Default Barometric damper

At a loss today. 1943 built home with furnace that is only a couple years old. High effeciency oil burner. Then I noticed that the barometric damper had been sealed with clear silicone. Has anybody seen this done before? And perhaps a reason why?

Also, in opening the cabinet, there was a lot of powdery substance in the bottom of the tray. Not sure what it is except maybe an absorbant for spilled oil. The furnace tech was leaving just as I arrived. Any clues?




Stephen Stanczyk
Washington State Licensed Home Inspector # 221
President, Washington Association of Property Inspectors (WAPI)
(253) 241-0602 calls answered until 10pm


Pierce County -Thurston County - King County - Snohomish County

Last edited by sstanczyk; 3/22/09 at 1:31 AM..
Reply With Quote
  #2  
Old 2/23/06, 12:34 AM
Jay Moge's Avatar
Jay Moge Jay Moge is offline
Active Poster
 
Join Date: Aug 2005
Location: Derry New Hampshire
Posts: 761
Please Note: Jay Moge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Barometric damper

I can't think of any logical reason the damper was sealed, mayby noise? that powder is most likely "speedy dry". it's a clay that absorbs all the fuel oil spilled by the tech. from servicing the unit. when you run out of oil or have to break the lines to the burner, some pressure is needed to bleed the air out and get the thing running. i like to catch it in a can or cup, this guy just let it flow. not to profesional.
Reply With Quote
  #3  
Old 2/24/06, 7:58 PM
Patrick Bolliger's Avatar
Patrick Bolliger Patrick Bolliger is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Chicago, IL
Posts: 890
Send a message via Skype™ to pbolliger
Question Re: Barometric damper

Was the Damper a manually operated damper?

In Chicago you can not have a manual Barometric Damper in your flue.
An automatic damper is acceptable.

This could have to do with proper daft issues. Flue sizes perhaps with respect to proper chimneydraw .. Was any other appliance (water heater) removed from the same chimney flue / smoke pipe connection?

Or the homeowner felt a draft coming down from the chimney and figured it was not right so it was sealed. Hmmm You have to wonder who did this. I don't think a HVAC tech would use clear silicone for this "fix"...

Last edited by pbolliger; 2/24/06 at 8:05 PM..
Reply With Quote
  #4  
Old 2/25/06, 2:50 AM
Stephen W. Stanczyk's Avatar
Stephen W. Stanczyk Stephen W. Stanczyk is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Kapowsin, WA
Posts: 4,965
Send a message via AIM to sstanczyk
Default Re: Barometric damper

The only other item that may have been attached to the chimney was an old cooking stove that was closed off decades ago up in the kitchen, well before the installation of this new heating unit.




Stephen Stanczyk
Washington State Licensed Home Inspector # 221
President, Washington Association of Property Inspectors (WAPI)
(253) 241-0602 calls answered until 10pm


Pierce County -Thurston County - King County - Snohomish County
Reply With Quote
  #5  
Old 2/28/06, 10:38 PM
William Warner's Avatar
William Warner William Warner is offline
InterNACHI Member
 
Join Date: May 2003
Location: Dayton, OH
Posts: 3,293
Default Re: Barometric damper

Quote:
Originally Posted by pbolliger
Hmmm You have to wonder who did this. I don't think a HVAC tech would use clear silicone for this "fix"...
No, but some one calling themselves an HVAC tech might.

"I'm not an HVAC tech, but I play one on TV"




Submit your AWARDS NOMINATIONS here

Visit the InterNACHI Awards web portal here

Blessed are the blissfully ignorant... for they shall be easily led...
Reply With Quote
  #6  
Old 3/1/06, 3:40 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Barometric damper

Recommend damper to be free-moving. All oil fired appliances need a damper.

If there is an additional damper built into the chimney itself, recommend it be permanently sealed.
Reply With Quote
  #7  
Old 3/1/06, 10:44 PM
Harvey Gordon's Avatar
Harvey Gordon Harvey Gordon is offline
InterNACHI Member
 
Join Date: Mar 2004
Location: Margate, FL
Posts: 249
Default Re: Barometric damper

Not that anything the guys above said is wrong...and I am sure that you probably know this...but in the absence of knowledge "Uncommon condition exists at the damper, recommend further evaluation by Licensed Qualified HVAC contractor."





Harvey Gordon
- President -
FloridaNACHI
(The OFFICIAL Florida State Chapter of NACHI)
SEFloridaNACHI
(Serving NACHI Members in Martin, Palm Beach, Broward, Miami-Dade, and Monroe Counties)
______________
Questions or Comments about FloridaNACHI or if you would like to start a LOCAL Florida Chapter may be sent directly to me at hgordon@fl.nachi.org
______________







Reply With Quote
  #8  
Old 3/2/06, 8:00 AM
jrupert jrupert is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Grove City, OH
Posts: 47
Default Re: Barometric damper

The purpose of the damper is to allow cool air into the flue to bring down the temperature of the exiting flue gas, also to maintain proper venting and combustion efficiency. Sealing the damper decreases the efficiency, creates a possible carbon monoxide hazard and a possible fire hazard with in the flue to the roof.

The power does look like oil dry ??



John Rupert
Accurate Property Inspections
Solitaire Heating & Cooling
CSG Training (HVAC Training & Consulting)
Reply With Quote
  #9  
Old 3/6/06, 7:30 AM
Gary Reecher Gary Reecher is offline
Active Poster
 
Join Date: Aug 2004
Posts: 273
Send a message via Yahoo to Gary Reecher
Please Note: Gary Reecher is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Barometric damper

Is this an oil burner furnace? What make? Model? Some of the newer oil burners are direct vent but they must be set up according to manufacturers installation instructions.
Reply With Quote
  #10  
Old 3/9/06, 1:13 PM
Patrick Bolliger's Avatar
Patrick Bolliger Patrick Bolliger is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Chicago, IL
Posts: 890
Send a message via Skype™ to pbolliger
Talking Re: Barometric damper

In all cases the best approach is what the Mfg. installation instructions state. I think we are all on the same page here. The local AHJ may modify the install instructions but as we all know at some point upgrades/ modifications by (Homeowners, HVAC techs) do happen so original installs do change along with configurations...maybe. I hope the manual is available somewhere close to the appliance and should be there for all of us.

I always like to check the MFG. plates on the appliances after I get a general view of the install. Orphaned appliances, bad installs or modifications and efficiency of many appliances are coming into play. So what does that do for us? I think it makes it more of a detective thing with respect venting/ combustion air / dilution air and so on.. Safety issues all the time.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Gas log insert damper lbrown2 Inspecting HVAC Systems 12 9/18/08 6:07 AM
damper on fan assist flue bking Inspecting HVAC Systems 7 9/29/07 1:18 PM
Soot from Barometric Draft Damper (posted by Ted Hull) AskNACHI.org AskNACHI.org Inspection Questions Forum 3 5/11/07 6:49 AM
HVAC "hard pipe" w/mechanical damper ? nkienitz Inspecting HVAC Systems 4 3/25/07 8:14 PM


All times are GMT -4. The time now is 6:33 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts