was trouble shooting over the phone



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #8  
Old 1/6/09, 2:46 PM
Noah Darrow Noah Darrow is offline
New User
 
Join Date: Nov 2008
Posts: 3
Noah Darrow hasn't had much positive or negative feedback
Please Note: Noah Darrow is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Am I being lied to?

Much apprecited for the response!!

Its been a month since my post and my heating has been working very well...
I am still having a frost issue though, whihc from you post seems to be expected.

Here are a few pics of my unit.
Temperature on thsi day is mild (40 degrees or so) and wet.
http://www.flickr.com/photos/34096288@N04/

You can see the 4 distict frost rings taht are forming.

A question for someone who knows more than me (probably all of you!)

-Does this frost look "normal" for a heat pump
-Should there be any concern that it is only forming on a few "rings", is this indicitive of anything?
-Once i see it very frosted i have been turning off the air to prevent damage, it sounds like this is not necessary, is it?


THANKS!!!
Reply With Quote
  #9  
Old 1/6/09, 4:36 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 2,834
David A. Andersen .
Default Re: Am I being lied to?

No sir, I do not consider that normal operation.

The weather is too warm outside at 40° to be freezing in this manner.
What you see here are four White stripes that indicate there are four circuits to the outdoor coil. Each of these circuits are fed by small distribution tube after it passes through some form of metering device.

This metering device can be a device such as the carburetor on your car that changes the amount of gas passing through it depending on the load requirements. A second type device is an "accurator" which is a small piston with a properly sized hole that controls the amount of refrigerant passing into the coil. This type is most commonly found as the heat pump load is relatively stable at low outdoor temperatures.

This Frost pattern is an indication of a "starved outdoor coil" which can be indicative of a low refrigerant charge and/or an improperly sized accurator, a restricted orifice in the accurator (or in the event that you have a thermal expansion valve (the carburetor type device) where there are several things that could go wrong here.

First of all we must determine that the refrigerant charge is adequate according to manufacturer specifications.

If there is a restriction in the accurator, adding more refrigerant will not change anything.

If you add refrigerant and the frosts goes away, that was the problem.

The problem with heat pumps in the winter time is it there is no accurate way to determine the refrigerant charge without actually weighing the charge. If testing the refrigeration pressures according to the manufacturers charts does not show proper pressures for existing conditions, the refrigerant should be removed and weighed.

A further explanation of what is going on here is that refrigerant is actually being sucked through the outdoor coil by the compressor. If there is a low refrigerant charge or a restriction in the metering device the refrigeration pressures of the outdoor coil will go extremely low. Low pressure results in low temperature (resulting in the frosted lines). Proper charging and metering of the refrigerant through this coil should saturate the coil and provide an even Frost pattern from top to bottom under normal operation.

In the area where the frost is, you are converting liquid refrigerant to a vapor, absorbing large quantities of heat in the process. Once you've run out of liquid refrigerant and the vapor becomes superheated, it can not collect any more heat so the coil doesn't frost on the remainder of the circuit.

Another issue that you're experiencing is improper defrost. The coil freezes up solid after it runs long enough and does not automatically defrost. This is due to improper temperatures where the sensors are and possibly insufficient refrigerant charge to generate enough heat to melt the ice from the coil in an expedited manner controlled by the defrost computer.

Any HVAC contractor that's worth squat with heat pumps should be able to readily determine what's going on.

Considering your previous question about bad soldering techniques diagnosed by your HVAC contractor, the only soldering that is done during installation is at the lower two areas in the picture below.

The quality of workmanship from these photographs appears normal.
The other two areas indicate one individual circuit which is operating under approximately 50% capacity.
Attached Images
File Type: jpg 3174624944_493ecfeb5e_m.jpg (52.6 KB, 21 views)



David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Certified Infrared Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://thermalimagingscan.com
HVAC Certification EPA Cert#2046620

Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #10  
Old 1/6/09, 4:43 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 2,834
David A. Andersen .
Default Re: Am I being lied to?

Noah, I see your on line. If you have further questions, go to the message board on my web site at:
www.midtninspections.com

Lower right sidebar.



David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Certified Infrared Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://thermalimagingscan.com
HVAC Certification EPA Cert#2046620

Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #11  
Old 1/6/09, 4:47 PM
Blaine Wiley Blaine Wiley is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Rotonda West, FL
Posts: 2,381
Blaine Wiley is very trusted source of information Blaine Wiley is very trusted source of information Blaine Wiley is very trusted source of information Blaine Wiley is very trusted source of information Blaine Wiley is very trusted source of information Blaine Wiley is very trusted source of information Blaine Wiley is very trusted source of information Blaine Wiley is very trusted source of information Blaine Wiley is very trusted source of information Blaine Wiley is very trusted source of information Blaine Wiley is very trusted source of information
Send a message via MSN to bwiley
Default Re: Am I being lied to?

Damn good explanation David! Good stuff.



A government big enough to give you everything you want, is strong enough to take everything you have.
-Thomas Jefferson
Reply With Quote
  #12  
Old 1/6/09, 5:11 PM
Gerry Pallotta's Avatar
Gerry Pallotta Gerry Pallotta is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Mississauga, ON
Posts: 432
Gerry Pallotta is well trusted Gerry Pallotta is well trusted Gerry Pallotta is well trusted
Send a message via Yahoo to gpallotta
Default Re: Am I being lied to?

Great info David.



Gerry Pallotta
Alota Home Inspection Services
www.alotahomeinspect.ca
Reply With Quote
  #13  
Old 1/6/09, 11:30 PM
Gary Reecher Gary Reecher is offline
Active Poster
 
Join Date: Aug 2004
Posts: 156
Gary Reecher hasn't had much positive or negative feedback
Send a message via Yahoo to Gary Reecher
Please Note: Gary Reecher is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Am I being lied to?

As an HVAC Service Tech I have a question. Was the indoor coil changed with the condensing unit? If not there is a possibility that this is the problem. Not matching the system will result in problems.
Reply With Quote
  #14  
Old 1/7/09, 3:37 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 2,834
David A. Andersen .
Default Re: Am I being lied to?

What problems do you suspect could occur?



David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Certified Infrared Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://thermalimagingscan.com
HVAC Certification EPA Cert#2046620

Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #15  
Old 1/7/09, 12:30 PM
Gary Reecher Gary Reecher is offline
Active Poster
 
Join Date: Aug 2004
Posts: 156
Gary Reecher hasn't had much positive or negative feedback
Send a message via Yahoo to Gary Reecher
Please Note: Gary Reecher is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Am I being lied to?

Quote:
Originally Posted by dandersen View Post
What problems do you suspect could occur?

Here are some documents about mismatching a system.

Alabama and Power Study

Bristol Compressor Study

Carrier Why you need a matching indoor coil

Mismatched System Article

ARI (Air Conditioning Refrigeration Institute) Brochure on Mismatched Systems

Back in the early 90's the US Department of Energy was concerned about mismatching systems and commissioned Carrier Corporation to test systems with mismatched systems particularly outdated capillary tube metering devices. The study basically shows the same results that Bristol found. Lower performance less capacity. On heat pump systems the charge would have to be constantly readjusted for heating then cooling modes.

The problem of mismatching is being met by some manufacturers requiring the model and serial number of the evaporator on any compressor warranty change outs and disallowing warranty on mismatched systems.