Default Best option for replacing Bryant A/C unit

Hello fellow members ~ My first time for posting. So bear with me. My 26 year old Bryant A/C condensing unit (model#565AJ0-14) went out this summer. It is covered by home insurance (American Home Shield) and is rated at nearly 1 1/2 ton. It is part of a split system, connected to an Armstrong Air handler in the attic (model #AH24A08A ... SN8493D27704) Mfg approx 1993 and rated at 2 tons.

The HVAC Lennox contractor, assigned by American Home Shield, tells me that the A/C condenser and air handler are NOT matched and has recommended that I have him install a Goodman A/C rated for 2 tons. This A/C system is cooling our upper floor (approx 630 square feet). My HVAC contractor also tells me that he can install the new AC in the next week, even though the weather is hovering around freezing at night. But he can not test the entire system until later in the spring and warns me that there might be problems with the air handler.

I really can not afford a new heat pump and feel that I don't need it for the upper level. Possibly the lower level, yes.

I was told by another HVAC contractor that I may run into problems with the "new" Goodman unit because both it and the air handler will continue to use the outdated coolent. The Lennox HVAC dealer assures me that that he has been stock piling the older type coolant because he has many customers using the older style A/C units (R-22 vs ?).

My questions:

1. Did I make a good decision to go with a 2 ton replacement A/C unit?
2. What problems could I have with staying with the older type of coolant system?
3. If the air handler is found to be defective in the spring, what are my options at that time?

As a final comment, my attic has 4 inches of blown insulation. I plan to remove it (push it aside) and install R-30 rolls (9 1/4 inches thick) and place the blown insulation on top. Will this increased insulation cause any problems with my A/C system? I would think that it should improve it.

Thanks. Bob
Reply With Quote
Find an InterNACHI certified Texas Home Inspector (and anywhere else in North America)
  #2  
Old 12/11/09, 6:51 PM
gkay gkay is offline
New User
 
Join Date: Jan 2009
Location: Olkanagan Valley British Columbiia Canada eh
Posts: 50
Please Note: gkay is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Best option for replacing Bryant A/C unit

My questions:

1. Did I make a good decision to go with a 2 ton replacement A/C unit?

Your HVAC contractor should determine what size a/c unit is required with his/her heat gain calculations. What ever size is used get a matched system, that way you won't have any surprises (additional expenses) come spring.

2. What problems could I have with staying with the older type of coolant system?

The older type refrigerant R22 is an ozone depleting substance and will be phased out of production by 2020, meaning you will pay through the nose for any R22 which is available should you need any or you will need to buy another matched system which uses the new refrigerant R410A.
Anyone buying your home will be notified in the home inspection that you have an air conditioner that is using a refrigerant that is no longer available and should reserve some funds for a replacement.

3. If the air handler is found to be defective in the spring, what are my options at that time?

$$$$$

As a final comment, my attic has 4 inches of blown insulation. I plan to remove it (push it aside) and install R-30 rolls (9 1/4 inches thick) and place the blown insulation on top. Will this increased insulation cause any problems with my A/C system? I would think that it should improve it.

Why don’t you just leave the blown where it is and roll over it with the batts?
Reply With Quote
  #3  
Old 12/11/09, 7:22 PM
James E. Braun, CMI's Avatar
James E. Braun, CMI James E. Braun, CMI is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Jefferson City, MO
Posts: 6,585
Default Re: Best option for replacing Bryant A/C unit

Stay away from the Goodman brand and other other brands manufactured by Goodman. They are nothing but junk. When I use to own a heating and cooling company, we always stuck clients that have Goodman units to the back of the list. You would fix one thing on the unit and something totally unrelated would break the next week. Then the customer thinks that you did something to his unit. The odds are if you ask the installer if he will be performing all the service calls if the unit ever breaks down, he will say 'No" and for good reason. Sad but true.
Reply With Quote
  #4  
Old 12/11/09, 8:06 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,103
Default Re: Best option for replacing Bryant A/C unit

I have heard that Goodman units are ok now if installed correctly. This would include ones less than 5 years old. What years were you referring to James?



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #5  
Old 12/11/09, 11:11 PM
cjustason's Avatar
cjustason cjustason is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Eastern Iowa
Posts: 616
Default Re: Best option for replacing Bryant A/C unit

... .

Last edited by cjustason; 12/11/09 at 11:15 PM..
Reply With Quote
  #6  
Old 12/12/09, 9:46 AM
Bob Luebbers Bob Luebbers is offline
New User
 
Join Date: Dec 2009
Posts: 3
Please Note: Bob Luebbers is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Best option for replacing Bryant A/C unit

Thanks everyone for your responses. To help clarify my situation:

1. Attic space ... 630 sq ft. 2 x 10 & 2 x 6 joists on 16in centers contain loose fill white powder insulation with NO VAPOR barrier. Recommended attic insulation is R-49 for my zone 2. Because there is no vapor barrier, I plan to scoop the loose fill and move it to the side. Then inspect and fill any air gaps around electrical lines, etc running down into the walls below. Then add the first rolls of FACED 9in R-30 fiberglass insulation. I will then install 2x4 or 2x6 boards perpendicular to the existing joists and top the voids with the white powder loose insulation. I also plan to place a deck and add electrical lights and outlets so that the air handler can be easily serviced. Also will allow for storage space. Incidentally, moisture is controlled by 25in square wall vents on opposite ends of the attic. One of the vents has a fan controlled by a thermal switch that turns on when the attic temp reaches a given temp (I don't know the actual setting). There are NO soffit vents and I assume that this is intentional. Should I add soffit vents?

2. I plan to immediately call the Lennox HVAC and re-think the option of having him replace the "dead" A/C condenser with an appropriately sized Lennox heat pump. I realize from this thread that he will need to remove the Armstrong air handler and replace it. Gordon Kay made an excellent point that if I went with a replacement A/C unit, it would be using the outdated R-22 coolant and I agree that this would detract from the resale of the house if the future buyers knew that the A/C was R-22.

3. My HVAC guy was probably recommending Goodman because he knew that my home warranty would not pay for a Lennox brand. After all the original unit was 23 years old. So at this point, I am thinking of biting the bullet and upgrading to a heat pump.

Any thoughts?

Thanks all. Bob
Reply With Quote
  #7  
Old 12/12/09, 10:03 AM
gkay gkay is offline
New User
 
Join Date: Jan 2009
Location: Olkanagan Valley British Columbiia Canada eh
Posts: 50
Please Note: gkay is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Best option for replacing Bryant A/C unit

Quote:
Originally Posted by jbraun View Post
Stay away from the Goodman brand and other brands manufactured by Goodman. They are nothing but junk. When I use to own a heating and cooling company, we always stuck clients that have Goodman units to the back of the list. You would fix one thing on the unit and something totally unrelated would break the next week. Then the customer thinks that you did something to his unit. The odds are if you ask the installer if he will be performing all the service calls if the unit ever breaks down, he will say 'No" and for good reason. Sad but true.


All manufacturers' have experienced their share of problems over the years, I don't think you can single any one out as junk. Maybe things have changed since the good ol days. The only thing I have seen as junk is directly related to neglect by the owner or poor/lazy maintenance practices by service techs. For the most part the components of heating or cooling equipment are made by totally separate manufacturing corporations like GE, Emerson, Robertshaw, Honeywell, White Rogers, Tecumseh, Copeland, Sporlan, Ram….
The most important part of any cooling or heating equipment is properly sizing the equipment and proper installation, followed by regular maintenance. Most have a 10 year parts warranty nowadays and Goodman just finished giving away a 10 year parts AND labour warranty.

Last edited by gkay; 12/12/09 at 4:38 PM..
Reply With Quote
  #8  
Old 12/12/09, 10:50 AM
gkay gkay is offline
New User
 
Join Date: Jan 2009
Location: Olkanagan Valley British Columbiia Canada eh
Posts: 50
Please Note: gkay is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Best option for replacing Bryant A/C unit

A heat pump, sweeeet. Good choice Bob I am sure you will be pleased. Sounds like quite a project you have going there. I don’t envy you with the insulation relocation task, but at least you are going to do it proper and a service platform with lights for the air handler to boot!!. You da man.
What does your HVAC guy think about Goodman HP? Lennox is good too but may cost a bit more. I believe the warranties are similar.
Let your hvac guy know what you are doing and try to co ordinate the work if possible. By working together your hvac guy will do a superior job for you. Is your duct work properly sealed and insulated and is you filter easily accessible?
Reply With Quote
  #9  
Old 12/12/09, 2:37 PM
Bob Luebbers Bob Luebbers is offline
New User
 
Join Date: Dec 2009
Posts: 3
Please Note: Bob Luebbers is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Best option for replacing Bryant A/C unit

Gordon and all ~ Again thanks for the solid support. Yes, I am in close conversation with my HVAC contractor and he has convinced me to stay with the Goodman A/C replacement (SEER rated at 13 vs my 23/yr old Bryant, est SEER of 7.5 or . His reasoning:

1. Don't spend a lot of money on the up stairs cooling unit.

2. Live with the fact that many home owners throughout the US will still have R-22 systems in operation for the next 10 years or so.

3. Obtaining R-22 coolant from him will not be a problem.

4. He doesn't recommend a heat pump for the upstairs because we have enough additional heat sources in the winter (e.g. electric base boards and hydronic radiant heating coils in the concrete floor (via an Arco electric boiler). On this last point, I totally agree.

Instead, he is advising me to focus on the eventual replacement of the downstairs air handler and A/C units which are old and the home inspector highly recommended that we budget for a replacement when the system fails. So now I am learning about the advantages of the newer energy efficient heat pumps.

The attic insulation project will get under way soon. Because I plan to service the filter in the attic handler myself ... and inspect the condensation pans ... I want lights on the subject and a sold deck to walk.

Again, thanks for the excellent feedback.

Bob
Reply With Quote
  #10  
Old 12/16/09, 9:14 AM
Gary Reecher Gary Reecher is offline
Active Poster
 
Join Date: Aug 2004
Posts: 273
Send a message via Yahoo to Gary Reecher
Please Note: Gary Reecher is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Best option for replacing Bryant A/C unit

Make sure that the duct work seams and joints in the attic are sealed to prevent pulling in hot attic air into the system and that ductwork is insulated.

Go with a thermostatic expansion valve on the indoor coil.

Look at the option of variable speed motor on the air handler. Depending upon a/c useage may cut electrical bills anywhere from $150 to $300 a year x life useage that will save lots of money in the future. Electric companies rarely cut back on their rates so it will be a good investment.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
What is your HVAC procedure? sstowe Inspecting HVAC Systems 66 5/28/09 1:48 PM
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues for Inspectors 50 4/20/08 2:26 AM
Need Assistance on A/C Unit pcarter-old-04 Inspecting HVAC Systems 9 6/21/06 8:23 AM


All times are GMT -4. The time now is 11:21 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts