Default Attic Gas Fired Forced Air blows cold starting

This is my house but it has bugged me since moving in 4 yrs ago. My home has two heating/AC systems, one in the basement and the other in the attic. Both are forced air gas fired systems. The unit that serves the second floor blows cold air for about 4-5 seconds in the Winter each time it runs. I understand that the ducting is located in the unheated attic and it makes complete sense that I would get a short blast of cold air whenever it first comes on but it just seems like a design problem. This is my first home with a heating plant located in the attic. Is this a common complaint?

Dick
Reply With Quote
  #2  
Old 1/7/08, 6:35 PM
rramsey rramsey is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Bertram, Tx
Posts: 46
Please Note: rramsey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Attic Gas Fired Forced Air blows cold starting

Very common. I have heard it hundreds of times in 40 years of HVAC work.
Every one is so spoiled to central air. Imagine what our grandparents went through & we complain of a little cold air.
Reply With Quote
  #3  
Old 1/7/08, 7:29 PM
cbottger's Avatar
cbottger cbottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,738
Default Re: Attic Gas Fired Forced Air blows cold starting

Not a lot of options here don't know how old your furnaces are; your fan can be powered up either by time from a solid state board which is not adjustable but if you have an older furnace that has a heat activated fan switch which is adjustable the setting can and often is down around 90 degrees and that is to low I preferred mine to be above 100 and can set as high as 115 this allows the heat to rise up the plenum into the duct before the blower motor starts. Other than that your only option is to add more insulation to your duct work within the attic.

If your furnace is a horz in the attic your probally SOL



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #4  
Old 1/8/08, 10:47 AM
Richard A. Moran, 2nd Richard A. Moran, 2nd is offline
InterNACHI Member
 
Join Date: Jun 2007
Location: Clarksville, MD
Posts: 112
Default Re: Attic Gas Fired Forced Air blows cold starting

The "fix" I use to get around this problem is to install those plastic air diverters on the two ceiling vents located over our bed. Instead of washing down the windows and on to our bed it deflects the air into the room. Maybe not the best solution but it is cheap and almost invisible.
Thanks for your replies,
Dick Moran
MD HI #29927
Reply With Quote
  #5  
Old 1/8/08, 11:38 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 3,701
Default Re: Attic Gas Fired Forced Air blows cold starting

Insulate the duct more.

If the duct is on the attic floor, cover it with insulation.

The attic is a crappy place for the hvac no matter how you look at it, but saves you a closet!

Just perceive this, heat transfer rate is directly relative to the temperature difference inside and outside the duct. Q= 1/R * A * Delta T

For every degree difference there is one multiplier involved. 5 degrees is 5x faster.

Insulation only slows things down, but it may keep the air in the duct warmer between cycles. Also if the air registers are in the ceiling, warm air will rise up into the duct and if insulated more, will not be lost to the attic and when the furnace starts the air will be warmer.

Rolls of foil faced duct wrap are wider and easy to use and will also reject heat in the summer. The batt insulation is much more effective than loose fill.

The expense may be more than you are bothered by the draft!
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Building Science- research from respected sources Brian A. MacNeish Ancillary Services & Additional Topics 12 2/13/08 12:33 PM
Is inadequate roof or attic ventilation a defect? gliebig Exterior 85 1/16/08 7:56 PM
Spray Foam to the Rescue ? mcyr Structural 3 3/27/07 8:29 PM


All times are GMT -4. The time now is 9:14 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts