Default Another case of wrong

This was from today's inspect gas fired furnace 80 % efficient located in the attic with primary, secondary condensate drains installed with safety pan.

Who can explain why the drains are wrong and no you do not have to be a CMI to answer.



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.

Last edited by cbottger; 5/13/08 at 11:18 PM.
Reply With Quote
Old 6/12/07, 5:15 PM
Jae Williams
This message has been deleted by jwilliams4. Reason: Missed the picture...
  #2  
Old 6/12/07, 5:25 PM
Jae Williams's Avatar
Jae Williams Jae Williams is online now
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 2,844
Jae Williams is very trusted source of information Jae Williams is very trusted source of information Jae Williams is very trusted source of information Jae Williams is very trusted source of information Jae Williams is very trusted source of information Jae Williams is very trusted source of information Jae Williams is very trusted source of information Jae Williams is very trusted source of information Jae Williams is very trusted source of information Jae Williams is very trusted source of information Jae Williams is very trusted source of information
Default Re: Another case of wrong

On second glance, what appears the be the coil's secondary drain in going into the drain pan. Where does it go from there???



"not just an inspection, but an education"

www.homesweethomecincinnati.com
Reply With Quote
  #3  
Old 6/12/07, 5:58 PM
Bruce M. Graham, III's Avatar
Bruce M. Graham, III Bruce M. Graham, III is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Gainesville, FL
Posts: 1,319
Bruce M. Graham, III is well trusted Bruce M. Graham, III is well trusted Bruce M. Graham, III is well trusted Bruce M. Graham, III is well trusted
Default Re: Another case of wrong

Ya just gota wonder sometimes what people are thinking, well when there not.



Bungalows to Mansions
Professional Inspection Services, LLC
Bruce M. Graham III
Gainesville, FL 32608
352 871 8989
NACHI05091592
ICC 5268478
www.bungalowstomansions.com
Reply With Quote
  #4  
Old 6/12/07, 6:54 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,452
Charley L. Bottger .
Default Re: Another case of wrong

Quote:
Originally Posted by bgraham
Ya just gota wonder sometimes what people are thinking, well when there not.
This was a licensed contractor that installed this. Licensed but not qualified?????
</IMG>



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #5  
Old 6/12/07, 6:58 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,452
Charley L. Bottger .
Default Re: Another case of wrong

Quote:
Originally Posted by jwilliams4
On second glance, what appears the be the coil's secondary drain in going into the drain pan. Where does it go from there???
The secondary drain and the safety pan were Tee'd together and then travel to the exterior of the foundation near the A/C condenser. The secondary drain was draining water at the time of inspection.



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #6  
Old 6/12/07, 7:32 PM
Peter Doane's Avatar
Peter Doane Peter Doane is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Olympia, WA
Posts: 1,981
Peter Doane has a reputation beyond repute Peter Doane has a reputation beyond repute Peter Doane has a reputation beyond repute Peter Doane has a reputation beyond repute Peter Doane has a reputation beyond repute Peter Doane has a reputation beyond repute Peter Doane has a reputation beyond repute Peter Doane has a reputation beyond repute Peter Doane has a reputation beyond repute Peter Doane has a reputation beyond repute Peter Doane has a reputation beyond repute
Default Re: Another case of wrong

Hard to tell from just pictures.
1) Drain line drains into the pan,..
2) The exterior drain pipe is higher then the pan.

Potential overflow - water takes the path of least resistance.



Peter Doane
Realty Check Inspection Service
NACHI ID# 05120681
Reply With Quote
  #7  
Old 6/12/07, 8:11 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,452
Charley L. Bottger .
Default Re: Another case of wrong

Come on guys this one is just glaring at you don't let them CMI's out do you </IMG></IMG>



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #8  
Old 6/12/07, 8:18 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 8,523
Brian E. Kelly .
Default Re: Another case of wrong

The overflow pan piping goes higher than the top of the pan. Neato.





For my next trick I will need a volunteer

ps some of the opinions I have posted here may or may not be factually based.




AZ Cert # 39975
AZ Pest # 050898
Reply With Quote
  #9  
Old 6/12/07, 9:08 PM
William J. Decker's Avatar
William J. Decker William J. Decker is online now
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 5,579
William J. Decker is very trusted source of information William J. Decker is very trusted source of information William J. Decker is very trusted source of information William J. Decker is very trusted source of information William J. Decker is very trusted source of information William J. Decker is very trusted source of information William J. Decker is very trusted source of information William J. Decker is very trusted source of information William J. Decker is very trusted source of information William J. Decker is very trusted source of information William J. Decker is very trusted source of information
Default Re: Another case of wrong

No vent on the drain. The top vent appears to be capped.

In my area, they want these pipes insulated in an open attic.



Will Decker
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #10  
Old 6/12/07, 9:21 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,452
Charley L. Bottger .
Default Re: Another case of wrong

You guys are wearing the wrong hat today I placed the answer to this question in my first post??????



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #11  
Old 6/12/07, 9:26 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,452
Charley L. Bottger .
Default Re: Another case of wrong

Quote:
Originally Posted by wdecker
In my area, they want these pipes insulated in an open attic.
I can under stand insulating these lines up north but what if the furnace is not high efficiency and makes no water. Is it still required to be insulated if water is present only in the cooling season?



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #12  
Old 6/12/07, 9:53 PM
Dan Bowers, CMI Dan Bowers, CMI is offline
InterNACHI Member
 
Join Date: Oct 2003
Location: Shawnee Mission, KS
Posts: 1,426
Dan Bowers, CMI is very trusted source of information Dan Bowers, CMI is very trusted source of information Dan Bowers, CMI is very trusted source of information Dan Bowers, CMI is very trusted source of information Dan Bowers, CMI is very trusted source of information Dan Bowers, CMI is very trusted source of information Dan Bowers, CMI is very trusted source of information Dan Bowers, CMI is very trusted source of information
Default Re: Another case of wrong

Is it insulated inside the metal?????????
Reply With Quote
  #13  
Old 6/12/07, 9:54 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 8,523
Brian E. Kelly .
Default Re: Another case of wrong

I know it is right in front of me Charley and it is killing me................





For my next trick I will need a volunteer

ps some of the opinions I have posted here may or may not be factually based.




AZ Cert # 39975
AZ Pest # 050898
Reply With Quote
  #14  
Old 6/12/07, 10:04 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,452
Charley L. Bottger .
Default Re: Another case of wrong

Quote:
Originally Posted by bkelly2
I know it is right in front of me Charley and it is killing me................
Don't die big guy we need you



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #15  
Old 6/12/07, 10:05 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,452
Charley L. Bottger .
Default Re: Another case of wrong

Quote:
Originally Posted by dbowers
Is it insulated inside the metal?????????
What metal????



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.