This is a question I have on my house. The bathrooms vent to the attic. Bad.
I'm going to fix this. Should I put a vent in the roof, siding or the soffit. Does it matter. Should I use flex pipe, rigid or is PVC OK. Should it be insulated to prevent condensation or freezing. Should I put the vent pipe on top or under the insulation. Thanks Bill Bill Emelander Professional Edge Home Inspection Grand Rapids and all of West Michigan NACHI #03111914 www.proedgehi.com |
|
#2
|
|||
|
|||
|
I suggest...
Roof Rigid Not necessarily If it is horizontal before going through the roof, above the insulation. But then, what do I know? I asked my son-in-law, the roofing guy. But then, what does he know? "not just an inspection, but an education" www.homesweethomecincinnati.com Democracy is two wolves and a lamb. Liberty is a well-armed lamb. B. Franklin |
|
#3
|
|||
|
|||
|
This is for cold climates
The duct should vent out a gable end or the roof. Should not be in the soffit as the hot humid air may enter the roof space back up through the soffit. Rigid ducting to reduce friction and not too long for the same reason. Duct should be sloped to the exterior so if there is any condensation it will run out of the house and not back down the fan. Insulate the duct to the exterior so that the hot humid air will hopefully not condense in the duct untill it exhausts to the exterior Use a good quality exterior vent hood so hopefully it will not freeze shut in the winter. David |
|
#4
|
||||
|
||||
|
Quote:
Flex is okay for bathroom exhaust venting (and cheaper) No, on top... my $3.95 worth, for Sunny Climes like Mine! - Mike Michael W. Gault, SC RBI 1728 A to Z Home Inspections Charleston, Dorchester & Berkeley Counties in S.C. NACHI05040682 www.atozinspector.com (843) 442-9755 Charleston Home Inspector |
|
#5
|
||||
|
||||
|
I'd rather see David's way.
A brief study of thermal dynamics tells me the hot air exhaust into the soffit area will rise back into the attic. Erby Crofutt B4U Close Home Inspections Georgetown, Kentucky KY Lic# HI-2041 www.b4uclose.com http://www.kentuckyradon.com Kentucky Home Inspections Kentucky Home Inspectors NACHI02090301 "LIKE" me on Facebook Kentucky Homeowner Resources @ http://www.kentuckyhomeinspections.com BLOG by Erby, The Central Kentucky Home Inspector Join Active Rain HERE |
|
#6
|
||||
|
||||
|
Please Note:
tneumann is a non-member guest and is in no way affiliated with InterNACHI or its members.
Does it look like this? I just found this in mom in laws attic.....
|
|
#7
|
||||
|
||||
|
Please Note:
phinsperger is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Quote:
Quote:
Quote:
|
|
#8
|
|||
|
|||
|
Please Note:
James D Mosier is a non-member guest and is in no way affiliated with InterNACHI or its members.
FWIW.
After living in my new house for about two years I noticed that there didn't seem to be any exhaust fan venting. Upon further investigation I found that was the case. Just a fan unit covered with blown in insulation, black insualation, not pink like the rest of the attic. The sheathing 2 ft above this area was also starting to turn black. I bought a flexible vent duct and the roof termination for it. Since it was the dead of winter I just routed the flex tube from the fan towards the center of the attic (6ft below sheathing opposed to 2ft) and planned on fininshing it that summer. Well, you know how plans come and go, that one went. It has been seven NE Ohio summers and winters with no additional mold growth. Maybe this summer I'll take care of it. |
|
#9
|
||||
|
||||
|
Bill you are in MI, condensation is an isue make sure you account for it.
Joe |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Plumbing vent next to exhaust vent | mpettitt | Plumbing Inspections | 4 | 10/12/07 6:38 PM |
| Air admittance valves everywhere | apfaff | Plumbing Inspections | 13 | 4/16/07 10:17 AM |
| Gas and oil hot water tank and Boiler Share Vents | hvanderbeek | Miscellaneous Discussion for Inspectors | 8 | 1/25/07 6:22 PM |