Default Re: Attic ventilation requirement

Here's an example of how I word it:


"The attic space is considered to have inadequate ventilation. Only two gable vents provide ventilation for the structure. For venting to be effective the air has to be able to move. It is recommended that the structure be ventilated with both: A) An intake preferably located as close to the eaves as possible. (Most often this is done through soffit vents. Ensure the soffit vents are not obstructed by insulation.) B) An exhaust preferably located as close to the ridge as possible.
The total net free ventilating area should not be less than 1 to 150 of the area of the space ventilated except that the total area is permitted to be reduced to 1 to 300...” provided mechanical ventilators are used. When only gable vents are used, effectiveness is more determined by wind movement. Area calculations were not conducted; it is recommended that a state licensed general contractor evaluate the adequacy of attic ventilation and add ventilation as deemed necessary. Reference: International Residential Code R806.1/R806.2"



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #17  
Old 4/5/06, 12:31 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,559
Default Re: Attic ventilation requirement

Very nice, Joe. Very, very nice.



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #18  
Old 4/5/06, 3:06 AM
Gary Reecher Gary Reecher is offline
Active Poster
 
Join Date: Aug 2004
Posts: 273
Send a message via Yahoo to Gary Reecher
Please Note: Gary Reecher is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Attic ventilation requirement

Any addition of attic exhaust fans should be followed up by recommending that the draft of all natural vent equipment be tested with a draft meter. Addition of any exhaust motors can cause back drafting.
Reply With Quote
  #19  
Old 4/5/06, 5:20 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,686
Default Re: Attic ventilation requirement

Also note that the vent area is NET AREA. That is the opening of the vent, less the mesh or screen restriction. The vent Mfg lists this info.
Reply With Quote
  #20  
Old 4/5/06, 5:28 PM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 8,067
Default Re: Attic ventilation requirement

I'm inspecting 24 new Townhouses, they all have a flat roof system with no ventilation at all, and excepted by the AHJ.

The building plans do not call for any ventilation of the rafter system.....
Reply With Quote
  #21  
Old 4/5/06, 6:16 PM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,559
Default Re: Attic ventilation requirement

Quote:
Originally Posted by dandersen
Also note that the vent area is NET AREA. That is the opening of the vent, less the mesh or screen restriction. The vent Mfg lists this info.
I've never seen a manufactured soffit vent, gable vent, or ridge vent. I've always constructed them myself as a necessary part of the structure.



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #22  
Old 4/5/06, 11:55 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,686
Default Re: Attic ventilation requirement

If you make it yourself, do the math.
Reply With Quote
  #23  
Old 4/6/06, 1:03 AM
ccarrington's Avatar
ccarrington ccarrington is offline
InterNACHI Member
 
Join Date: Jul 2005
Location: Abilene, TX
Posts: 69
Default Re: Attic ventilation requirement

Free is exactly that, Unencumbered by nothing, not so much a 1 single louver. Louvers and coverings reduce the free flow of air. I use a 50% reduction of free flow for louvers vents, 75% reduction for turbines and I follow the MFG instruction for other systems. Wood louvers are very inefficient at a 75% reduction to free flow… Hope that helps
Reply With Quote
  #24  
Old 4/6/06, 1:28 AM
Mark A. Timpani, CMI's Avatar
Mark A. Timpani, CMI Mark A. Timpani, CMI is offline
InterNACHI Member
 
Join Date: May 2004
Location: Tucson, AZ
Posts: 2,131
Default Re: Attic ventilation requirement

I did a new house on Monday. 1600 sq ft floor plan. No turbine, ohagen(sp) or soffit wents. Only one 2ft gable vent on one end of the attic area. I recommended more ventilation and insulation. The insulation was only about R-20 and was supposed to be R-32. My client brought this up to the super who asked the builder and they all ended up with the prints at the county building.

I guess here in AZ., for ventilation,they do not use the IRC. In 2001 or 2 due to thermal imaging, they came up with thier own formula and can almost have zero ventilation to create a dead air space. They said the lack of moisture here does not create problems that are found elsewhere.

Today (Wed.) I got a call from our client saying that although the builder stated that the current vent is ok according to the code, he is going to install 8 Ohagen(sp) vents. My client also said that today they went and blew in more insulation.

Sometimes things work out the way they should...




"Be Proud of Your Home, Go With Pride!"
'Not just a Home Inspection, but an Education'

Pride Property Inspections provides professional Home Inspections throughout Tucson and Southern Arizona including Pima, Cochise, Pinal, Santa Cruz, Graham counties.

Reply With Quote
  #25  
Old 4/6/06, 1:35 AM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 8,067
Default Re: Attic ventilation requirement

Quote:
Originally Posted by mtimpani
I guess here in AZ., for ventilation,they do not use the IRC. In 2001 or 2 due to thermal imaging, they came up with thier own formula and can almost have zero ventilation to create a dead air space. They said the lack of moisture here does not create problems that are found elsewhere.
Mark, I have been finding less ventilation, more insulation on the ceilings, and a thermal barrier on the OSB lately (new construction).
Reply With Quote
  #26  
Old 4/6/06, 2:40 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,559
Default Re: Attic ventilation requirement

Quote:
Originally Posted by mtimpani
ohagen(sp) . . . vents.
More information, please.
Pretty please.
Oh please oh please.
Darn margaritas.



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #27  
Old 4/6/06, 10:40 AM
Mark A. Timpani, CMI's Avatar
Mark A. Timpani, CMI Mark A. Timpani, CMI is offline
InterNACHI Member
 
Join Date: May 2004
Location: Tucson, AZ
Posts: 2,131
Default Re: Attic ventilation requirement

Sorry R2, so far I can't find a pic. They are called O'hagen roof vents or invisivents. They look just like the tiles when you are looking at a tile roof. Same colors, same profile, they just stick up about 1/2 inch or inch higher then the tiles. So from the road you can not even tell they are on the house.




"Be Proud of Your Home, Go With Pride!"
'Not just a Home Inspection, but an Education'

Pride Property Inspections provides professional Home Inspections throughout Tucson and Southern Arizona including Pima, Cochise, Pinal, Santa Cruz, Graham counties.

Reply With Quote
  #28  
Old 4/6/06, 10:48 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,559
Default Re: Attic ventilation requirement

Ah-ha.

I know exactly what you're talking about. Thanks.



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #29  
Old 4/6/06, 11:17 PM
Jay Moge's Avatar
Jay Moge Jay Moge is offline
Active Poster
 
Join Date: Aug 2005
Location: Derry New Hampshire
Posts: 761
Please Note: Jay Moge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Attic ventilation requirement

not to hijack another thread, but i've been looking for some info on metal roofs installed over shingles. it seems to be common practice up here, my question is, does this effect the venting at all, they do have ridge vents, kind of, and there's about 1'' of air space between metal and shingle. the ridge and drip edges aren't "air tight" but they do deflect water well.
Reply With Quote
  #30  
Old 4/7/06, 10:58 AM
Mark A. Timpani, CMI's Avatar
Mark A. Timpani, CMI Mark A. Timpani, CMI is offline
InterNACHI Member
 
Join Date: May 2004
Location: Tucson, AZ
Posts: 2,131
Default Re: Attic ventilation requirement

If any one has pics of O'hagen vent could you please post them?




"Be Proud of Your Home, Go With Pride!"
'Not just a Home Inspection, but an Education'

Pride Property Inspections provides professional Home Inspections throughout Tucson and Southern Arizona including Pima, Cochise, Pinal, Santa Cruz, Graham counties.

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Is inadequate roof or attic ventilation a defect? gliebig Exterior Inspections 85 1/16/08 7:56 PM
Info on Attic Ventilation dfogleman Exterior Inspections 0 1/6/07 6:47 AM
Historical perspective of attic ventilation escanlan Exterior Inspections 2 8/28/06 7:20 PM