Default Baseboard Heat

I made a note on my last inspection that one of the baseboard heaters was controlled with a wall switch and not a thermostat like all the others...my client wanted to know if it was a safety hazard. I told him it was more of a wallet hazard if left on...because those things eat electricity and it would never shut off.

Now....baseboard heaters can and will be fire hazards just based on how they work, if not used properly. But, could this thing be a fire hazard because it isn't on a thermostat? I don't think it would be an inherent fire hazard, but I suppose it could be hazardous as it would never shut off no matter the temp.....hmmm...any thoughts please, if I was wrong I want to let him know.....thanks!

BTW, I told him an electrician/hvac guy should be able to install a thermostat rather easily.....
Reply With Quote
  #2  
Old 3/24/06, 8:14 PM
Timothy J. Gardner Timothy J. Gardner is offline
InterNACHI Member
 
Join Date: Sep 2003
Location: Moneta, VA
Posts: 270
Default Re: Baseboard Heat

The thermostat is basically an on/off switch. The room might get pretty warm, but is not a fire hazard, any more than a thermostatically controlled one.
tg
Reply With Quote
  #3  
Old 3/24/06, 8:22 PM
bkelly1's Avatar
bkelly1 bkelly1 is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Rives, TN
Posts: 1,757
Please Note: bkelly1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Baseboard Heat

Agreed
Reply With Quote
  #4  
Old 3/24/06, 8:28 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,095
Default Re: Baseboard Heat

What does the manufacturer's installation/operating instructions say?
Reply With Quote
  #5  
Old 3/24/06, 9:03 PM
Jay Moge's Avatar
Jay Moge Jay Moge is offline
Active Poster
 
Join Date: Aug 2005
Location: Derry New Hampshire
Posts: 761
Please Note: Jay Moge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Baseboard Heat

how about the voltage rating on the switch? some electric heat system require a special 240vac t-stat, and i'd question if the switch is rated for more than 125 vac??????
Reply With Quote
  #6  
Old 3/25/06, 1:15 AM
tneumann's Avatar
tneumann tneumann is offline
Active Poster
 
Join Date: Jan 2006
Location: Woodland Park, co
Posts: 2,074
Please Note: tneumann is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Baseboard Heat

Very nice Jay.....I didn't think of that..hmmm, perhaps I should rethink that one...hmm...now how the f do I backtrack? Mr. Client, I'm sorry I'm a dumbarse and didn't think of this before, but that switch may need to be rated for a different voltage...you really should call sparky to evaluate as it is possible that it is unsafe... oops.
Reply With Quote
  #7  
Old 3/25/06, 1:24 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,726
Default Re: Baseboard Heat

Just take out the "I'm a dumbass" part and you'll be alright.
Reply With Quote
  #8  
Old 3/25/06, 1:29 AM
JLilly's Avatar
JLilly JLilly is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Parkersburg, WV
Posts: 232
Default Re: Baseboard Heat

Every baseboard heater I've ever seen was 220V. No light switch is appropriate for baseboard heat. The right device is a 2 pole line voltage rated wall t-stat. Very inexpensive.
Reply With Quote
  #9  
Old 3/25/06, 1:41 AM
JLilly's Avatar
JLilly JLilly is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Parkersburg, WV
Posts: 232
Default Re: Baseboard Heat

Specifications:

Easy to install Honeywell Line Voltage Thermostat
Mounting: Standard 2x4 in Electrical Box
Line voltage thermostat
Electric ratings: 22 amps at 120-240 Vac, and 19 amps at 277 Vac
Switch type: SPST (2-wire) or DPST (4-wire)
Attached Thumbnails
baseboard-heat-baseboard.jpg  
Reply With Quote
  #10  
Old 3/25/06, 1:44 AM
Joseph Hagarty's Avatar
Joseph Hagarty Joseph Hagarty is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 3,434
Default Re: Baseboard Heat

Any receptacles currently installed above these baseboard electric heaters?



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #11  
Old 3/25/06, 1:56 AM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,095
Default Re: Baseboard Heat

I don't know the brand of the heater you saw but this mfg (Cadet) says a t'stat is required like Jay & James indicate, not a switch. See the 2nd paragraph on page 2.

Last edited by mboyett; 4/9/09 at 10:37 PM..
Reply With Quote
  #12  
Old 3/25/06, 2:54 AM
Jeffrey D. Clark's Avatar
Jeffrey D. Clark Jeffrey D. Clark is offline
Active Poster
 
Join Date: Nov 2005
Location: Vashon, Wa
Posts: 645
Please Note: jclark1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Baseboard Heat

The contacts on a light switch are not rated for that kind of current, especially if it's 120v baseboard (they do make them) either way the resistive current required for all but the smallest baseboard can heat up a regular light switch, they do make some pretty heavy duty 220v switches with heavy duty contacts for motors that look like regular light switches . But most houses have cheapo switches and receptacles, not even commercial or spec grade.
Reply With Quote
  #13  
Old 3/25/06, 4:53 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,246
Default Re: Baseboard Heat

Quote:
Originally Posted by tneumann
Very nice Jay.....I didn't think of that..hmmm, perhaps I should rethink that one...hmm...now how the f do I backtrack? Mr. Client, I'm sorry I'm a dumbarse and didn't think of this before, but that switch may need to be rated for a different voltage...you really should call sparky to evaluate as it is possible that it is unsafe... oops.
Very easy, and it's one that I use quite often since I have the luxury of not providing on-site written reports.

When there is something at the site that intrigues me (read, confuses the hec out of me), I will tell the Client that I found something that is interesting and that I have access to a trade association that has 8,300 registered and certified home inspectors. I will pose the question with a picture and see what the masses have to say. If it proves to be a problem, I'll put that information in the written report. If there is nothing in the written report about it, then it's not a problem.

If I've already provided a written report and read something on NACHI that starts me thinking about something, then I follow up the same way.

Let them know that you don't know everything but that you have access to the world's largest home inspector trade association, as well as various plumbing, electrical, etc. Internet sites. Your client will eat that up and refer you to the world.



  • Need a positive networking site? Click here to join Active Rain, a networking community of over 140,000 real estate professionals helping others.

  • NACHI 2005 U.S. Member of the Year
Reply With Quote
  #14  
Old 3/25/06, 7:52 AM
bkelly1's Avatar
bkelly1 bkelly1 is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Rives, TN
Posts: 1,757
Please Note: bkelly1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Baseboard Heat

I have seen plenty of 120v baseboard heaters. A good way to tell is also the length of the heater. The ones here were usually 120 v until they reached 8 ft. The 6ft could be 120v or 220v. The 4ft were 120v almost alll the time. Here that is.
Reply With Quote
  #15  
Old 3/25/06, 11:17 AM
tneumann's Avatar
tneumann tneumann is offline
Active Poster
 
Join Date: Jan 2006
Location: Woodland Park, co
Posts: 2,074
Please Note: tneumann is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Baseboard Heat

Great information guys!

That is worth the 289 right there....!

I have let him know that I have more info for him on the baseboard heaters....now the question is....how do I add an addendum to the official report to CMA?

I plan to just type up an explanation, using the info I got here , and tell him to check on it w/ sparky and hvac guys....that should cover me shouldn't it?
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
efficiency of 15 yr old peerless afrost HVAC 11 11/19/07 10:51 AM
baseboard heat pfranks Electrical 5 10/28/07 12:54 AM
Condemned Furnaces Spark Safety Issues Gary Reecher HVAC 7 3/8/07 9:17 PM
Heat pump in a 80+ year old masonry house jskrypka HVAC 9 11/25/06 11:47 PM
Radiant Heat Transfer rmyers1 Structural 0 6/1/06 12:21 AM


All times are GMT -4. The time now is 3:26 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts