Default Anything Wrong Here?

Do you see anything wrong with this? I called it out because that is the same

brick as on the mantel wall. Thats not fire brick, is it?

Thanks, Steve
Attached Thumbnails
anything-wrong-here-notfirebrick.jpg  
Reply With Quote
  #2  
Old 6/22/06, 7:50 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: Anything Wrong Here?

Looks good to me.

It appears to be a fire-rated material.
Reply With Quote
  #3  
Old 6/22/06, 8:59 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,686
Default Re: Anything Wrong Here?

"Fire Brick" is commonly referred to the synthetic liner of fabricated fireplaces and panels on the inside of stoves.

Brick is brick in your case. So long as it is not the "stick on" type you have sufficient fire rating. The Mantel wall is also fire-proof!
Reply With Quote
  #4  
Old 6/22/06, 10:13 PM
scosta's Avatar
scosta scosta is offline
Active Poster
 
Join Date: Oct 2005
Location: North Royalton, Oh
Posts: 186
Please Note: scosta is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Anything Wrong Here?

Sorry Guys, I'm not buyin it.Regular brick isn't the same, it isn't built to take the heat. Didn't you ever build a fire ring in the back yard out of some old brick? When the fire got hot, the bricks cracked.(at least mine did) I have and have had fireplaces, woodburning fireplace inserts and woodburning furnaces, and in every one of them are "fire brick" they are heavy, come in varying thicknesses and are kind of a cream color. I am gonna contact a CSIA certified chimney sweep and see what they say.I will let you know, Steve
Reply With Quote
  #5  
Old 6/23/06, 12:23 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,758
Default Re: Anything Wrong Here?

Looks like a standard masonry fireplace/chimney. I would have walked right on by and not given it a second thought. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #6  
Old 6/23/06, 1:24 AM
gmaher gmaher is offline
New User
 
Join Date: Jul 2005
Location: Fargo, ND
Posts: 97
Please Note: gmaher is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Anything Wrong Here?

I have never seen firebirck of that color, brick red. It is always a creamy yellow, even if you scrub the soot off of the brick, it should come up creamy yellow. So, my vote is that it is regular brick and NOT firebrick. I have assembled more than one fireplace with firebrick and from different suppliers - the firebrick was creamy yellow. My vote, not firebrick but regular brick.

George Maher
Home - Safe Home, L.L.C.
Fargo, ND
Reply With Quote
  #7  
Old 6/23/06, 2:01 AM
Russell L. Britton Russell L. Britton is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Evans, Ga.
Posts: 119
Default Re: Anything Wrong Here?

Steve,
If we were taking a poll I would vote for regular brick. Have never seen fire brick that color. Let us know what you find out with the CSIA.

Russell
Reply With Quote
  #8  
Old 6/28/06, 12:00 AM
scosta's Avatar
scosta scosta is offline
Active Poster
 
Join Date: Oct 2005
Location: North Royalton, Oh
Posts: 186
Please Note: scosta is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Anything Wrong Here?

No reply to my first email to a sweep. Sent another email tonight, will keep you posted.

Steve
Reply With Quote
  #9  
Old 6/28/06, 12:58 AM
edrover edrover is offline
InterNACHI Member
 
Join Date: Apr 2006
Location: Pickering, On
Posts: 1
Default Re: Anything Wrong Here?

Hi steve
Been building fireplaces for 25 years, NO that is not fire brick and it is not the same as fire brick. I'm from Ontario and that would definitely NOT pass inspection. Not only would it not pass building code but it is a fire hazard. I would also assume that it was built with regular mortar in the joints instead of fire cement. Its only a matter of time before the mortar starts to weaken and deteriorate. That brick I'm seeing in the picture looks like a common bark clay brick. Hope this answers your question.
Reply With Quote
  #10  
Old 6/28/06, 1:33 AM
Darrell B. Hadler's Avatar
Darrell B. Hadler Darrell B. Hadler is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Medicine Hat, AB
Posts: 367
Default Re: Anything Wrong Here?

Agreed...firebox must be fire brick, they are made to stand the extreme heat that the fire produces and keep that heat inside the fire box.
Reply With Quote
  #11  
Old 6/28/06, 9:12 AM
Blaine Wiley Blaine Wiley is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Rotonda West, FL
Posts: 3,161
Send a message via MSN to bwiley
Default Re: Anything Wrong Here?

Steve,

How old was that house? Fireplaces were frequently built that way in the 40's and 50's. When I used to live in a cold climate, I would see them all of the time.

If it is that old, has it not withstood the test of time?

Always recommend a level II inspection by a CSIA or equivalent anyway.
Reply With Quote
  #12  
Old 6/28/06, 10:44 PM
scosta's Avatar
scosta scosta is offline
Active Poster
 
Join Date: Oct 2005
Location: North Royalton, Oh
Posts: 186
Please Note: scosta is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Anything Wrong Here?

House was built in 1986.

I did call it out for further inspection.

Here is the reply from a CSIA sweep that looked at the picture.

The NFPA 211 states that if a low duty fireclay brick is used the total thickness of the back and sides shall be 8 inches, with a minimum of 2 inches of firebrick lining the firebox. 11.2.1.5 Where the lining is not provided the thickness of the back and sides shall not be less than 12 inches.--that IS FROM OUR STOVE SHOP MANAGER AND CERTIFIED SWEEP AND IS DIRECTLY FROM NFPA 211 FIRE CODE

I wouldn't know how to figure that out after its constructed, but thats the professional answer, I'm just glad I called it out and refered it to a pro.
Steve

Last edited by scosta; 6/28/06 at 10:45 PM.. Reason: readability
Reply With Quote
  #13  
Old 6/29/06, 10:06 AM
scosta's Avatar
scosta scosta is offline
Active Poster
 
Join Date: Oct 2005
Location: North Royalton, Oh
Posts: 186
Please Note: scosta is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Anything Wrong Here?

The other reply also came in,

When building a fireplace and using NFPA 211 2006 edition or any of the past 6 editions I have seen they all say



11.2* Masonry Fireplaces.
11.2.1 Construction.
11.2.1.1 Fireplaces shall be constructed of solid masonry
units or of reinforced portland or refractory cement concrete.

or

11.2.1.4 Where a lining of low-duty fireclay brick (ASTM C
27, Standard Classification of Fireclay and High-Alumina Refractory
Brick), firebox brick (ASTM C 1261, Standard Specification for
Firebox Brick for Residential Fireplaces), or the equivalent, at least
2 in. (51 mm) thick laid in medium-duty refractory mortar
(ASTM C 199, Standard Test Method for Pier Test for Refractory
Mortars), or the equivalent, or other approved lining is provided,
the total thickness of back and sides, including the lining,
shall be not less than 8 in. (203 mm).

You can get a copy of this at any library to look at
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Another case of wrong cbottger Inspecting HVAC Systems 23 6/21/07 7:05 PM


All times are GMT -4. The time now is 8:48 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts